I have a Worcester Bosch Greenstar 18Ri regular boiler installed within my garage.

There is also a Honeywell T4360 Frost Thermostat installed just above and to the left of the boiler.

The problem I was having was that the Frost Thermostat was kicking in in cold weather and firing up the boiler for very long periods of time which in turn was heating up the house.

After reading up on the internet, I did find out that if a frost stat is used that a pipestat should be used in conjunction to turn the boiler off once the pipework temperature is high enough to prevent the pipes from freezing, which one is not currently fitted.

From reading my boilers user manual it states that there is already an inbuilt frost protection function within the boiler. So for a quick fix we temporarily disconnected the power from the frost stat, to prevent over heating as it was becoming a major problem.

So wondered if anyone could confirm the following queries.

1.
Does my boiler actually need an additional frost stat and pipe stat?
As the boiler has its own frost protection function, or should it have both frost/pipe stat and the boilers inbuilt protection active?

2.
If the frost stat is still wired into the boiler, but does not have power going to the frost stat itself, will this prevent the boilers inbuilt frost prevention function from activating?

3.
As you can see from the snippet from my boilers user manual this is how the inbuilt frost protection function works:

If the temperature within the boiler falls below 8°C the pump will run to circulate water and prevent the system freezing.

If the temperature does not rise to 9°C within 30 minutes of the pump operating, the boiler will fire up to provide heat to bring the temperature up.

If the temperature within the boiler falls below 5°C the boiler will fire, bringing the boiler temperature up to 12°C to avoid the possibility of the system freezing.

This process will be repeated until such time that the boiler temperature does not drop below 5°C.



Last night the outside temperature dropped to -1.6C (about 4.0C in the garage) but I did not hear the central heating pump come on, so I am not sure if the boilers inbuilt frost protection is working or not.

FYI. the heating in the house was off over night, it turned off at 23:00. So there was no heating demand throughout the night.

So I would have expected that the frost function would have activated as the temperature in the garage was less than 9.0C.

Would the temperature within the boiler have stayed above 9.0C all night if the heating was turned off at 23:00? I was up until 2:30 in the morning (in bed), and never heard the pump come on. Only until 5:00am when the timer was set to turn the Central Heating back on.


Also, when the above mentions that 'the pump will run to circulate water' would this be an 'internal pump' within the boiler, or the pump which is located within my airing-cupboard? Just so I know if I should be listening for the one in the airing-cupboard or not.

Any advice would be appreciated.
 
As your boiler has no integral pump, it needs an external frost and pipe thermostat. These are wired in series. Both then need to be activated to bring th boiler on.
Your boiler does have a frost thermostat, but it looks like the pump is not wired back to the boiler.
 
Thanks for your reply and info.

I will get a pipe stat fitted and reconnect the frost stat as soon as
I can. As this won't be for a couple of days, could you advise
on my previous point '2', below.

2.
If the 'frost stat' is still wired into the boiler, but does not have power going to the 'frost stat' itself, will this prevent the boilers inbuilt frost prevention function from activating?

As I would like to make sure the boiler is still protected
in this cold spell of weather.
 
Status
Not open for further replies.

Reply to Worcester Bosch Greenstar 18Ri Frost protection in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
172
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
207
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
200
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
144
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
203
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock