Had a problem with an oil burner today. Burner going to lockout and I found that the control unit wasn't sending power to the electrodes. Replaced it (Honeywell TF832.3) and found that the ignitor worked but the solenoid wasnt getting triggered. However if you turn the thermostat down then up again, the silenoid clicks open and the boiler fires. On checking the voltage to the solenoid coil, at the beginning you get about 60v which doesnt trigger the solenoid. FLicking the thermostat off and on gives you 240v.

I am presuming there is a fault with the control box. Anyone ever had this happen to them?
 
Last edited:
I have had the same problem / it turned out to be a lack of combustion air (inlet)
I took the balanced flue pipe connection off and it was ok
It was a new install and the supplied flue was not the correct one for the burner rating
 
Never had that one before, sounds like something sticking in the new control box. Take it that it was a new out of the box control box? Wouldn't be the first time though that a 'new' part was faulty. Caught me out a few times in the past thinking that 'new', 'out of the box' can't possibly be faulty. :)
 
I have had the same problem / it turned out to be a lack of combustion air (inlet)
I took the balanced flue pipe connection off and it was ok
It was a new install and the supplied flue was not the correct one for the burner rating

I'm not getting the solenoid to trigger at all to let oil in - don't get as far as oil coming in and not igniting througn insufficient air. Will be onto the suppliers in the morning.
 
I don't have a magnet to try it witn but I assume it will. Basically it's not getting enough voltage at the start to work the solenoid. When you click the stat off and on again it seems to get full voltage and runs the burner until the boiler reaches the thermostat setting and cuts off.
 
could the fault possibly be with the stat? wot voltage are you gettting comimg out of the stat when your only getting 60v at the sol' valve
 
I don't have a magnet to try it witn but I assume it will. Basically it's not getting enough voltage at the start to work the solenoid. When you click the stat off and on again it seems to get full voltage and runs the burner until the boiler reaches the thermostat setting and cuts off.

Try the Air inlet hose as it suprised me too as well as the manufacturer
 
I have known engineers had a problem with the control box base with a hairline crack causing problems, it sounds electrical, obviously a pain to re wire but worth a go
 
Was neither of what I thought - turned out to be a bad contact on the wiring to the photocell.
 
Well found!! Bet you were chuffed with that!

Many thanks for posting the solution - had me stumped (but then many oil burner problems do - in fairness to me though, I've yet to be defeated.)
 
nasty one, not come across that before. I'll have to remember that!
 
Status
Not open for further replies.

Reply to Oil burner problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
147
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock