Search the forum,

Discuss Combi boiler: water pressure question. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
23
My son recently moved house;...the CH boiler is an Ideal Logic Combi ES30 and it’s about 2 or 3 years old.

When the system is cold the water pressure shows approx 1.9 bar,...when the CH has been on for a while and everything is fully heated-up the pressure gauge rises to approx 2.9 bar.

If the boiler is then turned off the pressure returns to 1.9 bar within 15 mins or so.

Is this pressure range normal?...is 2.9 bar too high?

The CH and hot-water appears to be functioning perfectly.

As ever, all advice gratefully received.
 
When your heating is on, pressure rise is Normal, but your sons pressure is set to high to start with, it should be set to 1bar when boiler is cold. Go round and bleed the radiators and make sure they're all full. If they are then attach a hose to the drain off valve and drain a little water out the system until it's around the 1 bar mark, but only do this when the heating is off and cold.
 
Many thanks for the reply Craig,...greatly appreciated.:)

I’ve read a suggestion that it might be an expansion vessel pressure problem.

However, there are no error codes of any kind on the display and everything appears to be functioning normally.

I will reduce the water pressure as you suggest but in the meantime is 2.9 bar dangerous?...the water pressure gauge doesn’t show any ‘RED’ warning sectors.
 
2.9 is just on the limit before the prv will open, not particularly dangerous but if the valve opens, it may not re-seat and will want replacing.
Your expansion vessel is not at fault, pressure just set too high, that's all.

And yeah, as Scott says, get a full service done.
 
Many thanks for the swift and helpful replies guys.:)

Is a 1 bar fluctuation in pressure acceptable when going from cold to hot?;...or would you expect the difference to be less than 1 bar,...or maybe expect the pressure the remain stable?

Does it vary from boiler to boiler manufacturer?
 
Many thanks for the swift and helpful replies guys.:)

Is a 1 bar fluctuation in pressure acceptable when going from cold to hot?;...or would you expect the difference to be less than 1 bar,...or maybe expect the pressure the remain stable?

Does it vary from boiler to boiler manufacturer?

Please see answers given above.
 
Many thanks for the swift and helpful replies guys.:)

Is a 1 bar fluctuation in pressure acceptable when going from cold to hot?;...or would you expect the difference to be less than 1 bar,...or maybe expect the pressure the remain stable?

Does it vary from boiler to boiler manufacturer?
The pressure fluctuation varies depending on system size, when water heats up, it expands so the bigger the system, the bigger pressure increase. On a typical 10 rad system I would expect the pressure to increase from 1 bar to around 1.5 bar when heated. However because your system was already at a higher pressure, there is less room for expansion so when your system heats up, the pressure increase is greater.

Drop the pressure, get the boiler serviced and it will be fine.
 
The pressure fluctuation varies depending on system size, when water heats up, it expands so the bigger the system, the bigger pressure increase. On a typical 10 rad system I would expect the pressure to increase from 1 bar to around 1.5 bar when heated. However because your system was already at a higher pressure, there is less room for expansion so when your system heats up, the pressure increase is greater.

Drop the pressure, get the boiler serviced and it will be fine.

Thanks for the comprehensive reply Craig. Greatly appreciated.
 
Hi guys,

As recommended, I reduced the water pressure to 1 bar in its cold state;...probably about 0.95 bar actually, but it’s difficult to be any more accurate given the vagaries of the gauge itself and the difficulty in actually reading it!....not the cleverest placement of an indicator gauge tbh.

Checked all rads (10 rad system) for any air and and switched on. The CH temp selector was on its max setting.

The water pressure climbed slowly and eventually settled at about 1.6 bar when fully heated-up and the burner had clicked off. When the burner was active the pressure climbed slightly to 1.7 bar but dropped back to 1.6 bar when the burner switched off.

I’ll get a GSR engineer to give it a service this week but in the meantime any comments on the above info?....i.e. is it an indication of anything untoward etc?
 

Reply to Combi boiler: water pressure question. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock