Hello,
I have a Combi Boiler (Vaillant Ecotec Plus 428) and an Unvented Cylinder (Vaillant uniSTOR VIH GB 180s). Since yesterday we have no more hot water in the house, it comes out cold or luke warm. But the heating works fine.

When a hot water tap is fully opened, the boiler reads S.30 (no heating demand from external source). I have run the diagnostic, and the hot water flow sensor (D.36) reads 0 l/min as well.

My question is could the issue be most likely with the boiler (aqua sensor..) or the cylinder (valve..) ?
I'm wondering if I should call an unvented qualified or a gas engineer.

Thank you for your help.
David.
 
Last edited:
Issue probably with zone valve to cylinder, you need an unvented g3 engineer to fix just use immersion temporarily
 
Thank you for the reply. It is actually the Ecotec Plus 428.
Can I set up the immersion heater manually? I couldnt see a switch on the tank.
 
Issue probably with zone valve to cylinder, you need an unvented g3 engineer to fix just use immersion temporarily

Hi Alex,
I've attached a picture of what I believe to be the Zone Valve of my cylinder. I see there's a 'Manual Open' mode.
Would you know how to use it to troubleshoot perhaps?
Thank you,

plumbinn.co.uk/prodimg/80/honeywell-v4073a-zone-valve.jpg
 
Last edited:
Post some actual pictures, thats the wrong sort of valve for an unvented cylinder
Or post your loaction on here, you may need a gas safe registered plumber with unvented (G3) ticket
 
Post some actual pictures, thats the wrong sort of valve for an unvented cylinder
Or post your loaction on here, you may need a gas safe registered plumber with unvented (G3) ticket
 
Post some actual pictures, thats the wrong sort of valve for an unvented cylinder
Or post your loaction on here, you may need a gas safe registered plumber with unvented (G3) ticket

I've attached a picture of the actual valve.
Thank you,

20170120_174532.jpg
 
I confirm that when the programmer is on (from 6am to 8am) the boiler receives no heat demand (code S.30) so does not ignite.

But later today when I turned on the programmer, the boiler did ignite, I saw the zone valve opening and the pipe to the cylinder getting hot. But just for a couple of minutes, nothing after that.

Is the issue more likely with the programmer or the valve itself (Tower 2port VAL222MV)?

Programmer.jpg
Boiler.jpg
Tower_Zone_Valve_back.jpg

PS: There's hot water when I use the electrical immersion heater.
 
Last edited:
If heating is working, nothing wrong with boiler. G3 qualified needed. Suspect safety cutout on cylinder. Definitely not a DIY. Must not be bypassed.
 
If heating is working, nothing wrong with boiler. G3 qualified needed. Suspect safety cutout on cylinder. Definitely not a DIY. Must not be bypassed.

Thanks for your reply. So does the cylinder cutout close the zone valve AND stop the boiler? That would explain why I saw the boiler stopped after few minutes.

I see there is a thermal cutout reset button, but I'll contact a G3 qualified. Thank you.
 
Status
Not open for further replies.

Reply to Vaillant Combi Boiler Unvented Cylinder - Hot water problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
231
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...