Currently reading:
Inadequate Circulator Pump?
Discuss Inadequate Circulator Pump? in the Central Heating Forum area at PlumbersForums.net
That gives a flow rate of 21LPM and a boiler output of 23kw, also the mid point (mean) temp of each rad is remarkably consistent at ~ 62/63c and probably pretty accurate as the mean of the boiler flow&return is 63C, giving a rads output of ~ 84%, don't see any real reason to balance these rads based on your numbers. 18C is a almost perfect dT IMO. You might just take another cycle time after full system heat up as difficult to see your hose requiring 23kw to maintain 19/20C.
Thank you for the assistance and calcs with this! Yes for sure I'll re check boiler run times tomorrow they appear too high but I think the stat was just off and back on again.
Upstairs been running for about an hour there on its own. I did a better balance on the rads - each rad has about 5c drop across it. All rad temps pretty much identical at 64c.
4 doubles and 1 single at present. (1 double missing again!)
Boiler outlet temp 74c
Return temp 57c
2.19 run time
1.43 off time
On watching it for 2no cycles the run time dropped by a few seconds which would make sense as the house heat demand/ soak will drop off as it heats up I guess. If running longer would probably go 50/50 or less run time I would say.
Since the first 2L of X800 cleaner was wasted due to no water circulation and drained I added another 1.5L tonight.
I'll let that run for a few days and add the last .5L just before draining.
The mag filter is collecting black sludge. A day of running it has about 5mm coating on it. Again this system was never fitted with a filter so I expect this will drop off as I monitor and clean it.
The cleaner is probably moving the stuff around and the mag grabbing it. Ill monitor and clean the magnet until such times as it remains clean for a week or more run time.
It is a Grant Mag One 28mm filter, really well designed bit of kit,. Just a minute or two to shut off, drain, clean and bleed again.
They are definitely highly effective wish it was fitted sooner.
Return temp 57c
2.19 run time
1.43 off time
What size are those rads?, I am getting 2.9kw/double rad (assuming "4.5" doubles) based on heat input of 13kw and 3.5kw/double rad based on heat input of 15.73kw (based on cycle time). This gives a average rad deltaT of 8.5C or 10.3C almost double of your values.
Can you post the size of burner nozzle fitted to the Firebird.
The rads are all glossy white so was hard to get accurate temps on them. Whilst 5 was about the average a couple were nearer 10 maybe depending on what exact spot I took the reading.
2 of them are 4 ft Myson double Finned (belt out the heat)
2 other doubles are older none finned 6 foots. And a tall vertical single radiator in bathroom.
The boiler has a 0.65gph nozzle at present.
Pipes also run down an unheated cubbyhole, they are lagged but probably lose some heat there too.
Happy New Year to all! I did get the rising CH expansion tank issue resolved. I fitted 28m ball valves on the stove pipes in the boiler room which shut it off from the system when not in use. This is 100% fine as it is only lit once in a blue moon and only by me so I know to open the yellow levers before lighting it. And for avoidance of doubt I will fit a warning notice on the stove to instruct same.
I reduced the pumps speed setting to 1 and the house still heats 100% fine that way. I am currently progressing the painting of the boiler room and will be fitting new pipe lagging in there too.
I do wonder now should I fit an automatic bypass valve?
A reminder is this house had no TRVs and was all one zone with no stats.
Now it is split into 2no zones and TRVs are fitted to all rads except the 2no In the rooms with the stats.
I wonder that now if one of the 2no 2 port zone valves fails to open the pump will be running with no where for the pressure to go. Since it is no longer a smart pump either.
As a safety factor, to reduce stress on pump / boiler and in order to reduce noise of TRVs when the others start to shut I think it would be a good idea(?) There is no such device on this system at present automatic or otherwise but then at the time that wouldn't have been a consideration with no TRVs etc.
I could install an automatic bypass valve between the 22mm upstairs zone pipes about 2m pipe distance from the boiler. After pump and before boiler return and where there are no zone valves yet to stop flow around the bypass loop.
If anyone here thinks that would be a good idea I may go ahead and order a quality ABV by Honeywell or similar and get it installed which would complete this project.
If the port valves don’t open the pump shouldn’t run
Better to put a bypass rad before the zones as with abv on big pumps they tend to be always open as there normally installed close to the pump
Thanks for that and yes fair point. My system is using the microswitches so probably not an issue. I guess a gate valve I'm conjunction with the abv would provide additional control. But with the big pump being so efficient on speed 1 I don't hear any trv valves making excess noise so I'll just monitor and if its not broke don't fix it!!
Being in the boiler room alot the past couple of days I did notice that on the first startup of the day there is a faint popping noise heard inside the burner. I think the new boiler would benefit from a Tiger Loop. I'll order the correct all metal internal type and vent it externally per instructions.
Oil fired boilers in general do not need ABVs as the Hx holds 20/25 litres of water which acts as a buffer so when the boiler+ pump cuts out, the water temperature (from a target temp of say 70C) will not rise > 90C/95C, a long way from the hi limit lockout of 113C. Gas boilers have a Hx content of only a few litres and this is why they have a timed pump overrun after all zone valves shut, the water then has no where to go so need a ABV.
might just be metal expanding on first heat up
It's actually the flame, the second it fires up I can hear it shuddering and popping for a few seconds. Say around 10 seconds then it goes solid burn no popping or hesitation thereafter.
On reading up on tiger loops and single line oil systems they do appear to be a good idea anyway to ensure maximum efficiency and eliminate any potential for air bubbles at the nozzle which I suspect is the problem. There may be tiny air bubbles in the oil line then as it sits overnight these go up near the pump and it has to clear them when first firing up.
And no need to bleed oil line either if the tank runs out of oil.
Great explanation 👌 thanks for that I will not bother with an ABV in this instance it should be aok without it unless trv noise is a problem but does not appear to be even with the house up a 24c this evening.
TRV noise (or lack of) has always been a bit of a mystery to me, I have used them for years and have never had a problem with noise, I have now replaced almost all, apart from one Myson, as the plastic heads were getting a bit brittle after 10/12 years or so, I have replaced them with EPH and all of them are/and always have been installed horizontally on the rad returns. Some makes seem more prone to noisy operation, your's must also be "noise free" as the pump on setting1 is still producing 5M.
Getting some progress on boiler room. Insulating pipes now, there is a pair of 22mm pipes very close together. For those I'll slice the insulation with a razor so both layers fit around the pipes. Is there a better way to do that? Kind of want all the insulation the same VS using a wrap.
All pipes will be fully lagged. Then on the small radiator in here I'll keep turned on low. And fit a frost stat inside this room which will override the downstairs zone. That should protect the whole system from getting frozen. (Both internal room stats also have set back temp settings and frost stat if turned on standby)
New fire ceiling going in and will paint floor to finish the boiler room.
Reply to Inadequate Circulator Pump? in the Central Heating Forum area at PlumbersForums.net