Before I call a plumber .........

My boiler (Gloworm 18sxi) slowly loses pressure and I'm having to regularly top it up. There are no obvious leaks anywhere and no discharge from the PRV as far as I can tell.

Just reading through the manual for the boiler, it says that it has an internal 8 lire expansion vessel and a maximum system content of 130 litres and there is a note saying "For larger systems use an additional expansion vessel". It provides a schematic on where to place the additional vessel.

I have a 4 bedroom house with 15 radiators, five of which are doubles. I've read that a rule of thumb is 10 litres per single radiator, so that would make my system something closer to 200 litres.

1. Do I need to get a plumber in to add an additional expansion vessel?
2. Is this likely to have anything to do with the loss of pressure issue?

Thanks
 
Normally 1l of expansion per rad so a 15l one is needed but that wouldn't cause your loss of pressure are there any valves under the boiler (on the 22mm pipes) ?
 
1, Yes you could do with an additional expansion vessel.

2, No it would not normally cause the system to loose pressure.

Is there a constant drip or running water coming from the condensate pipe? I've had a few glowworm SXi heat exchangers fail and one of the symptoms is loss of pressure.

How often is a top up of pressure required?
 
.... are there any valves under the boiler (on the 22mm pipes) ?

This is what is under the boiler if it helps ...

IMG_3396.jpg
 
Is there a constant drip or running water coming from the condensate pipe? I've had a few glowworm SXi heat exchangers fail and one of the symptoms is loss of pressure.

How often is a top up of pressure required?

Unfortunately I cant tell if there is a constant drip or running water from the condensate pipe because it goes through the wall and is joined directly into a guttering downpipe.

I'm having to top it up every 4-5 days at the moment.
 
Turn the boiler off

Turn the red valves off left and right

And leave it for a day

If the pressure drops it's inside the boiler if it doesn't it's on your system
 
Status
Not open for further replies.

Reply to Do I need an additional expansion vessel in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
133
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
175
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
255
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock