J

Jason brad

I've had a new Firebird combi oil boiler fitted and the hot water pressure is low( in fact it's terrible)..the cold water pressure is good and I can't find any leaks and loose no pressure. Please help. Thanks alot
 
The hot water pressure is terrible?, do you mean the hot flow rate is very poor but the flow rate is OK but too cold if a hot tap is opened fully?
What is the Firebird power output.
 
Should be the same as the mains pressure
 
20 kw output. Thanks
20kw should give a hot tap temperature of 40C at a flow rate of 14LPM or 7LPM at 60C, can you just open a hot tap fully and see how long it takes to fill a 2 litre container or any sized container and compare this with the time taken to fill the same container from a cold tap.
 

Reply to Low hot water pressure in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
153
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
140
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
140
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
232
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
208
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock