  1. sessi

    sessi Guest

    Hello

    I wonder if anyone could throw any light on a very tiresome problem. We have the above oil fired boiler. The engineer has been out and seemingly tried everything. He has serviced it, replaced the injector leads, altered the power thingy lol to the burner, and goodness knows what else.

    After altering the injector, it did fire up on it's own for a day, and now is back to having to manually press the reset button. I am sure he is as frustrated as we are, but now the cold weather is coming I really don't want to have to keep doing this.

    Another thing, today, when I pressed the reset button it looked like a little flame came out of the box surrounding the button, which is worrying..

    Any ideas???

    Thank you for your time.
     
  2. kimbo

    kimbo Guest

    It is always difficult to diagnose a fault without actually being there. We need to know exactly what happens when the boiler locks out, does it happen when you are there or does it happen overnight etc. The engineer has obviously checked certain things but things to check would be partially blocked oil filter, worn drive dog, faulty solenoid, faulty transformer whether the pump pressure is steady etc. A trained competent engineer should be able to at least recognise where the fault may lie. If it is an intermittent fault then that can be a different story.If the engineer cant sort it I doubt whether you will be able to, You will have to get the engineer to give you some idea of what he is going to do or you will have to change the engineer.
    Trianco eurostars go through a lot of photocells and solenoids.
     
  3. sessi

    sessi Guest

    Thank you for your reply Kimbo, I was not considering tackling anything myself but rather trying to see if there was just something that could help a little. The Engineer is a very nice man just scratching his head now! I will mention the parts that you have mentioned and see if he has a lightbulb moment! In answer to your question of timing of this, it is not on the timer, I just leave the hot water on constant and use the thermostat to put the heating on as and when. When I come down in the mornings it is always out, and have to reset it, sometimes takes more than one go. Sometimes after showers baths etc it will fire up and sometimes it doesn't. So very random really.

    Thank you very much.
     
  4. Best

    Best Trusted Plumber Top Contributor!!

    As Kimbo has said, it could be anything. Assuming everything obvious is ok, then I would add, - motor or motor capacitor. If it fails to start in morning it may have locked out previous night. If it is cold start problem, then flame not igniting as electrodes or combustion wrong. On first going to the boiler I would first - check basics like oil filters & mechanical parts like oil pump , motor and drives. If all ok then solenoid, control box, motor capacitor and photocell, perhaps in that order. Easy to change. Transformer is usually fine if good spark. Should be noted that solenoids if faulty, tend to not work at all or else only work in periods which can vary up to about 1 hr if boiler not cutting on & off too much, ie only heating hot water.
     
    Last edited: Oct 26, 2011
  5. dontknowitall

    dontknowitall Guest

    What's the state of the fire valve? I've had one recently locking out after about 10 minutes of running, reset then lock out after 30 seconds. Left for quarter of an hour then boiler ran again for around 2 minutes.

    Many fire valves suffered last winter and with recent rain, if water has got in it might explain why it was working during the (dry) summer but not now.
     
  6. kimbo

    kimbo Guest

    Cold starts is sometimes indicative of the capacitor as there is more drag on the motor when cold. Also ther could also be air in the system and overnight it wont allow the boiler to start it might take a number of attempts to get rid of a small amount of air.. If the motor turns every time you reset the lockout button before it starts it does not sound like anything seized. Methodical approach is the best and check everything through thoroughly starting from the tank with the filters and joints etc
     
  7. Best

    Best Trusted Plumber Top Contributor!!

    I agree. Capacitors are often overlooked. If you turn boiler on several times, you sometimes find that motor will suddenly fail to turn, with only a hum noise. Then probably oil pump/ motor has stopped on a more tighter spot which shows the capacitor weak. If any motor has a split second hum every time it goes to start, same applies. Faulty, tight oil pumps & motors ruin capacitors, so pays to change them.
     
  8. gpm86

    gpm86 Guest

    hiya i dont tink there is anything wrong wit your boiler/burner,i think the problem is your boiler is not being called on when you want it from the motorised valves,it would be worth checking the motorised valves,they are probably in your hot press and it is very common for them to jam and need replacing.you should get a plumber he will figure it out quite quickly!!
     
  9. Best

    Best Trusted Plumber Top Contributor!!

    No, def has to be with the burner on the boiler not firing when it gets power, because owner stated it is going to lock out -( on control box which is at burner only)
     
  10. WHPES

    WHPES Trusted Plumber GSR

    What happens before it goes to lockout? Does the motor turn OK? Does it ignite?

    Do the electrodes arc correctly when they are supposed to?

    If you say you got a flash from the control box it may be bust now. This is sometimes caused by a failing ignition transformer
     
    Last edited: Oct 27, 2011
  11. Best

    Best Trusted Plumber Top Contributor!!

    I was assuming the " flash" they mentioned was the normal spark you see through the clear satronic control box that may be on the burner. Eurotraders had Sterling burners ( & other types) which often use Satronic boxes. That's the trouble, not enough info.
     
  12. WHPES

    WHPES Trusted Plumber GSR

    I had a faulty transformer last year actually melted a control box.
     
  13. Best

    Best Trusted Plumber Top Contributor!!

    Yes, I have come across a few that both the control box & transformer were gone. I assume that control box went faulty first & kept ignition running, so then burned out the transformer. Mainly seen satronic boxes doing this.
     
    Last edited: Oct 27, 2011
  14. dontknowitall

    dontknowitall Guest

    Useful tips here from various posters, thank you for those!

    Slightly off topic, had a call out to a breakdown at 5pm, half hour away from home. Dreaded not being able to fix it. I've done more installations than breakdowns. Anyway, got there, been told boiler had been serviced a few weeks ago.

    Checked oil supply - tiger loop and wall hung boiler. More panic as I've no idea how to start an empty tiger loop if needed. No oil isolation valve . grrr. Struggled to remove burner.

    Filthy nozzle. Service? Not in my book!

    3/4 hour later I'd changed nozzle and thought I'd try boiler. It bloomin' worked!!! Ran as fast as I could!!
     
  15. Best

    Best Trusted Plumber Top Contributor!!

    Often u don't need to do much to start an empty tigerloop as use press reset button ( if oil tank refilled). One of the many advantages of t.loops!
     
    Last edited: Oct 28, 2011
Loading...
Similar Threads - Intermittent firing Trianco Forum Date
Intermittent problem - Vaillant Turbomax Plumbing Forum Apr 18, 2017
Worcester 28cdi pressure guage up and down hot water intermittent Gas Safe Register Forum - Public Forum Mar 2, 2017
Baxi 15-HE Loud intermittent noise Central Heating Forum Feb 23, 2017
Ideal Mini C24 on/off intermittently VIDEO Central Heating Forum Feb 8, 2017
Mira shower - intermittent heat - can it be fixed? Bathrooms, Showers and Wetrooms Jan 16, 2017
intermittent F22 error on turbomax combi boiler Central Heating Forum Jan 7, 2017
Ferroli HE31 C - intermittent hot water Plumbing Forum Jan 1, 2017