Got a problem with a Worcester combi not firing in the morning from cold.

Boiler approx 14 years old.

Pressing the reset button once only gets the boiler to fire OK.

The fault is intermittent and happens about once per week.

The fault is not connected with frosty weather.

The tank had been contaminated with water and there was dross in the oil line. Flushed line and emptied water out.

Changed pump and solenoid coil, made little difference.

Any suggestions?
 
Have you tested the resistance on the Limit stats? if they are greater than 1 ohms they have a short circuit which could do this.
check aps aswell and thermistors.
clean venturi

Does it have a programmable room stat? i'd check the connections on that.

but hey i am not an oily engineer.
 
Capacitor? Losing charge/whatever it is after a cold spell?
 
I'd try a new capacitor.

But I did have one a couple of years ago, intermittent lockout on a morning and it was the transformer.
 
Last edited:
Could be a micro leak on the oil line allowing air to build up in the line whilst the boiler is off over night then clearing after the first fire until the next extended off period
 
First I would check the motor starts on the split second every time, (give it loads of starts to test, with your ear near the burner) - any slight hesitancy & I would think capacitor.
Normally Control box does that, once in a while lockout, but photocells can do weird things.
As has been suggested, check the transformer is making a strong & constant spark.
 
gonna have to make you an honary oily, best change your monicker if your moderating this sub forum omho :)
oily gas man? looking into oftec and training in the next few months lots of farms near me and the resident oil mans retiring
 
farmers dont get the likes of us to service their boilers, its diy for them
 
The line is under pressure (tank higher than boiler).

Will try control box and photocell first and report back.

The burner is going to lockout so nothing to do with stats.
 
Over airing could be a possibilty but yeah I'd also try a new photo cell
 
Could be overaired but you would have already checked the flue gases, I would check the transformer, the EB1,s give the same symptoms, sometimes you can see the bulge in the casing when they are statrting to go.
 
OK I'll come armed with a control unit, photocell and EB1. If that doesn't sort it I'm really scratching my head!
 
Could be overaired but you would have already checked the flue gases, I would check the transformer, the EB1,s give the same symptoms, sometimes you can see the bulge in the casing when they are statrting to go.


And they stink!
 
My experience is if the EB1 goes, change the control box aswell, its often the box causing the damage.
 
Status
Not open for further replies.

Reply to Worcester Combi not firing in morning in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock