D

DEMPSEY1965

Hi All,
After turning the heating off after the winter I have noticed that the rads are still getting warm. Hot water is set to constant on the timer and the heating is set to off. I will be calling in the experts and I just want to know roughly what is going on here. The system is gravity fed, Greenstar ri boiler, Drayton Lifestyle timer, digistat in the hallway 3 port valve in airing cupboard. Valve appears to be moving freely when heating/water is selected. Also the pump appears to be running all the time even after the boiler has shut off and the only way I can stop it is to turn off the power completely. I have turned off all the rads which was ok but I am a little worried that I will be doing damage just to get the water hot. Now I have turned the heating off completely and using the immersion for the hot water. Any ideas please and thank you for your time.
 
I think your getting a little confused here if your hot water is set to constant on your programmer then the pump will run all the time even when the boiler has fired up and gone off , you will not have a gravity fed system with a 3 port valve unless you mean a open vented system fed by a small expansion tank in the loft a greenstar ri boiler is only suitable for a fully pumped system which I think you have all you need to do is program some hot water times into the programmer regards kop
 
In many systems, and almost certainly yours, the pump continues to run for a while after the boiler shuts off. The purpose of this pump overrun is to dissipate the heat generated by the boiler. By closing all the rads, unless the system has been provided with a bypass, you're preventing the circulation from returning to the boiler.
Are your radiators fitted with TRV's?
Radiators heating up when only Hot Water is being called for is usually a sympton of reverse circulation.
 
In many systems, and almost certainly yours, the pump continues to run for a while after the boiler shuts off. The purpose of this pump overrun is to dissipate the heat generated by the boiler. By closing all the rads, unless the system has been provided with a bypass, you're preventing the circulation from returning to the boiler.
Are your radiators fitted with TRV's?
Radiators heating up when only Hot Water is being called for is usually a sympton of reverse circulation.
Hi All,
Many thanks for your concern and reply. Yes and excuse my ignorance I have an expansion tank in the loft and the valve has 3 pipes going in so I thought was 3 port, I know it has WMH. What you are saying does make sense except as far as I know has never happened before, I have never had to turn the rads off during the summer months when the heating was off. My water was timed for once a day set from 7am-11pm, so if I set the timer from 7am-9am and then 4pm-11pm this will stop the reverse circulation and is this a normal thing to happen and no need to call in a heating engineer? Valve, timer, stats etc are working normally?
Thanks again
 
I would think so and it will save you money on your electric and gas bill running your system as you are the heat has a tendency to creep down the heating return pipework and warm the radiators , you may need to get a single check valve put in the return which comes back from the radiators and into the common return back to your boiler regards kop.

Screenshot_2017-05-29-05-36-06.png
 
Last edited:
if your hot water is set to constant on your programmer then the pump will run all the time even when the boiler has fired up and gone off
That is true if the boiler stat is turning the boiler off because the boiler water is up to temperature, not the cylinder water. But if the cylinder stat has turned the boiler off, because the cylinder water is up to temperature, the pump should stop.

Dempsy:
When the problem occurs, does the pipe from the motorized valve to the rads get warm (don't check right next to the valve)? If so, the valve is faulty.
 
Yes, the vertical pipe and the 2 horizontal pipes, left and right are all hot, in full all 3 pipes going in/out of the valve are hot and the pump does eventually stop I have found. I think the valve theory makes sense because this sort of thing has never happened before. I think I may go for the valve change, annoying because it's only about 4 years old. Should I try just the electrical part before getting someone in to drain down? Thanks so much for your time and knowledge.
 
Get the whole valve changed as it's false economy just changing the head. Just make sure to employ a heating engineer to correctly diagnose the issue, not just tell them to change the valve.
 
Yes. Sounds like Motorised valve sticking. If it was working previously it probably won't be a wiring fault. Have valve replaced :)
 
I would also say a faulty valve next to the cylinder. Once replaced you should be ok again.
 
I would also say a faulty valve next to the cylinder. Once replaced you should be ok again.
Hi Again
Well I had the whole valve replaced today and I don't know whether things are just settling down but some of the rads appear to be lukewarm, any thoughts on this?
 
Just the one in the airing cupboard
Just strange as I am sure this hasn't happened before, it's not like I have had some work done recently, I keep looking at the controls etc thinking I have moved something. The valve is moving nicely, the timer and stats work are ok, just annoying now!
 
If the plumber had to drain the system, which I'm sure he would have. You probably still have air trapped in the system.
There should be a manual air vent in the airing cupboard. It's normally on an upstand pipe just on top of the pump?
 
If the plumber had to drain the system, which I'm sure he would have. You probably still have air trapped in the system.
There should be a manual air vent in the airing cupboard. It's normally on an upstand pipe just on top of the pump?
Yep there is one of those, hopefully there is air trapped etc
 
Vent a bit, until water spurts out a bit. Then leave a few minutes, vent again.
Obvs vent all the rads too, starting downstairs and moving up through house.
 
Vent a bit, until water spurts out a bit. Then leave a few minutes, vent again.
Obvs vent all the rads too, starting downstairs and moving up through house.
Ok thanks for the advice. At present my rads are turned off as is the central heating, water is on from 7am-10pm. So shall I turn on the central heating along with the rads?
 
To clear air out I usually find that running EITHER hot water OR heating is best.
This is because the pump then has more push either around the coil inside the cylinder or around the radiators circuit.
This will either push air up your vent pipes in the attic, drive air into your rads, where it can be bleed out or into your upstand pipe in the airing cupboard, where you can vent out using your manual air vent.
 
Ok, will give that a go and will let you know how I get on, thx again
 
Morning, I have done the above, water on/heating off and bled the rads, no air is coming out. Some of the rads are slightly warm though still. The hall rad, one of the lounge rads. This is driving me insane! Think I will let things settle down and hopefully as time passes and air is the problem it will slowly go away and the rads will not heat up. Incidentally, there is a small red round metal thingy in the airing cupboard on the pipe above the pump but not bleed screw on it.
 
When you say the whole valve was changed, do you mean just the brass body/water side of your 3port valve or was the actuator changed also? If they have both been changed I would look more down the lines of reverse circulation possibly? Didn't the engineer who replaced the valve test it on hot water alone for a period of time to double check that it was not passing down the heating? Best to probably call the engineer back to double check.
 
When you say the whole valve was changed, do you mean just the brass body/water side of your 3port valve or was the actuator changed also? If they have both been changed I would look more down the lines of reverse circulation possibly? Didn't the engineer who replaced the valve test it on hot water alone for a period of time to double check that it was not passing down the heating? Best to probably call the engineer back to double check.
That is what you have paid him for!
 
Maybe if you have a bypass valve installed that is faulty or not set correctly.
Sometimes plumbers just use a gate valve which pretty much does the same thing.
If you adjust them by screwing them down tighter you will limit the flow yonyhe heating and send it around the hot water coil instead
 
Hi,
Very interesting, regarding the plumber he is competent in plumbing but admits he is not a heating engineeer, my fault but the valve is good so at least I have a new one all for £60 labour 2 hours work. The pipe from the valve that goes to the heating is a touch warm whereas the others are hot! I like your idea of the bypass valve and will try that as I know there is one there pointed out by my plumber. I do thank you for sharing your ideas and knowledge.
 
Hi,
Very interesting, regarding the plumber he is competent in plumbing but admits he is not a heating engineeer, my fault but the valve is good so at least I have a new one all for £60 labour 2 hours work. The pipe from the valve that goes to the heating is a touch warm whereas the others are hot! I like your idea of the bypass valve and will try that as I know there is one there pointed out by my plumber. I do thank you for sharing your ideas and knowledge.
When you say a touch warm how long has the hot water been on for? If the central heating pipe from the 3port valve is a touch warm an your radiators are hotter then ain't going to be the 3port valve passing. Depends really where the by-pass is piped into on the primary return. I'd honestly suggest looking for a local GSR heating engineer to take a look.
 
Water on for about 5 minutes I felt the heating pipe and at the valve is warmish and the other 2 are very hot, where the pipe goes into the floor it is cold. Thought it may be just heat from the valve/other pipes. The rads are off now so not sure if they are getting hot, think I might just bite the bullet and get a proper heating man.
 
Water on for about 5 minutes I felt the heating pipe and at the valve is warmish and the other 2 are very hot, where the pipe goes into the floor it is cold. Thought it may be just heat from the valve/other pipes. The rads are off now so not sure if they are getting hot, think I might just bite the bullet and get a proper heating man.
Turn on all your rads again, an just put your hot water on. On your three port valve your going to have the primary flow from the boiler which will be hot, the second pipe (which you say is hot should be to the cylinder coil) the third pipe may have some heat to it but that could be considered conduction along the pipe work. If the pipe you say goes to the floor is cold an I'm assuming that's the central heating from the 3port then I'd say that's just some heat conduction from the valve. Looking at all the responses an help we have tried giving you here it's probably just easyier to get someone who knows what there doing, it will only save you time an money hopefully.
 
Yes, the plumber said it was probably heat transfer and the pipes are exactly how you said. It's not like like it's leaking etc and I have turned all the rads off so not a problem with the heat in summer, just kind of annoying. Thank you all again for your time.
 
Status
Not open for further replies.

Reply to Heating Off Rads getting warm in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
75
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
207
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
89
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
365
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9