Hi everyone,
Recently my central heating system has developed a problem. When the system is on and just calling for hot water the boiler lights and runs for 1 to 2 mins and gradually starts kettling before cutting out. Once it has cooled a bit it cycles and does the same again.
If it is calling for heating it runs just fine and the radiators get nice and warm. The system has a gravity fed hot water tank in the roof and pumped rads.
I think there must be a blockage or air in the gravity feed to the hot water tank stopping the flow. Does anyone have any experience of a problem like this?
For the moment I have left the whole system turned off, relying on the immersion heater, but I'm going to need it soon with autumn coming.
Thanks for any advice,
Andy
 
TBH I would be looking to convert the hot water to pumped as well
 
Check, or take a photo of, the side of the cylinder where the pipes from the boiler connect, there maybe an air bleed on the upper one.
 
Hi everyone,
Recently my central heating system has developed a problem. When the system is on and just calling for hot water the boiler lights and runs for 1 to 2 mins and gradually starts kettling before cutting out. Once it has cooled a bit it cycles and does the same again.
If it is calling for heating it runs just fine and the radiators get nice and warm. The system has a gravity fed hot water tank in the roof and pumped rads.
I think there must be a blockage or air in the gravity feed to the hot water tank stopping the flow. Does anyone have any experience of a problem like this?
For the moment I have left the whole system turned off, relying on the immersion heater, but I'm going to need it soon with autumn coming.
Thanks for any advice,
Andy
Does it cut out on the control-stat or the limit-stat? The limit-stat usually needs manual reset, but if it is cutting out on that, the control-stat could be the problem. In HW only mode the heat transfer into the cylinder will be less than boiler output, so if the control-stat doesn't stop it the water gets too hot and kettling starts. In CH mode it's OK because the rads dissipate the heat so it doesn't reach control-stat setting before it stops on the room-stat.
 
Thank you for the replies.
I've had another look tonight. There is no air bleed on the water cylinder where the boiler connects, but that is where the vent take off is, so I guess that acts as an air bleed for the coil?
The boiler cuts out on the control stat. If I set the boiler temp control to low and it trips I can get it to restart by turning the temp control, so I assume the control stat is OK?
 
Thank you for the replies.
I've had another look tonight. There is no air bleed on the water cylinder where the boiler connects, but that is where the vent take off is, so I guess that acts as an air bleed for the coil?
The boiler cuts out on the control stat. If I set the boiler temp control to low and it trips I can get it to restart by turning the temp control, so I assume the control stat is OK?
It still sounds as if the heat isn't being dissipated when in HW mode, though why the problem has only just come up is a puzzle.
You didn't confirm whether the HW primary is gravity or pumped, you said "The system has a gravity fed hot water tank in the roof and pumped rads" but that tank is on the secondary (taps) side.
Are the pipes very hot before the kettling starts? If so you might get away with turning the control-stat down a touch. Unlikely to affect the CH performance, as I said in #4.
If it is gravity HW my guess it's an old system, maybe there's sludge build-up in the pipes.
 
Thanks fixitflav, the system was left idle for a bit in the hot weather, so maybe that wasn't a good thing, and that is why it has started playing up.
Sorry I wasn't clear, only the rads are pumped, the hot water primary is gravity. Because it cuts out so quickly when set to HW only, the tap water doesn't get heated much, it gets a bit warmer in CH mode, but not really enough.
It is an old system and I think you're right there is sludge build up, although it was cleaned and flushed 18 months ago. Think it's time to do it again.
Thanks to everyone for the help.
Andy
 
Last job I had with those symptoms had 2 issues.
Blocked pipework going into the cylinder coil and a broken 2 port valve.
System had been run for at least a year with the broken port valve as they said HW only setting still heated rads, so the least used route for the water ended up blocking over that time.
After replacing the 2 port the boiler would kettle and cut out on HW only setting.
The blockage was around the air separator, the area where the expansion pipe is teed into the pipework, that's a common area for a blockage that could give the symptoms you describe.
You can test the pipework for blockages with a strong magnet, any pull at all shows a blockage. If it is blocked there the best solution is to cut out that section of pipework out and replace it.
Would be worth getting a magnetic filter installed while the work's being done, and make sure the system is inhibited.
 
Thanks fixitflav, the system was left idle for a bit in the hot weather, so maybe that wasn't a good thing, and that is why it has started playing up.
Sorry I wasn't clear, only the rads are pumped, the hot water primary is gravity. Because it cuts out so quickly when set to HW only, the tap water doesn't get heated much, it gets a bit warmer in CH mode, but not really enough.
It is an old system and I think you're right there is sludge build up, although it was cleaned and flushed 18 months ago. Think it's time to do it again.
Thanks to everyone for the help.
Andy
With gravity HW, you can only have HW only, or HW + CH, not CH only. Wiring diagram below (I forgot to label the switches in the timer, but it's self-explanatory).

upload_2018-9-5_18-4-28.png

But what you could do is rewire it as the dotted line. Then the boiler only fires when the pump is running, ie only in CH mode. That would get rid of the kettling. You would need to use the immersion for hot water, but you've been doing that anyway.
 
OK, thanks for that, I'll give it some thought. Not sure how often we use CH and don't need hot water. I guess it's always been like that so we never thought about it, we always seem to need hot water ...
 
OK, thanks for that, I'll give it some thought. Not sure how often we use CH and don't need hot water. I guess it's always been like that so we never thought about it, we always seem to need hot water .
Agreed, you would have to use the immersion for hot water. I assume there is no cylinder stat, or any automatic valves (in the cylinder circuit)?
As it is, any time the whole system is available on the timer, if the room-stat is satisfied the pump doesn't run, so kettling will happen. The revised wiring avoids that.
 
Agreed, you would have to use the immersion for hot water. I assume there is no cylinder stat, or any automatic valves (in the cylinder circuit)?
As it is, any time the whole system is available on the timer, if the room-stat is satisfied the pump doesn't run, so kettling will happen. The revised wiring avoids that.
To add to that - if you do this mod I would also close a valve in the gravity circuit, otherwise you could get some flow through the cylinder from the pump, cooling it before things get up to temperature. So you'd be partly heating the house with electric, which you don't want.
 

Reply to Vented hot water problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
164
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
332
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
266
Hi, I'm looking for a water pump to pump water from a storage tank at a constant 3 bar pressure. It's at a campsite I run that's at the bottom of a long, steep hill. We struggle with very high and often fluctuating (around 7 bar) water pressure, which wreaks havoc with our water heaters. I've...
Replies
2
Views
69
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
386
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock