Need some advice and help! (I am not a plumber so will try and give as much info as i can)
I have a room in my house with 2 loops of ufh in it. They are controlled by the same thermostat.
They have separate actuators at the manifold as well.

When the heating comes on one actuator opens fully and warms its half of the floor, while the other only seems to open half way (looking at the gauge level on the actuator) and only half warms the floor?

The pins are not sticking as i can take actuator off and the pin moves freely up and down fully.

Is this a problem with the actuator, or do I need to adjust the flow of that zone?

Thanks for any help in advance
 
Is this a new problem or one you've adopted with a house purchase? Are both actuator pins moving the same distance and freely?
What setting is the pump on?
It could be a case of balancing the loops or air locks providing the above is correct.
Are both loops covered by the same flooring?
 
Is this a new problem or one you've adopted with a house purchase? Are both actuator pins moving the same distance and freely?
What setting is the pump on?
It could be a case of balancing the loops or air locks providing the above is correct.
Are both loops covered by the same flooring?

Hi, thanks for your response.
Its a house i built - never really paid attention before - only come up as I have had to change other room thermostats so could have been like this from the start?
Pins are all moving the same distance.
Dont know the setting on the pump.
Both loops are in the same room with the same floor.

Is there a way i can test the actuator is opening ok? ie swapping it to another circuit on the manifold?

Thanks
 
Hi, thanks for your response.
Its a house i built - never really paid attention before - only come up as I have had to change other room thermostats so could have been like this from the start?
Pins are all moving the same distance.
Dont know the setting on the pump.
Both loops are in the same room with the same floor.

Is there a way i can test the actuator is opening ok? ie swapping it to another circuit on the manifold?

Thanks

Hi. As you're a new member your posts have to be verified, hence why I'm only just seeing it.
You could isolate the electrical supply to the system and swap the actuator heads then resupply power to prove function, if you're competent with a multimeter you could check signal as well.
I suspect this is a balancing issue and fine tuning the flow rates is required.
If you can see the UFH pump which should be on or near the manifold then check to see what setting it's on.
 
Is it just a 2 port manifold with this one room on? If so you can just remove the actuators and leave the pin valves open constantly. The system will then go on and off when the pump stops spinning.

If you have more then 2 port you'll most likely need to purchase a new actuator. We supply these for £19.20 IncVAT.

 

Reply to ufh actuator advice!! in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
138
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
192
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
245
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock