Hi guys, I’m in the process of ripping out an old one pipe system and replacing it with a two pipe, feed and return. The new system will be on two zoning valves one for upstairs and one for downstairs.

Originally i wanted the system on a single stat and single zone valve... with a flow of 0.477 l/s and a 3.9m head loss (excluding loss over the boiler) I was going to use the Grundfos Alpha 1 as I liked the idea of balancing the system from the mobile app (potentially a time saver) and the option of auto adjusting flow rate as the TRVs close.

I’ve since changed my mind to a multi zone with upstairs and downstairs on separate zone valves and wondered if the same pump would be able to adjust flow automatically when the zone valves close.

If I go with the two zones, at the pump the flow is still 0.477 l/s but of one zone valve closes, the upstairs loop has a flow of 0.22 l/s with 1.5m head (excluding boiler) and the downstairs loop has a flow of 0.25 l/s with a head loss of 2.1m. Would the alpha 1 be able to reduce the flow rate enough to keep the return temp to the boiler the same no matter which valves are open or closed?

Thanks
 
Thanks for the replies...

In terms of piping it's a vented S-plan system with a 24kW Worcester Greenstar Ri boiler. There's a bypass (gate valve) fitted which I hoped would maintain flow when the zone valves close.

I was hoping to add an additional zone valve in parallel with the existing CH valve? Would I need a low loss header/close couple tees for this to work?
 

Reply to Circulating pump for Multi zone? in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
217
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
176
Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
169
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
256
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock