Hi all. I seen an install today of a direct unvented cylinder which looked odd and just wanted some advice on it please. On a composite valve am I right in thinking, there’s a 22mm cold inlet, 2 balanced cold outlets and a prv??
 
expansion vessel port normally after the balanced
 
expansion vessel port normally after the balanced
I thought that was the case but I’m being assured that the 22mm connection on the side can be used for a balanced cold as well as a balanced cold out the bottom of the valve??
 
Never have two balances, if it got the plastic plug in it thats for the ex vessel , could do with a pic or manufacturer
 
I thought that was the case but I’m being assured that the 22mm connection on the side can be used for a balanced cold as well as a balanced cold out the bottom of the valve??

it could be but no scv in the end so would require one
 
That’s the set up guys!

89283EED-4D92-41DA-95E6-60C6DD040CEB.png
 
I thought that was the case but I’m being assured that the 22mm connection on the side can be used for a balanced cold as well as a balanced cold out the bottom of the valve??
Balanced cold only any good before the check valve, if you blow back through the valve (opposite direction of flow) the port your getting air through is for the expansion vessel and the other will be for balanced cold
upload_2018-8-9_22-15-24.png


upload_2018-8-9_22-15-24.jpeg
 
Balanced cold needs to be before the check valve or you could get hot water flowing back from the cylinder
 
Balanced Cold or Manifold.png Are we talking about the red item or the blue ?
Cos I see only one balanced cold port (blue). The other is a manifold for the cold water (red).
 
View attachment 34172 Are we talking about the red item or the blue ?
Cos I see only one balanced cold port (blue). The other is a manifold for the cold water (red).
This is what I couldn’t grasp, not sure what he was trying to ask. I think he means the cylinder side of the combination valve but don’t get why you would want to do that anyway when there’s a balanced cold there
 
Single check valve ??

Yea else hot water could flow backwards

Pressure reducing valve
Balanced take off with internal check valve
Balanced take off
Single check valve
Pressure relief valve

Would have to go like that so separate prv and relief valve needed
 

Reply to Unvented composite valve (reliance) query? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock