My faithful S410 F4 has all but given up the ghost and it is time to replace it. It's done well - 37 years of service, so I'm not complaining!

It features a pre-standardisation back plate, so I wanted to run a check by some kind soul before I replace it with the Drayton LP522 that's sitting on my dining table...

My CH system is gravity fed; boiler, pump, thermostat and motorised valve. All very simple.

I downloaded the 410 wiring details from Sangamo, and the details for the Drayton are 'straight out of the box':

F410 Terminal LP522 Terminal
1 3
3 L
4 N
5 N
8 4

I'm happy with most of this - the only one I'm not 100% confident about is F410 terminal 5 going to the N...

Thanks to those who took the time to read this,

Chris
 
My faithful S410 F4 has all but given up the ghost and it is time to replace it. It's done well - 37 years of service, so I'm not complaining!

It features a pre-standardisation back plate, so I wanted to run a check by some kind soul before I replace it with the Drayton LP522 that's sitting on my dining table...

My CH system is gravity fed; boiler, pump, thermostat and motorised valve. All very simple.

I downloaded the 410 wiring details from Sangamo, and the details for the Drayton are 'straight out of the box':

F410 Terminal LP522 Terminal
1 3
3 L
4 N
5 N
8 4

I'm happy with most of this - the only one I'm not 100% confident about is F410 terminal 5 going to the N...

upload_2017-5-14_12-30-1.png


Thanks to those who took the time to read this,

Chris

Added the S410 F4 wiring diagram!
 
After some careful checking and double checking (including advice from an electrician neighbour) I've successfully installed the LP522. All that's left to complete is the programming!

The wiring converts as follows:

F410 terminal 1 is wired to terminal 3 on the LP522
F410 terminal 2 should have no wiring
F410 terminal 3 is wired to L on the LP522
F410 terminals 4 and 5 are wired to N on the LP522
F410 terminal 6 (which is a link wired to terminal 1) can be discarded
F410 terminal 7 should have no wiring
F410 terminal 8 is wired to terminal 4 on the LP522

I hope this helps someone, somewhere. There's nothing worse than a helpful looking thread in a forum that turns into a dead end!
 
Status
Not open for further replies.

Reply to Sangamo 410 F4 wiring check in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
306
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
230
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
219
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock