Discuss System boiler tripping RCD at consumer unit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
5
Hi, I am looking for advice on a system boiler on S plan that keeps tripping the RCD for heating system. Friend called me, she had no power to boiler and called an electrician as the RCD wouldn’t reset. The electrician checked programmer and said it had power to connections and thermostat, but no power to the boiler. The programmer display was flickering and the red leds weren’t illuminated when selecting CH & HW on selector. I’m going to have a look tomorrow and she asked me to pick up new programmer, is it likely to be this with power to the connections on programmer or could it be pump or MV. Sorry but I don’t do much fault finding and repairs although I’m industry, was just so I can pick a pump and MV up while at merchants, any advice welcomed, thanks !
 
I've had the accellerator on the thermostat short out against a metal bit: had to bend the resister away from the metal bit (it was almost new too!). Drayton Combistat.
 
Hi, thanks for all the advice, it was the pump that failed. Disconnected the pump from wiring centre and replaced 3amp fuse in spur, reset the trip and it was fine. Measured the ohms across the live/neutral and was 110 ohms, changed pump and got power at boiler cheers for the advice !
 

Reply to System boiler tripping RCD at consumer unit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
230
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
102
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock