    Question TRV - Radiators either Hot or Cold

    Hi - I have a bedroom where the radiator is either blazing hot or cold. It is fitted with a TRV (I have tried several different ones to eliminate the TRV as the issue). When the TRV is set to "0" the radiator remains cold. At all other settings the radiator gets hot and stays hot even when the room temperature is 25 degrees +. I would expect that the TRV would at some stage close off the valve and the radiator would cool down especially at a low setting. If the valve is turned to "0" it does go off. As I said, this happens with different TRVs, some that are working normally that I have swapped from other radiators. So the radiator works, the valve works, the TRV works but the room temperature is never regulated by the combination. Is this a balancing issue?

  2. #2
    Super Moderator


    super-mod
    steveb's Avatar
    Join Date
    Nov 2007
    Location
    hythe hampshire
    Posts
    12,866
    Thanks
    631
    Thanked 1,218 Times in 1,182 Posts

    Default Re: TRV - Radiators either Hot or Cold

    when the trv is at "0" it is turned off so will not heat up at all. all the other settings will to a certain extent allow the radiator to heat up, 5 being fully open and each subsequent lower number closes the trv by a small amount while still being open.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please don't be offended when we ask for your details. diyers, bodgers, odd job people and have a go heroes need not apply



  3. #3
    Member
    Join Date
    Mar 2010
    Location
    West London
    Posts
    254
    Thanks
    5
    Thanked 38 Times in 36 Posts

    Default Re: TRV - Radiators either Hot or Cold

    TRV's sense the room temperature, but they sense it close to the valve itself. It is quite possible, for example, to have a TRV exposed to a cold draught, while the rest of the room is at the set temperature, and the TRV will not turn off.

  4. #4
    Member
    Join Date
    Nov 2016
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: TRV - Radiators either Hot or Cold

    Quote Originally Posted by steveb View Post
    when the trv is at "0" it is turned off so will not heat up at all. all the other settings will to a certain extent allow the radiator to heat up, 5 being fully open and each subsequent lower number closes the trv by a small amount while still being open.
    Thanks - That's what I thought. So is it that even at a setting of "0.5" there is enough flow through the radiator to maintain heat and during operation a TRV NEVER moves to a completely OFF state? In that case why do my other radiators not behave in this way? Is it possible that my lockshield valve is fully open and needs to be closed down a little?

  5. #5
    Member
    Join Date
    Nov 2016
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: TRV - Radiators either Hot or Cold

    Thanks - The valve is not in an exposed location, I have tested it with an electronic TRV (Energenie) which showed that the room temperature was 25 degrees as measured by the TRV. I had set a target temperature of 18 degrees, the software app with the e-TRV was telling me that it was cooling towards the target temperature yet the radiator remained hot until the heating timer on the boiler turned off. This is the same behaviour I see with a standard TRV.

  6. #6
    Member

    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    6,918
    Thanks
    231
    Thanked 779 Times in 760 Posts

    Default Re: TRV - Radiators either Hot or Cold

    Sounds like your TRV is faulty.
    When you turn it to 0, the rad is off, you say, so the head part must not be pushing the pin far enough down for some reason. Some valves I see doing same - the odd one of Peglers Terrier TRVs for example.
    If you have identical TRV elsewhere, swap the head part to test. If rad still keeps heating, get a plumber to replace entire valve

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Radiators keep going cold
    By Faith O-J in forum Central Heating Forum
    Replies: 6
    Last Post: 21-02-2016, 09:35 PM
  2. Replies: 14
    Last Post: 08-12-2010, 08:12 PM
  3. Boiler cutting out and cold cold radiators
    By greenhorn in forum Central Heating Forum
    Replies: 3
    Last Post: 05-01-2009, 10:05 AM
  4. Nearly cold radiators
    By MattBCardiff in forum Central Heating Forum
    Replies: 6
    Last Post: 05-11-2008, 04:27 AM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.