Discuss Does my Boiler need replacing? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

I have an old Ideal Mexico system boiler. I have not had it serviced for a few years and I know it should be serviced.

Yesterday the boiler did not light. I could hear the spark clicking repeatedly but after 10 minutes it still had not lit. So I assumed it was dead. I called a engineer.

Today I tried the boiler again and it works. The ignition comes on first click but latter on I noticed it takes a few clicks to ignite.

Anyway, warm again.

Engineer arrives and takes off front ONLY (just the white case) Looks at working boiler and turns the temp knob back and forth and states that the gas valve is likely needing replacement, the Spark PCB likely needs replacement, and the control knob is not properly working. He recommends a new boiler as the replacement parts are going to be costly.

Now I KNOW a new boiler will be cheaper to run, but as I am trying to sell the house it is not an investment I want to make.

HOWEVER I have to question how the engineer can determine that the gas valve needs replaceing without looking at it, not why the spark PCB needs replacing as it is clearly working. He said that it is on the way out and the spark is no longer big enough.

Am I being given a tall tale?
 
Parts can be expensive, especially some PCBs, but it seems to me he just wants to fit a new boiler.
Thank you, possibly my thoughts too, and in a way he is right. It is a very old inefficient boiler and I would probably get my money back in a few years. BUT I want to move.
Is he right the pcb could be working at a lower efficiency and thus need replacing. I just assumed that they either worked or did not work.
 
i presume its a fanned flue boiler mexico could be a couple of things but if sparks and lights than just let other engineers check it out they do sometimes take a few sparks to light and then they ignition electrode also is the flame sensor so this proves that it is lit then brings on full gas.

as i said could be a couple of things so dont just take his word for it but also as its an old boiler the purchaser will be told to get the heating boiler checked as part of his survey so could come back at you with a lower offer as the house needs an updated heating system.
 
I have an old Ideal Mexico system boiler.

It is not a system boiler but I know what you meant by saying that.

The Mexico was a very good boiler in my opinion. If it is working now the chances are it's something and nothing. I would say by the sounds of it that you need a good service carrying out by an experienced Heating Engineer.
As far as changing it goes. You won't get the money back so if you're moving house, my advice is get a good service by a competent person and ask them to give you some written info on the condition. A lot carry service / inspection sheets or if not they can no doubt send you something.

Twiddling knobs doesn't tell you anything much.
 
It is not a system boiler but I know what you meant by saying that.

The Mexico was a very good boiler in my opinion. If it is working now the chances are it's something and nothing. I would say by the sounds of it that you need a good service carrying out by an experienced Heating Engineer.
As far as changing it goes. You won't get the money back so if you're moving house, my advice is get a good service by a competent person and ask them to give you some written info on the condition. A lot carry service / inspection sheets or if not they can no doubt send you something.

Twiddling knobs doesn't tell you anything much.


Thank you. I assumed as much.

It did not start out in life as a system boiler, but when I moved in 10 years ago I had it upgraded (extra sensor) and it is now in a sealed system (no cold water header tank and pressure guage etc.)
 
Thank you, possibly my thoughts too, and in a way he is right. It is a very old inefficient boiler and I would probably get my money back in a few years. BUT I want to move.
Is he right the pcb could be working at a lower efficiency and thus need replacing. I just assumed that they either worked or did not work.

I’ve never Heard of a pcb working at a lower efficiency, just the boiler itself. Like others have said get an engineer who is willing to do the job and competently.
 
Thank you. I assumed as much.

It did not start out in life as a system boiler, but when I moved in 10 years ago I had it upgraded (extra sensor) and it is now in a sealed system (no cold water header tank and pressure guage etc.)

It still not a system boiler. It is a regular boiler on a sealed system.
Hope you get sorted with it.
 
Thanks for all the helpful comments. The second engineer arrived, and although it took 3 and a half hours! he fully serviced the boiler, recommended an extra vent (fair cop) and all is working fine. He said that the flames are burning at a good efficiency and the flue has a very good draw. He said the boiler was good for a years to come BUT parts would probably become scarce. So time to start saving for a replacement and plan for the future.
 
It
i presume its a fanned flue boiler mexico could be a couple of things but if sparks and lights than just let other engineers check it out they do sometimes take a few sparks to light and then they ignition electrode also is the flame sensor so this proves that it is lit then brings on full gas.

as i said could be a couple of things so dont just take his word for it but also as its an old boiler the purchaser will be told to get the heating boiler checked as part of his survey so could come back at you with a lower offer as the house needs an updated heating system.
Thank you for your information. It is in fact an open flue boiler. No fan that I can see. It is not as efficient as modern boilers but the rest of the system is. Y-Plan with independent timer control on each bedroom radiator ( to reduce the heating on the spare rooms) plus wireless and wifi connected main heating thermostat in the living room. A relatively new hot water tank with layer upon layer of insulation. Apart from the boiler there is limited room for improvement. I will be getting a quote for a new boiler anyway and see if they can provide a comparison of the cost of the old vs the new. It would help in either negotiation or as you say, get the boiler replaced myself.
 
If it is working then I would do as advised above and be prepared to lose a little money on the sale price then buyers can have their choice of new boiler, if you buy a new one now I would say that it will lose you money in the long term.
 
There you go sounds like an good engy
 

Reply to Does my Boiler need replacing? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

K
My conventional boiler needs to be replaced. One engineer suggested combi with an external pump because water pressure in my flat is low, the other said there's no need for a pump. He even said that if the pump would have a detrimental effect on the boiler. Who is right?
Replies
5
Views
512
It was fitted with the boiler a Potterton Suprima 30L about 21 years ago. Two PCB's later and a new fan the boiler is working perfectly. However, the programmer display is not showing any digits for the clock or anything else so I am unable to program it. It still works the boiler manually...
Replies
14
Views
997
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The existing pump flows downwards. The manual for the proposed replacement recommends that it should pump upwards. This would involve rearranging the flow &...
Replies
8
Views
599
I need some advice please. My Baxi boiler went recently faulty. A Baxi engineer came and fixed it in 10 minutes, he said that the ignition lead was connected incorrectly. He said that although the boiler was working, it was struggling until it failed. The boiler was serviced 2 months ago by a...
Replies
7
Views
383
Hi Guys, I am the miserable owner of a Keston C36 boiler. It has had EVERYTHING on it replaced. My questions is, what do I replace it with and can it be done without replacing the entire flue. The dual flue is at least 10m long and has a couple of 45 degree turns in it. Am I going to need...