Hay guys i have never attempted a back boiler oil link up before, i have a customer who has purchased a back boiler wood burning stove and is looking to link it up 2 the oil heating to heat the water and rads! Only problems is that its a bungalow and the hwc is on the same floor as the stove so have no way of installing a gravity circuit to the stove! i was thinking of just fully pumping the system and linking the flow and return from the stove into the boiler flow and returns just where they enter the building (obviously installing all the necessary non return valves! Obviously doing it this way is abit dodgy incase of power faiure and the pump fail to operate, causeing the system to pump over into the f &e but i cant see this being a major problem??? any advice guys, has any1 installed a back boiler which is fully pumped????
 
You need to take care! Why can you not have gravity to cylinder in a bungalow? Can you take the return below floors? Or are they solid?
 
You cant install a solid fuel boiler without having a gravity circuit to get rid of excess heat in the event of power outage.
There are ways to do this correctly, "H2panel layout 8" is one for a bungalow with a buffer located in the loft, Google it
 
You need to take care! Why can you not have gravity to cylinder in a bungalow? Can you take the return below floors? Or are they solid?


Yes the floors are all solid, would be abit of a nightmare! explain what you mean exactly, as a would need to take the flow up into the roofspace and down into the hwc that wouldnt work on gravity???
 
You cant install a solid fuel boiler without having a gravity circuit to get rid of excess heat in the event of power outage.
There are ways to do this correctly, "H2panel layout 8" is one for a bungalow with a buffer located in the loft, Google it

thanks will check it out now!
 
Yes the floors are all solid, would be abit of a nightmare! explain what you mean exactly, as a would need to take the flow up into the roofspace and down into the hwc that wouldnt work on gravity???

Taking the flow higher than the hot cylinder before dropping down to top connection of coil is totally okay, - providing the cylinder is raised a bit & that the expansion tank is well above flow pipe. Flow must rise to vent pipe & fall from it to cylinder. It is actually an advantage to have the connection above cylinder, even in a house.
Only problem in a flow pipe going over the roofspace is you get the heat of cylinder reversing to fire, when fire is colder.
 
You cant install a solid fuel boiler without having a gravity circuit to get rid of excess heat in the event of power outage.
There are ways to do this correctly, "H2panel layout 8" is one for a bungalow with a buffer located in the loft, Google it[/QUOTE

Can only see a diagram for a bungalow incourprating a unvented system into the link up!
 
Taking the flow higher than the hot cylinder before dropping down to top connection of coil is totally okay, - providing the cylinder is raised a bit & that the expansion tank is well above flow pipe. Flow must rise to vent pipe & fall from it to cylinder. It is actually an advantage to have the connection above cylinder, even in a house.
Only problem in a flow pipe going over the roofspace is you get the heat of cylinder reversing to fire, when fire is colder.

Thanks for eliberating on that best! Idealy you would be looking a double coil cyclinder then!
 
Thanks for eliberating on that best! Idealy you would be looking a double coil cyclinder then!

Always a double coil cylinder to prevent other gravity or pumped circuits mixing, - unless you are using some sort of neutraliser, or thermal store.
 
Flux

Its a completely unsafe installation that you are describing.

The only way that you may be able to achieve a link up in a bungalow is to get the cylinder well up in height above the solid fuel boiler, possibly in the loft space - however that may present problems with siting the cisterns.

There are normally two accepted methods of connecting the two boilers together, the H2 panel as described or a Dunsley Baker Neutraliser. In both cases the there needs to be a fail safe to allow heat to dissipate from the boiler in the event of power supply cut off, this is achieved by positioning the cylinder and a heat leak radiator at sufficient height above the solid fuel boiler to permit effective gravity circulation. Also remember that it's the difference in height between the centre line of the boiler and the centre line of a cylinder or radiator that creates the circulating pressure in a gravity circuit so having them at about the same height will not work.

Correct link ups to do them well and safely are not a job for the faint hearted.

Jon
 
Cylinder does not need to be extremely high in a bungalow. In an ideal world it would be well above the fire - as in a house with cylinder upstairs, which would prevent back heating from cylinder.
If the cylinder is raised at all, with the returns & flows all highest at coil, it will work.
Obviously keep it up as high as reasonably possible. Most are just raised about max 600mm from floor on wrap around back boilers, but depends on what height the stove is in your case.
 
Minimum centre to centre height in MI is normally around 1.0m on a very short run. It will work with less height but won't be capable of dissipating sufficient height in the event of overheating on a banked fire, therefore additional height to create adequate flow will be required.
 
Why the need for a gravity circuit?
Just fit a metal f&e and let it steam the loft on the few rare occasions it might boil. Let the pump do the rest.

I fitted a big fan assisted 40kw multi fuel solid boiler in a gaffe a while back and just instructed the guvnor to lash a bucket of water into the fire box if it boils. He seemed happy enough with that.
I demonstrated it to him a few times when it went into china syndrome. Its no big deal.
 
Last edited by a moderator:
Bit frightening for the customer with a 7kW, possibly 12kW appliance boiling away, they aren't usually to pleased.

Besides there shouldn't be any valves pumps or the like in the main primary circuit on solid fuel as an uncontrolled heat source because they can block as its normally providing the vent pipe route as well.
 
Its not worth going to a lot of hassle over. A dry burner is a better option in many cases.
Fan assisted multi fuel jobbies in the garage are the way to go. Then no fuel to carry inside.
 
I wouldn't want a boiler boiling the water & turning it to steam, & besides, surely it would be better for the welded steel boiler not to be overheated?
Stove instructions will have to be adhered to or bettered for warranty & for building control if they are involved.
 
It would only get overheated if no water was inside.
Good way to stress relieve the welds.
 
Its not worth going to a lot of hassle over. A dry burner is a better option in many cases.
Fan assisted multi fuel jobbies in the garage are the way to go. Then no fuel to carry inside.
Think that is true, - unless the fire is going to be used properly & often, then it might be better just with a dry stove. More heat to room, so better in a large room or open plan area & saves all the problems of sealed systems & unvented units not compatible. Larger stoves not always best as too big sometimes.
Dry stove would work well in a house with full air conditioning, as the heat would be put around the building.
 
It would only get overheated if no water was inside.
Good way to stress relieve the welds.
No, wasn't questioning your thoughts on dry stoves, - I agree completely. A lot of heat on a dry stove won't matter.
They put some serious heat to room out! :smile:
 
Why the need for a gravity circuit?
Just fit a metal f&e and let it steam the loft on the few rare occasions it might boil. Let the pump do the rest.

I fitted a big fan assisted 40kw multi fuel solid boiler in a gaffe a while back and just instructed the guvnor to lash a bucket of water into the fire box if it boils. He seemed happy enough with that.
I demonstrated it to him a few times when it went into china syndrome. Its no big deal.

Thats what i was thinking, aslong as you inform the customer before you do it, also tell them never to use the fire when the power is out.lol
 
Why the need for a gravity circuit?
Just fit a metal f&e and let it steam the loft on the few rare occasions it might boil. Let the pump do the rest.

I fitted a big fan assisted 40kw multi fuel solid boiler in a gaffe a while back and just instructed the guvnor to lash a bucket of water into the fire box if it boils. He seemed happy enough with that.
I demonstrated it to him a few times when it went into china syndrome. Its no big deal.

What a tool you are
This is silly and very dangerous this member should be banned for such advice
 
[SUP]Which bit is silly? Steaming the loft or lashing a bucket of water into a 40kw fan assisted boiler? :rofl:

Solid fuel boilers regulary boil in the uk and the feed and vent to BS6700 do their jobs. Heat leak rads may be turned off, undersized or just not fitted.
Dousing flames in a solid fuel boiler is no big deal. You've obviously never done it which is why your drama queen arm waving histronics have come into play..

I might fit a dps plate cooler to it some time if I get the time or one of kotlys thermal coolers.
Its all money though which customers these days have less and less off.[/SUP]
 
Last edited by a moderator:
No drama queen It's dangerous iv fitted more solid fuel link ups than I care to remember
 
The thought of chucking a bucket of water into a 40kw solid fuel boiler is a ridiculous idea. It would be dangerous and possibly end in a visit to A&E.
 
Must be a real convoy to even contemplate that
Should be banned for stupid comments like that IMHO
 
Water expands by 1600 times its original volume when turned to steam, I dont think a one gallon bucket would quench a 40Kw boiler! :cowboy::75:
 
There are proper ways to quench solid fuel boilers but using a bucket is not one of them. The others although they work are not yet legal to fit in the UK.
If you really are advising people to do this you are being irresponsible to say the least.

Sure as a youngster i can remember the water spouting out the expansions onto the roofs from the small circulator s everyone had but that was piped differently and not into over a tank.
 
Well couldn't believe what I was reading until I got onto page three and sanity rained. I mean seriously, telling the customer to chuck a bucket of water on it. Do it right and do it safely. As ecowarm and others have mentioned H2 panel or dunsley neutraliser, if not sure get somebody who has done it before to come in and assist. It shouldn't be a case of just chucking it in because the cust doesn't have the money. If they ain't got the money then tough!
 
A bucket of water works fine. A fire extinguisher would work too but water's cheaper.

And thats what my customer uses if it overheats to just douse out the flames as it prevents his garage becoming a steam room. Its working fine now anyway as all the air has been expelled but will still probably overheat in a power cut or control failure which he is aware off.
As for the other methods btw such as the plate cooler, they are legal as dps supply them. Its just an external cooler instead of an internal one which many solid fuel boilers now being installed in the uk are fitted with and implemented anyway. Its nothing new.

From the SFA..

The heat leak radiator is not a safety device but serves to reduce the risk of water boiling and discharging into the header tanks and out the overflow. I am not aware of any legislation which covers this issue.

In any case it would be some what bizarre if an installer fitted a safety device such as a bvts valve capable of cooling the entire output of the boiler and be told its illegal.






 
Last edited by a moderator:
Well see how legal it is if he ever no sorry when has to claim on house insurance for your workmanship
Or try's to sell house lol I'd love to see a picture or your expert installation lol
 
He may not have house insurance. I certainly don't. A waste of money and another unecessary bill imo.
 
Here's the valve station I built for it...
http://alturl.com/mgztz


You won't find anything like that on your travels through the sticks of Tyrone. What do you think of that big Danfoss AVTA cooling valve in there and the 28mm sheeps crook anti gravity loop? Nice features I think and works extremely well.
 
Last edited by a moderator:
Looks over complicated to be honest without knowing what is feeding it or what its purpose is For
H2 panel Whould that not of done same job??
Your quite neat though
And no not saw that sort of think in Tyrone or anywhere else in the north
But some god awful stuff in south
 