Hi,

Long story short: my boiler (gas, conventional, vented, three port system) has been moved from one side of the house to the other.

Previously the immersion cylinder return was the final tee before reaching the boiler, and all worked fine.

Now the immersion cylinder return is a few tees before the boiler, and I'm experiencing many of the radiators coming on when only hot water is called for. The heating side of the 3 port remains cool, so I believe that this is reverse flow caused by the the freedom of water to go into radiators closer to the boiler return.

All of the materials I can find say that the immersion cylinder return must be the final tee before the boiler - and it makes perfect sense (the water can therefore only return to the boiler because the other direction is ultimately blocked by the 3 port valve being closed).

Anyhow, is there a standard attached to this principle that I can refer to, please?

Thanks
 
It’s a misunderstanding to think a cylinder return should be the last tee on the return.
In fact it doesn’t matter. All that does matter, is that all returns on the radiator circuit are teed in a common return, before joining the primary return.
 
It’s a misunderstanding to think a cylinder return should be the last tee on the return.
In fact it doesn’t matter. All that does matter, is that all returns on the radiator circuit are teed in a common return, before joining the primary return.
I don't see what you mean there. If "all returns on the radiator circuit are teed in a common return, before joining the primary return" that is the same as all heating returns being commoned before joining the cylinder return. And it's essential, to avoid the problem the OP is seeing.
 
Google the three tee rule.

Originally it was vent/feed ,cylinder and heating then when system design changed it may have been bypass, cylinder , heating.

Not sure if there's have ever been a British standard for it. It would come under general design practices.
 
Sounds very much like the work was completed by someone who didn't know what they were doing !!
Non-return valve is likely to be your only hope now.
but for god sake don't use the spring loaded type.
 
Thanks very much for the reply. Here's a grainy shot of the problem:

A is where the original final return for the boiler was.
B is a return from some of the the upstairs radiators
C is the return from the immersion cylinder
D is the return from all other radiators.

The problem is that A has now been capped, and the boiler return is now at the far end of D, beyond various radiator return tees.

Advice very much appreciated, thank you :)

exported.jpg
 
It’s a misunderstanding to think a cylinder return should be the last tee on the return.
In fact it doesn’t matter. All that does matter, is that all returns on the radiator circuit are teed in a common return, before joining the primary return.
Thanks very much. Radiator tees exist on both sides of the immersion cylinder return, so not in a common return at all. (Apologies - I'm a newbie!)
 
General design practices sound good - I'll search it out. The Three Tee Rule makes sense, thank you. I just need to create a cohesive argument to get the person who did the work to fix it, hence the wish to get something official. Much appreciated!
 

Reply to The final return tee: always the immersion cylinder return, but is it a standard? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
168
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
212
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock