I am always surprised that Boilers don't display return temperatures. I manually adjust flow temps to achieve a return of about 53 as a form of weather compensation. Last time the best flow temp was 62 with return 54 and as you can see my solid walled home couldn't get there.

A hand on the return pre and post bypass showed the problem. Radiator returns were in the 40s. I estimate 50% of boiler flow was heading straight back. Interestingly the valve stayed jammed open even after the foreign body was out, presumably due to wear. It is a big aperture, so even a slight opening has a large curtain area.

Quick swap, Boiler temps now 70 - 50 and boiler output up from 10kw to 16kw.

I know this is not rare, but the lesson for me is to check return temps before and after the bypass regularly, when the system has recently started up.
 
View attachment 35187 View attachment 35189
I am always surprised that Boilers don't display return temperatures. I manually adjust flow temps to achieve a return of about 53 as a form of weather compensation. Last time the best flow temp was 62 with return 54 and as you can see my solid walled home couldn't get there.

A hand on the return pre and post bypass showed the problem. Radiator returns were in the 40s. I estimate 50% of boiler flow was heading straight back. Interestingly the valve stayed jammed open even after the foreign body was out, presumably due to wear. It is a big aperture, so even a slight opening has a large curtain area.

Quick swap, Boiler temps now 70 - 50 and boiler output up from 10kw to 16kw.

I know this is not rare, but the lesson for me is to check return temps before and after the bypass regularly, when the system has recently started up.
I love stuff like this , it’s very informative thank you
Rob Foster aka centralheatking
 
There is very little about this out there when I searched. So I posted this. I wondered how many boilers out there fail to condense for this reason, and how many are checked for this.

A man of great esteem and intellect such as Robert perhaps feels this stuff beneath them, their advice being to fit a leaky filter thingy I suppose.
 
View attachment 35187 View attachment 35189
I am always surprised that Boilers don't display return temperatures. I manually adjust flow temps to achieve a return of about 53 as a form of weather compensation. Last time the best flow temp was 62 with return 54 and as you can see my solid walled home couldn't get there.

A hand on the return pre and post bypass showed the problem. Radiator returns were in the 40s. I estimate 50% of boiler flow was heading straight back. Interestingly the valve stayed jammed open even after the foreign body was out, presumably due to wear. It is a big aperture, so even a slight opening has a large curtain area.

Quick swap, Boiler temps now 70 - 50 and boiler output up from 10kw to 16kw.

I know this is not rare, but the lesson for me is to check return temps before and after the bypass regularly, when the system has recently started up.
some do, good ones
 

Reply to Dodgy Bypass Preventing Condensing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are a few months into our Viessmann Vitodens 100-W 19KW Heat Only boiler and it is working fine. We replaced an old 1999 Baxi. Our house is a 2 bathroom 4 bed detatched, built 1999. The engineer did not really know the Viessmann boiler and I am not convinced his approach of “turn everything...
Replies
5
Views
3K
S
Hello all I have a Worchester Bosch greenstar 32CDi combi with an S plan, 3port for UFH downstairs (4 zones) via manifold & mixer valve, & upstairs 4 rad system, with towel radiator always open for a bypass. I have a full tado system that is basically set to relay on/off when any thermostat...
Replies
0
Views
1K
StuckWithUFH
S
    • Like
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few threads on a few different forums but I wanted to share a full write-up with all the steps needed, benefits and costs. Overall, I fully recommend...
Replies
1
Views
1K
If the auto bypass in my condensing boiler is stuck open will it cause a problem and/or significantly reduce the boiler's efficiency? I think the bypass is stuck open because the temperature of the bypass pipe is always the same as, or close to, the temperature of the boiler flow, when measured...
Replies
0
Views
788
Hi all, I have recently had a UFH circuit added to my existing CH/HW system and had a question on performance when UFH and CH are operating at the same time. My boiler is an Vailliant EcoTec Plus 630 and for a number of years this was running with a CH and HW loop only. Each loop had a 2 port...
Replies
3
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock