Boiler not firing

Discuss Boiler not firing at UK Plumbers Forums; Hi all i would really like some advice please 2 zone heating 1 upstairs 1 downstairs on an ideal combi boiler 2 Honeywell cm707 programmable stats one for each valve ...
  1. #1
    Member
    Join Date
    Nov 2016
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Boiler not firing

    Hi all
    i would really like some advice please
    2 zone heating 1 upstairs 1 downstairs on an ideal combi boiler
    2 Honeywell cm707 programmable stats one for each valve
    wired to Honeywell junction box(wiring centre) as follows
    perm live from fused spur to term 1
    perm live from term 1 to boiler
    perm live to both stats in term 1
    perm live (grey) to both valves in term 1
    All neutrals in term 2
    all earths in term 3
    the stats have the perm live going in term A with the
    return term B out of stat (black) going to wiring centre in with brown upto valves
    orange from valve back to wiring centre with a grey going to boiler s/l
    each black from stat go into a separate terminal 4 and 6 with a brown from the valve

    when the stat is pumped up for heat the valves open but boiler does not fire is the wiring correct
    the valves are Drayton any help much appreciated thanks

  2. #2
    rpm
    rpm is online now
    Member rpm's Avatar
    Join Date
    Jan 2013
    Location
    Wherever I lay my hat
    Posts
    7,958
    Thanks
    352
    Thanked 483 Times in 468 Posts

    Default Re: Boiler not firing

    Mr Swale of Swale Heating, currently taking a bashing on another forum?

  3. #3
    Responsible Moderator...


    APPlumbing's Avatar
    Join Date
    Nov 2010
    Location
    Locks Heath fareham
    Posts
    13,460
    Thanks
    243
    Thanked 927 Times in 889 Posts

    Default Re: Boiler not firing

    Quote Originally Posted by rpm View Post
    Mr Swale of Swale Heating, currently taking a bashing on another forum?
    You're such a forum tart!!!

    I nearly joined swale about 18 years ago....
    Swale and Masood like this.
    Behind every great man is a woman rolling her eyes.

    I have an unfortunate problem. I should stand upwind if I were you!

    IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

    Read more: http://www.ukplumbersforums.co.uk/pl...#ixzz2AiWGkgEG

  4. #4
    UK Plumbersforums Trusted Advisor.
    SimonG's Avatar
    Join Date
    Feb 2011
    Location
    in the land of make believe, in the county of durham, next best to Yorkshireland
    Posts
    16,112
    Thanks
    555
    Thanked 1,560 Times in 1,499 Posts

    Default Re: Boiler not firing

    Use a tester to check power at necessary points. Simple s plan.
    Swale and Masood like this.
    Fly Me To The Moon And Let Me Play Among Stars.............




    No I'm not cheap, but I'm happy in my work.

    Wouldn't you rather have somebody that's happy working in your house?


  5. #5
    rpm
    rpm is online now
    Member rpm's Avatar
    Join Date
    Jan 2013
    Location
    Wherever I lay my hat
    Posts
    7,958
    Thanks
    352
    Thanked 483 Times in 468 Posts

    Default Re: Boiler not firing

    Quote Originally Posted by APPlumbing View Post
    You're such a forum tart!!!
    APPlumbing likes this.

  6. #6
    Member
    Join Date
    Nov 2016
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Boiler not firing

    Quote Originally Posted by rpm View Post
    Mr Swale of Swale Heating, currently taking a bashing on another forum?
    Hi Iam not mr swale Iam a new build installed trying to get my head round this 2 zone heating that contractors want in, never done it before, swale is the river next to me
    rpm likes this.

  7. #7
    Member
    Join Date
    Nov 2016
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Boiler not firing

    Thanks for reply, 240v at both terminals 4-6
    240v at terminal 10 orange x 2 and s/l grey upto boiler
    240v at boiler perm live and switched live when stats are on

  8. #8
    Plumbers Arms member

    Masood's Avatar
    Join Date
    Nov 2011
    Location
    East London / Essex border
    Posts
    4,824
    Thanks
    623
    Thanked 587 Times in 530 Posts

    Default Re: Boiler not firing

    Quote Originally Posted by Swale View Post
    Hi all
    i would really like some advice please
    2 zone heating 1 upstairs 1 downstairs on an ideal combi boiler
    2 Honeywell cm707 programmable stats one for each valve
    wired to Honeywell junction box(wiring centre) as follows
    perm live from fused spur to term 1
    perm live from term 1 to boiler
    perm live to both stats in term 1
    perm live (grey) to both valves in term 1
    All neutrals in term 2
    all earths in term 3
    the stats have the perm live going in term A with the
    return term B out of stat (black) going to wiring centre in with brown upto valves
    orange from valve back to wiring centre with a grey going to boiler s/l
    each black from stat go into a separate terminal 4 and 6 with a brown from the valve

    when the stat is pumped up for heat the valves open but boiler does not fire is the wiring correct
    the valves are Drayton any help much appreciated thanks
    Quote Originally Posted by Swale View Post
    Thanks for reply, 240v at both terminals 4-6
    240v at terminal 10 orange x 2 and s/l grey upto boiler
    240v at boiler perm live and switched live when stats are on
    Sorry, I'm finding it hard to visualise what you're describing. A photo or diagram would be really helpful.

    Alternatively, take a look at the Honeywell website for a standard S-plan system which is what you're trying to configure. Follow the diagram and you won't go wrong. Terminal numbers and wire colours aren't that important, just follow the switching sequence..
    Last edited by Masood; 03-12-2016 at 08:19 PM.
    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

    Find us at:

    http://www.ifraplumbingandheating.com


  9. #9
    Member
    Join Date
    Mar 2013
    Posts
    1,446
    Thanks
    46
    Thanked 224 Times in 220 Posts

    Default Re: Boiler not firing

    Use multimeter not volt stick. If perm live and s/l going to boiler are both 240v. then, other than checking fuse on PCB, you will need GS engineer.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. oil boiler not firing
    By Inverness in forum Oil and Solid Fuel Forum
    Replies: 2
    Last Post: 06-01-2016, 11:07 PM
  2. Boiler not firing up, or only firing up briefly.
    By Unregistered in forum Central Heating Forum
    Replies: 5
    Last Post: 04-01-2016, 01:12 AM
  3. Boiler not firing
    By milkman in forum Central Heating Forum
    Replies: 5
    Last Post: 09-03-2009, 11:38 AM
  4. Grant Oil Boiler Firing, stopping firing etc?
    By jimk280 in forum Central Heating Forum
    Replies: 3
    Last Post: 08-12-2008, 11:21 AM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.