Can someone help diagnose Vaillant ecoTEC plus 837 with persisting F75 fault please?
We already replaced the pressure sensor, installed F75 kit, replaced the main heat exchanger, and the pump, and the PCB, and flushed the system and installed a filter on the return, but still sometimes we get F75. The boiler still reset and run, but we would like to get to the bottom of it if at all possible. Thanks in advance.
 
All those parts has been replaced in the course of 5 years not all at ones, and from different reasons, but the F75 has been creeping out all this time, some times the fault would be gone for months so you think that it was cured. The boiler is otherwise working well. There are two questions: 1) if there is a fault why the boiler always reset and continue to work sometimes for months? 2) if there isn't a fault why is the F75 keep creeping out? Thanks for your thoughts.
 
Yes, every three months or so, and it does seem to keep F75 away for a while, we are now on 1.8 bar when cold and 2.1 bar when hot
 
I believe F75 is a fault code for when boiler pressure is too low/ also doesn’t detect an increase in pressure when pump kicks on. Have you ever noticed what pressure your boiler is sitting at when this code is showing?
 
I noticed that if the F75 starts kicking and if after the first reset F75 returns, it makes it calm down if I top up. Last time boiler was at 1.7 bar before the first F75 kicked in. Generally speaking Vaillant have different fault code for low pressure and the boiler can work very well with 1.2 bar or even a bit lower, but that only if the boiler is not faulty.
 
ah Right could be a number of things. Sound like a defect in the sensor or it’s partially blocked if it needs such a high pressure to pick up anything. Has your expansion vessel ever been investigated as well as everything else you had mentioned?
 
I will check the vessel. After installing F75 kit is it best to leave the bottom sensor connected or it's best to disconnect it's plug?
 
I will check the vessel. After installing F75 kit is it best to leave the bottom sensor connected or it's best to disconnect it's plug?

Best to get a gas safe engy
 
I thought that this forum is there to help one another, so sorry for troubling you.

You are gas safe or your getting one ?
 
We have found the solution. For those of you who tried to help, if you would like to know please pm me. And to the others that didn't, no, we are not DIY
 
We have found the solution. For those of you who tried to help, if you would like to know please pm me. And to the others that didn't, no, we are not DIY
Do you have an external pump as well as the one in the Boiler?
 
We have found the solution. For those of you who tried to help, if you would like to know please pm me. And to the others that didn't, no, we are not DIY
Why would someone as a professional gas safe engineer make the customer poor by changing almost the whole boiler? Why not calling manufacturer and get some information or perhaps get it solved via warranty. It doesn’t seem very good to change all those parts ... very unprofessional
 
Why would someone as a professional gas safe engineer make the customer poor by changing almost the whole boiler? Why not calling manufacturer and get some information or perhaps get it solved via warranty. It doesn’t seem very good to change all those parts . very unprofessional

Apparently changing bits here and there over 5yrs cured it only for it to return after a few months is the answer.
 
Status
Not open for further replies.

Reply to Vaillant ecoTEC plus 837 R1 with persisting F75 fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
328
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
4
Views
174
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
189
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
183
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
276
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock