Discuss Pressure drops when 650 litre buffer tank is filled with water but no drop with air in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Re: Pressure drops when 650 litre buffer tank is filled with water but no drop with a
Wierd !
Air will obviously contract a lot. So the temperature of air put in, once stabilised will drastically change pressure just like testing a large gas installation but you've thought of that ?
I am not sure I follow what you are saying. How is that relevant?
Please read the whole thread.
I have also you haven't tested the whole install only sections which is not good enough
Only two sections dropped pressure so it was those two sections that were most intensively tested.
To be clear, the pressure drops occured when the system was filled with water. The sections that were losing pressure stopped losing pressure when that water was replaced with pressurised air. When that pressurised air was replaced with water there continued to be no pressure drops.
For a start you can't pressure test with air anything over 0.5 bar needs to be water
Well, the reason for testing with air was that there were no visible water leaks. So air was tried to see if bubbles appeared in the exposed underground pipework that was covered with water.
The result was unexpected. No more pressure drops!
I've had fittings tested on air and no leaks come to water test leak so get your plumber to test the whole system to 10 bar water and leave it for half a day (if you can't 2-3 hours will do)
soon see what's at fault
If the air you pump into the system is, for example at 21 deg or room temp and you push it into buried pipes, that are say 12deg ( in the ground), the air will contract a lot as the temperature stabilises.
This will give the impression that you're loosing pressure when you're not.
i don't know if they waited when testing with air or give it up straight away.
To me it sounds like that's what happened. You said you had no leak when filled with water !
Unfortunalely you have not understood what I have written in this thread. Your comments are therefore irrelevant.
There was no pressure drop when air was in the system, nor when the air was replaced with water.
The testing with air took place over several days.
Well Trevor,
I have read the thread and commented throughout.
I am only trying to offer suggestions to the ridiculous sounding situation you're in.
It has gone on a while now and I admit I've kind of lost where we're up to.
For the life in me, I don't understand why your installer hasn't solved this by now. It is extremely difficult reading threads and other people's posts, in trying to solve a problem like this
I.e. Not physically dealing with it.
All that said, I understand that you think my comments are 'irrelevant '.
I wish you luck with this. I hope you get to the bottom of it soon.
Well Trevor,
Thanks for taking the trouble to respond. It was only your last comments that I felt were irrelevant.
The installer has not solved the cause of the pressure drops. They are as puzzled as everyone else.
Time to get the manufacturer of the pipe system involved.
Uponor were involved a long time ago. They say that their pipe does not leak. But if a leak is found they would investigate. No leak has been found.
Does the system have automatic air vents. Is the underground pipe dead level?
Yes there are some automatic air vents, but the red plastic caps are screwed closed.
No, the underground pipe is not dead level.
Reply to Pressure drops when 650 litre buffer tank is filled with water but no drop with air in the Plumbing Jobs | The Job-board area at PlumbersForums.net