Discuss Gas Engineers > What is the correct procedure attending a boiler breakdown? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Also @ShaunCorbs & @firemant isnt what you are both describing a KW rating and not a gas rating. A gas rating for a 30kw boiler is about 3.2kw not 30kw? Or am I missing something here?

I don't quite understand your post, HF.
Probably strictly speaking, a gas rate would be measured in M3 but after saying Kw is not a gas rating, you go onto suggest it is.
A 30Kw boiler will be typically about 31/32Kw input, not 3.2. was that a typo?
 
I don't quite understand your post, HF.
Probably strictly speaking, a gas rate would be measured in M3 but after saying Kw is not a gas rating, you go onto suggest it is.
A 30Kw boiler will be typically about 31/32Kw input, not 3.2. was that a typo?
I mean that this is a gas rate mate

3D31C1DB-8248-4A3D-9475-4FAF0E193CC2.jpeg
 
My figures are direct on the meter to give you x amount of kw
 
But my view is that what you are both taking about is an output rating not a gas rate.

It is a gas rate (meter) comes out at 30kw

Eg

004.10
004.20

On the meter
 
I get that, but when you do this calculation 2.8 x 10.65 = 30 ish kw. The end figure which is 30 kw is not the boilers Gas rate it is an output rating.

I don't get what your trying to say ?

You want the input rating ?
 
its not hard if you know if you dont

write the number down time then write the numbers down work it out from there or time it if imperial

or if you do know what kw should give you like

.10 is 30kw
.095 is 28kw
.08 is 24 kw
.05 is 15kw
My point is, that this is an input/output rating dependant on how far you got with your calculations and not a gas rate.
 
.

HF: Like Shaun, I am slightly confused as to your line of thought. The GAS RATE is the INPUT, which arguably should be measured in M3, but we tend to do the calcs to Kw. The chart you produced, IIRC, showed the input in M3. So it IS the rate chart, as you understood.

But where are you reading your figures? The chart shows a 30Kw boiler as having a nominal input of 3.27M3.

Incidentally, that is the figure often copied onto the benchmark ;)
 
I think we are arguing the same thing mate. But I call the figure in the bold circle the gas rate and the figure in the thin circle the input/output rating. Ignore the exact figures I wasn’t getting them from anywhere they were just random figures :D:D

6122976A-44C0-445D-8B59-E18329059947.jpeg
 
I think we are arguing the same thing mate. But I call the figure in the bold circle the gas rate and the figure in the thin circle the input/output rating. Ignore the exact figures I wasn’t getting them from anywhere they were just random figures :D:D

View attachment 35478

Blimey, HF, they reckon a marathon is hard work :).
Yes, the 30Kw (thin circle) is the nominal output - but I don't really get your " input / output rating" description. it is simply the designed Output.

The (thick circle) IS the nominal Input, therefore the "gas rate" you are looking for. However, most of us, I think, would present the "gas rate" in KW/hr's.

So, yes, essentially we are in agreement.

What was your question? :)
 
Blimey, HF, they reckon a marathon is hard work :).
Yes, the 30Kw (thin circle) is the nominal output - but I don't really get your " input / output rating" description. it is simply the designed Output.

The (thick circle) IS the nominal Input, therefore the "gas rate" you are looking for. However, most of us, I think, would present the "gas rate" in KW/hr's.

So, yes, essentially we are in agreement.

What was your question? :)
I don’t have one:D:D:D it’s been a long day. Sorry mate.
 

Input/output are 2 different things on that data badge

That is a 24Kw boiler? The 24Kw is the advertised OUTPUT, but the actual MAXIMUM OUTPUT, as it happens, is 24.7Kw.
(Advertising a 24.7Kw boiler as such is not as snappy as saying "24", although I do not know why they don't just do the data plate at an Input relating to a 24Kw output. But they are not alone)

The MAX INPUT is 25.7Kw. The boiler is range ratable, between 11Kw and 25.7Kw INPUT. It is this range which you would be looking for, and verifying against, when as rating.
 
Input/output are 2 different things on that data badge

That is a 24Kw boiler? The 24Kw is the advertised OUTPUT, but the actual MAXIMUM OUTPUT, as it happens, is 24.7Kw.
(Advertising a 24.7Kw boiler as such is not as snappy as saying "24", although I do not know why they don't just do the data plate at an Input relating to a 24Kw output. But they are not alone)

The MAX INPUT is 25.7Kw. The boiler is range ratable, between 11Kw and 25.7Kw INPUT. It is this range which you would be looking for, and verifying against, when as rating.
I understand that mate. But what I was saying is that at college here. We are taught that the gas rating is the lower figure and the output rating is the higher figure. That is what I was saying.
 
I understand that mate. But what I was saying is that at college here. We are taught that the gas rating is the lower figure and the output rating is the higher figure. That is what I was saying.

Back to front, HF. Or is that a typo.? Are you still training, HF?

The Gas rate is the Consumption (Input) (higher figure), which HAS to be greater than the OUTPUT (lower figure).


(I KNOW, before someone comes back with 103% efficiency :) )
 
Back to front, HF. Or is that a typo.? Are you still training, HF?

The Gas rate is the Consumption (Input) (higher figure), which HAS to be greater than the OUTPUT (lower figure).


(I KNOW, before someone comes back with 103% efficiency :) )
I’m too tired to carry this on mate. I will just agree with you.
 
Okay. But you really do need to know. It is actually not difficult. You need to speak to your trainer, if you are, in fact, still training.
Mate. Let me explain this to you. Either we have got crossed wires here or it is not me that is wrong. What it sound like you are talking about is a equivant heat input. (Not a gas rate) a gas rate is how much gas an appliance uses in 1 hour, not the figure you get once you times this figure by 10.65, or whatever calorific value you are using. (This figure is an input rating) I cannot explain it any clearer. The diagram below if the best I could find.

A1F9F8B5-14A5-4BB4-9A1F-90370EC9D97D.jpeg
 
Okay. But you really do need to know. It is actually not difficult. You need to speak to your trainer, if you are, in fact, still training.
Mate. Let me explain this to you. Either we have got crossed wires here or it is not me that is wrong. What it sound like you are talking about is a equivant heat input. (Not a gas rate) a gas rate is how much gas an appliance uses in 1 hour, not the figure you get once you times this figure by 10.65, or whatever calorific value you are using. (This figure is an input rating) I cannot explain it any clearer. The diagram below if the best I could find.
Okay. But you really do need to know. It is actually not difficult. You need to speak to your trainer, if you are, in fact, still training.
I’ve been qualified for 12 years mate. Not ages but long enough.
 

Reply to Gas Engineers > What is the correct procedure attending a boiler breakdown? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Had a call to a 82 Old man, he paid these £300 up front for a years cover, and I find out on arrival he's been waiting for 3 weeks, no heating or HW.. ( I had to dig backwards from the customers phone number he had) . Turns out the email for invoice i asked for is fake, dont reply to my text...
Replies
3
Views
552
Just an update to anyone who was following the thread on this site: Tify to gas engineer, what will it take? I got a DM from a user asking for an update, he like myself was gobsmaked at the level of abuse I got from asking a basic question. Thanks Tom for the DM, I managed to pass in 2019...
Replies
2
Views
416
I was sent an engineer by Ideal Heating to fix a problem with my system. When he left he drove over a pot of sealing compound (which must have dropped out of his van) on my shared drive. My neighbour pointed it out to me since he was parked in her space. I tried to remove it with water and...
Replies
10
Views
618
Hi everyone I currently work in oil and gas industry working in North Sea and further afield operating on high pressure oil and gas plants. This line of work means I have on average 6+ months off a year, im thinking of training to become a domestic gas engineer in my time off to earn a bit extra...
Replies
0
Views
853
Hi, I’m looking to retrain as a gas engineer and do a new entrants gas course. I’m a bit concerned by the ‘on-job’ work experience/shadowing, as some course want to charge £1500 to pair you up with a qualified engineer. Some courses don’t offer pairing and suggest you find your own engineer to...
Replies
1
Views
442
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock