Discuss flue terminal too close to cooker vent in the Plumbing Jobs | The Job-board area at PlumbersForums.net

leiadad

Gas Engineer
Messages
84
some advice needed, I could do with some input on a fanned flue outlet being 200 mm away from a cooker hood vent, the vent has flaps which close when not under positive pressure from hood. would this be classed as safe due to the flaps closing when cooker hood not in operation. I respect the fact maufactures instructions and bs expect 300 mm but I am a suing this would be in an open vent or window which is not under any pressure. any help would be great
 
Yes but I would note it down anyway
 
some advice needed, I could do with some input on a fanned flue outlet being 200 mm away from a cooker hood vent, the vent has flaps which close when not under positive pressure from hood. would this be classed as safe due to the flaps closing when cooker hood not in operation. I respect the fact maufactures instructions and bs expect 300 mm but I am a suing this would be in an open vent or window which is not under any pressure. any help would be great
I would not class this as safe. Both manufacturers and bs state 300mm. In the end if something goes wrong you are the one who gets the problem. Especially when people cook a lot they will use it.
 
some advice needed, I could do with some input on a fanned flue outlet being 200 mm away from a cooker hood vent, the vent has flaps which close when not under positive pressure from hood. would this be classed as safe due to the flaps closing when cooker hood not in operation. I respect the fact maufactures instructions and bs expect 300 mm but I am a suing this would be in an open vent or window which is not under any pressure. any help would be great

The 300mm does not apply to vents from a fixed appliance, such as cooker hoods.
I will dig out a reference
 

Reply to flue terminal too close to cooker vent in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
365
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
168
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
212
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock