Search the forum,

Discuss Unvented wiring . in the Plumbing Jobs | The Job-board area at PlumbersForums.net

townfanjon

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
8,642
Strange request for Easter Sunday lol , its just in my head .
have any of you fine chaps got a wiring diagram for a y-plan with a new 2 port wired in for an upcoming unvented installation.
I usually change them to an s-plan but the boiler is miles away from the cylinder and would cause a load of work getting perm lives to the 2 ports .
Cheers in advance
 
Can you add a 2 port to a y plan? With the 3 port keeping one zone permanently open, what happens when the 2 port calls for heat? You'll get unwanted heating of a zone.
 
Can you add a 2 port to a y plan? With the 3 port keeping one zone permanently open, what happens when the 2 port calls for heat? You'll get unwanted heating of a zone.

Yes you can. It's on the HW side, so you can leave your 3 port in situ and have the 2 port for thermal cut out for the Unvented after the 3 port valve. It's doable but for everyone that i've come across it's not worth the hassle and easier just sticking two 2 port valves in.
 
Yes you can. It's on the HW side, so you can leave your 3 port in situ and have the 2 port for thermal cut out for the Unvented after the 3 port valve. It's doable but for everyone that i've come across it's not worth the hassle and easier just sticking two 2 port valves in.
Ok, I get what your saying, but if the 2 port acts only as a thermal cut out, what happens when the cylinder stat on the first cylinder is satisfied but the thermostat on the second isn't? You could end up with unbalanced temperatures.
 
Ok, I get what your saying, but if the 2 port acts only as a thermal cut out, what happens when the cylinder stat on the first cylinder is satisfied but the thermostat on the second isn't? You could end up with unbalanced temperatures.


I have never done it but a 2 port should be fitted on to a y plan unvented installation, yes a right pita
 
Ancient boiler pal , so no spare wires but just realised there must be a hw off wire , but really need 2
If you've got a HW off wire then you're sorted. Change that for a perm live, you'll already have Neutral and Earth there, along with HW on and CH on.

It's when you haven't got a HW off wire that's the issue (So when they have to have HW and CH at the same time)
 
If you've got a HW off wire then you're sorted. Change that for a perm live, you'll already have Neutral and Earth there, along with HW on and CH on.

It's when you haven't got a HW off wire that's the issue (So when they have to have HW and CH at the same time)

I have not looked , I just thought of it as I was typing
 
So your not having 2 cylinders? Why do you have to a 2 port on a yplan when feeding an unvented?
Part of the G3 regulations. Must have a thermal cut out, as a 3 port valve is always open in some form that doesn't meet the requirement.

See so many Unvented cylinders on 3 port valves, it's worrying! Had one where the High limit stat kept cutting out, so cylinder must have been about 85/90oc!
 
Part of the G3 regulations. Must have a thermal cut out, as a 3 port valve is always open in some form that doesn't meet the requirement.

See so many Unvented cylinders on 3 port valves, it's worrying! Had one where the High limit stat kept cutting out, so cylinder must have been about 85/90oc!
Good to know, I suppose if I had my g3 I would have known that :rolleyes:
 
If you've got a HW off wire then you're sorted. Change that for a perm live, you'll already have Neutral and Earth there, along with HW on and CH on.

It's when you haven't got a HW off wire that's the issue (So when they have to have HW and CH at the same time)

I am no sparks , is it acceptable to use the one perm live and split to supply both 2 ports ? Assuming there is one lol
 
Good to know, I suppose if I had my g3 I would have known that :rolleyes:
Many of the 3 ports that i've seen have been left in/fitted that had their G3 qualification.

It's daft really, the Manufactures instructions clearly state that a 2 port is needed, along with them sending one with the cylinder. If it comes with the cylinder then you'd be thinking I have to fit this thing!
 
Here you go.

3portwith2port.png
 
wire the port valve into the stat but you need a neutral
 
wire the port valve into the stat but you need a neutral
Isn't as simple as that unfortunately. As the HW Stat on a 3 port fires the boiler when it's just HW only. If the heating was running on the 3 port (So Live on the Orange wire on the 3 port) , it would back feed and hold the HW 2 port valve open. Therefore defeating the object of a thermal cut out.
 
Isn't as simple as that unfortunately. As the HW Stat on a 3 port fires the boiler when it's just HW only. If the heating was running on the 3 port (So Live on the Orange wire on the 3 port) , it would back feed and hold the HW 2 port valve open. Therefore defeating the object of a thermal cut out.

how would it as the 3 port wouldnt be wired to the stat
 
As the HW Stat is wired to fire the boiler (HW on to Common on stat, then 1 to S/L on boiler). Then the Orange wire for CH only on the 3 port is wired into the boiler at the same terminal (So your S/L on the boiler). So when you wire your additional 2 port into the 1 terminal on the HW stat (So that the 2 port closes when the stat breaks) if there is still a feed on the S/L to the boiler from the heating side the 2 port valve would still have a live feed and stay open.
 
As the HW Stat is wired to fire the boiler (HW on to Common on stat, then 1 to S/L on boiler). Then the Orange wire for CH only on the 3 port is wired into the boiler at the same terminal (So your S/L on the boiler). So when you wire your additional 2 port into the 1 terminal on the HW stat (So that the 2 port closes when the stat breaks) if there is still a feed on the S/L to the boiler from the heating side the 2 port valve would still have a live feed and stay open.

no it wouldnt

perm live to stat in

stat out to brown eg port valve open

neutral and earth the same done
 
Yeah, and the stat out also would have to go to boiler S/L. So if your S/L on the boiler is live from another source, so the heating. The valve would still be live and hold open.

No not with a safety stat 3 port doesn’t get wired to the stat
 
Every unvented manufacturer will provide a wiring diagram in their instructions for the use of the 3 port mid position valve & the required 2 port that must be installed with it. This is required as under fault conditions there could be an open pathway from the heat source to the cylinder allowing the cylinder temperature to go above 100deg C.

The only exception to this, to my knowledge, is Vaillant who applied & got a dispensation so long as their boiler & cylinders are used together as a package.
Megaflo one below Jon, whats the cylinder?
Y Plan unvented wiring .png
 
Every unvented manufacturer will provide a wiring diagram in their instructions for the use of the 3 port mid position valve & the required 2 port that must be installed with it. This is required as under fault conditions there could be an open pathway from the heat source to the cylinder allowing the cylinder temperature to go above 100deg C.

The only exception to this, to my knowledge, is Vaillant who applied & got a dispensation so long as their boiler & cylinders are used together as a package.
Megaflo one below Jon, whats the cylinder?
View attachment 38257

I didnt know about the Vaillant Chris , as far as I knew it was only Viessmann, on the 200’s its just a probe that plugs in to the board and the other end goes into the stat pocket .
Cylinder isn't chosen yet for this job yet , she will leave it up to me . Its just a shame the boilers a mile away from the cylinder .
 

Reply to Unvented wiring . in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
225
    • Like
  • Sticky
We have 2 brand new cordless, battery powered press tools in stock, and flying off the shelves. Our TekTools TZ1930 & TZ1550 are packed with advanced features - these cordless press tools are engineered for speed, precision, and ease of use across various applications. Just reply to this thread...
Replies
5
Views
854
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
230
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
306
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
218
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock