Sue66

Gas Engineer
Messages
41
Hi I'm newly qualified. Why would a boiler be 23mb at the meter on working pressure and 19mb at boiler inlet pressure and 14mb burner pressure. This is fine as per the MIs but i thought there was only supposed to be a 1mb drop.
 
Restriction of the gas valve you can loose 4-5 mbar on a gas valve

Also some burners are reduced in pressure and you can set them (not the same as inlet)

But inlet pressure seems low you done a quick gas pipework calc ?
 
There is about 4 meters of pipework to boiler mostly in 22mm. I thought it was low. I have gas safe inspecting me so I'm trying to get my facts straight. Its a Worcester 28i RSF. The other wierd thing is the co co2 ratio is 0.0003 and the MIs say it should be 0.003-0.007. Its really low. The gas rate is perfect though.
 
And Shaun thank you you are right the MIs say that it's preset to about 13.5mb so that bit is bang on.
 
would do it old school and just have a look at the ppm on the fga

(old school)

flame picture, burner pressure, gas rate

and gas pipework sounds ok, other than the inlet filter to the gas valve being slightly blocked it should be ok
 
Would it also be worth mentioning there is a 2mb drop off pressure on the installation that is apparently untraceable. Within the 4mb permissible limit with no smell of gas.
 
what meter is installed?

and did you isolate the boiler?
 
G4 meter.Yes i tried isolating the boiler and it made no difference there is a 22mm pipe that Ts off and goes underground to the cooker. I have yet to cap off either direction to find out which route is responsible for said drop in mb.
 
any gas fires?
 
No gas fires just the cooker and the boiler upstairs. Actually it goes underground in 28mm comes out the wall behind the cooker.
 
Last edited:
1499114266577158964415.jpg
 
looks like steel pipework in the ground
 
Ok that does not sound reassuring but helpful all the same. Ill wait till the gas safe guy comes and then fix it. I don't really know if he can penalise me for having a numpty gas installation prior to my qualifying.
 
aslong as you have an ok drop you will be fine and steel pipework is better than copper in concrete
 
Ok thanks mate. These inspections are scary when your newly qualified and i keep finding abnormal stuff lol. Just my luck!
 
You will be fine there only there to check your working safely
 
Status
Not open for further replies.

Reply to Old non condensing boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I've got a non condensing Glowworm Ultimate with gravity tank and hot Water tank in a 4 bed house. 11 radiators 1 double 1400mm length 1 P+ 1400mm length 2 P+ 400mm length 7 singles 400mm 1 mains shower average water pressure Any recommendations on combi boiler and KW? Boiler budget...
Replies
7
Views
481
I have a "Firebird Envirogreen Condensing Combi Oil Boiler 26kW" a part has went and I can't find it anywhere, I was at every plumbers merchant near me but they all need to ring Firebird who are closed till next week. I wonder if anyone can help me find this part please? It's a pressure sensor...
Replies
2
Views
371
Hi Can you help me determine if my new Navien lcb700 lsx is working as expected? I got the Navien oil boiler installed to replaced an old firebird boiler. The new boiler is a condensing oil boiler and I’m not sure if this is working as expected. I’ve a 300 L water cylinder and after one hour...
Replies
22
Views
2K
Hi, I have an 20yrs heat only potterton 50e boiler with 196x old house - suspended floor - designer radiators, open vent system and hot water cylinder on first floor with two motorised valves and stat. I want to replace the boiler with minimal cost and max efficiency so thinking of replacing...
Replies
1
Views
581
I've a client with a rusty 20yr+ old Certikin 180 (44kw) oil pool boiler that needs changing. Certikins replacement looks like it is the exact same boiler. It has a riello r40 burner and non condensing 85% efficient boiler... Oftec say it wouldn't be compliant and would have to contact Building...
Replies
2
Views
426
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock