Faulty Thermostat or Floor?

Discuss Faulty Thermostat or Floor? at UK Plumbers Forums; I currently have an en-suite with an estat 761 thermostat controlling electric underfloor heating which seems to have failed (works for about 30 seconds before rebooting itself, giving me just ...
  1. #1
    Member
    Join Date
    Oct 2016
    Posts
    2
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Question Faulty Thermostat or Floor?

    I currently have an en-suite with an estat 761 thermostat controlling electric underfloor heating which seems to have failed (works for about 30 seconds before rebooting itself, giving me just enough time to set the date and time!).

    I'm looking for any input as to wether this is a stat issue or a problem with the heated floor itself? Is there a way to test this, perhaps checking resistance?

    I'm hoping to put a heat miser neo e underfloor heating stat instead but was wondering if the temperature probe would be interchangeable as the current one is obviously already in situ. Does anyone have any experience with this? Obviously don't want to change the stat out if the floor is broken anyhow.

    Thanks

    Barry

  2. #2
    Plumbers Arms member
    Chalked's Avatar
    Join Date
    Jan 2013
    Posts
    3,814
    Thanks
    89
    Thanked 452 Times in 440 Posts

    Default Re: Faulty Thermostat or Floor?

    You will need yo disconnect the thermostat and test the resistance through the element wires. The manufacturer will have the correct readings for you. If you want to change yo a neo stat, it will need to be a thermostat with compatible resistance to thiers. If you tell Heatmiser what your manufacturer is, they should tell you if it is comparable. (Tbh most are)
    Uheat – Wojtek likes this.

  3. The Following User Says Thank You to Chalked For This Useful Post:


  4. #3
    Member
    Join Date
    Oct 2016
    Posts
    2
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: Faulty Thermostat or Floor?

    Thanks for the speedy reply. Tricky thing is, I've only moved into this property recently and the floor was already down, so no idea how I will tell what the manufacturer is. I'll see if I can get some readings anyhow and post them to see if there are any views.

  5. #4
    Plumbers Arms member
    Chalked's Avatar
    Join Date
    Jan 2013
    Posts
    3,814
    Thanks
    89
    Thanked 452 Times in 440 Posts

    Default Re: Faulty Thermostat or Floor?

    Basically, if you get a dead short it's kaput!

  6. #5
    ** UKPF Sponsor **
    Join Date
    Jul 2016
    Posts
    71
    Thanks
    0
    Thanked 5 Times in 5 Posts

    Default Re: Faulty Thermostat or Floor?

    Hi there,

    I've just checked it and it's an Aube thermostat (they brand them differently for some companies hence yours is called Estat).

    Floor sensor resistance should be 10k Ohm @ 25 deg C. If temperature will be lower resistance will go up.

    Please check your floor sensor resistance with Multimiter and if it's going to be close to the figure above then the floor sensor is fine.
    Heatmiser floor sensor resistance is exactly the same so you will be ok to swap the controllers without replacing the floor sensors (as long as the exsiting one isn't faulty).

    I can supply Neostat for £66.79 incl VAt (including your 5% forus discount).

    Thank you.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. faulty thermostat on programmer
    By simoneve in forum Plumbing Forum
    Replies: 8
    Last Post: 03-12-2015, 07:03 PM
  2. Can a thermostat with a click still be faulty?
    By reallybrokendav in forum Central Heating Forum
    Replies: 4
    Last Post: 28-10-2011, 05:05 PM
  3. Room Thermostat Faulty?
    By joben1 in forum Central Heating Forum
    Replies: 5
    Last Post: 21-10-2011, 03:24 PM
  4. Replies: 6
    Last Post: 30-01-2011, 07:00 PM
  5. Faulty boiler thermostat?
    By Connor Williams in forum Plumbing Forum
    Replies: 1
    Last Post: 09-12-2009, 07:16 PM

Visitors found this page by searching for:

estat 761

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.