Discuss Vaillant boiler with a possible poltergeist! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
20
Vaillant EcoTec 931 R1 47-044-32
I have worked in this industry for over 40 years and never experienced this. One of the issues being that the boiler is fitted in a property that I own and rent out. Apologies for the length of this post but it is a long and involved story and if any of you have experienced this or can suggest any explanation I would be grateful.
The tenant contacted me on a few occasions stating the boiler was loosing pressure and failing to F75. This was happening at random times, sometimes a few days apart and sometimes a month apart.
I inspected the boiler and system and there was no evidence of leaks.
Tenant goes away for Christmas, Ahah! my opportunity to find out what is going on. I checked the fault history and the last 10 faults were F75. So the system obviously was loosing pressure.
Thinking the PRV may be worn I switched the boiler off and attached a zip lock bag to the PRV pipe outlet outside. (tight enough to catch any spills but loose enough to be blown off if the PRV dumped completely). Checked after two days no pressure loss, no water in the bag. I removed the condensate pipe from the heat exchanger and left it open above a piece of paper to check if the heat exchanger was leaking internally, no joy. Pipe re attached.
Next with the aid of a mirror and torch (access underneath is less than manufacturers specs) I discovered that the flow and return valves could be operated with an allen key as I had been struggling to try and close them with a stubby screwdriver.
System isolated, pressure marked on the gauge. I will find out if the leak is on the system or the boiler. Returned two days later to check on progress. Water in the zip lock bag outside (goody), but when I went inside the pressure gauge was straining passed the red section. There was water dripping from the case. I removed the case, lowered the pressure and saw that the water was coming from the expansion vessel seam.
From this I deduced that
1. The PRV was not operating correctly as it should have kept bleeding the pressure off above 3bar (the gauge on the Vaillant doesn't have any figures as you will be aware)
2. The expansion vessel needed replacing
3. The plate heat exchanger must have failed to cause the increase in pressure.
As I am writing this I realise that the integral filling loop could also have caused the increase in pressure, but lets leave that for now.
I reduced the system pressure and dried the case out checking no water had gotten into the electrics. I turned the boiler on but it refused to fire showing F32. After several attempts the result was the same, so as the instructions were not much help I called Vaillant's technical help line where the lady I spoke to took me through the necessary electrical checks and readings to ascertain where the issue was. During these tests the damned boiler decided to start working with no obvious reason. The Vaillant tech suggested it might have been a loose connection, but I am not convinced.
After a visit to the merchants and lightening my wallet by two hundred pounds, I returned to fit the parts. (PRV, expension vessel, plate heat exchanger).
I isolated the cold supply and drained the boiler (still isolated from the system). I changed the parts and went to reestablish the cold supply by turning the valve back on, but there was no sound of water as expected. No water coming from the hot tap (the cold was working). I messed with this for ages but to no avail. I decided to remove the valve for inspection but that was going to be difficult due to the lack of clearance underneath the boiler. I turned the main stop tap off to remove the valve but then I stopped. (When changing a plate heat exchanger I always turn on the cold water first and check for leaks so that I know if a leak does occur which side it is on). I remembered that the system was still isolated. I turned on the system valves and the system pressure rose slightly as I would have expected. I turned back on the cold mains and water started flowing through the hot tap. I pressurised the system checked the boiler as I always do and waited for the system to get up to temperature. Once I was satisfied the heating and water were working I packed my tools and ran away.
So far (three days) there has been no further issue but I am not completely convinced that this is the end of the saga.
Any suggestions or insight into what I have experienced would be gratefully received.
Thanks
 
I've changed loads of the cold water Inlet valves on Vaillant boilers (ecotec) as they pass water into the boiler when off and over pressureise it
 
I've changed loads of the cold water Inlet valves on Vaillant boilers (ecotec) as they pass water into the boiler when off and over pressureise it
Thanks for your input. I think I will get a replacement cold water valve to change at a future point as it is obviously giving some problems.
However when the boiler over pressurised the cold valve was in the on position it was only the flow and return valves to the heating that were turned off. So I ruled this out as the reason.
We are now five days in and so far (touch-wood) no pressure loss. Fingers crossed. But I would still be interested in everybody’s input as there are so many anomalies.
Thanks again for your input.
 
The ecoTec internal filling loop is very expensive and not fit for perpose as so often both valves let-by, if possible cap it off and fit an external one.
 
All I'd say is that working in this industry even after 40 years there is always another first, to forever keep an open mind, because otherwise its time to give in. Sounds perfectly ok.
 
Thanks Vee
You are absolutely right. Sometimes experience can blinker you to new possibilities.
The boiler has held its pressure for a month until last Wednesday.
Due to family illness I haven't had a chance to fit the new cold fill valves that I have bought. I am tempted to monitor it for the next few weeks and see what happens.
Thanks again for your input.
 
Status
Not open for further replies.

Reply to Vaillant boiler with a possible poltergeist! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also have an UFH zone in the kitchen. Near the boiler I have 2 port valves which control this part of the system. The boiler has been loosing pressure...
Replies
1
Views
290
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem could be. We have a biomass boiler and stratification tank set up and recently had an issue with boiler pressure dropping off when the system was cold...
Replies
9
Views
344
Hi I have a baxi duotec combi boiler that every day or other day needs topping up as pressure drops below 0.5bar. When fired up it can reach OVER 2.5bar also whilst running CH. Is this more than likely a flat Expansion Vessel that needs inflating or could there be other possible causes if...
Replies
2
Views
346
Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd, London. Job Description: Problem: The boiler is not providing heating under normal conditions, although hot water supply is fine. Interestingly...
Replies
1
Views
386
Hi, I was hoping to replace an old system boiler with a Vaillant Ecotec Exclusive 627 system boiler, thats the one with the diverter valve so no need for zone valves, controling it with a V-Smart and a VR10. I've spoken to Vaillant Tech and they said you cannot use the VR10 with a vented...
Replies
0
Views
109
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock