I would drain down and wack some x800 in the system for a week then drain it down again and fresh inhb
Discuss Heating Bangs when switching off. in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Thanks for your advice. The pipe or pipes running across the garage ceiling are the flow and return to the boiler. The vent pipe is in the airing cupboard and goes about 18 inches abouve the header tank in the loft. When filling the heating back up after draining it doesn't bang, it's only when all the air is out the system so similar to your radiator test. Turning the pump down reduced the bang noise.Forgot to say, that as you mentioned the amount of muck in the magnet suggests that the system needs a good clean.
Got a picture of the new by-pass that’s been fitted ? Hard to tell from airing cupboard picture but is the open vent an cold feed teeing in just before pump
The valve put in on the by-pass looks like a ball fix turned 1/3 off have you tried opening this fully an seeing if this stops the banging
*shaun beat me to it,but that isn’t correct for a by-pass that’s why you still have the banging
I didn’t even pick up on that it was 15mm,that won’t help an then with the type of valve that will neither. You’ve said that with it fully open the banging stops.I could only say that since the 13years you’ve been there that the pipework /heatexchanger has become restricted.
bypass valve open vented system - Google pretraga ask your plumber who installed your by-pass to come back an rectify
Has a Plumber put that in?
Has a Plumber put that in?
It will do there if it is 22mm and automatic. I am presuming you have a 3 mtr min loop from boiler and back to boiler via by-pass?
View attachment 31830
One question, I have lived in the house for 13 years without a single bang. Why would this start after removing the radiator.
The distance from the boiler to the by pass is about ten meters. I will change the size of the plumbing and use solder joints as it looks a bit messy. I can fit it somewhere else if it works better. I would rather it be correct. Wish I had done the work myself.
Does the pressure have to be regulated by the pump flow speed. Cheers.
Does the pressure have to be regulated by the pump flow speed. Cheers.
Pump is on 2 as the system is quite large 12 rads.What speed is the pump on now?
Pump is on 2 as the system is quite large 12 rads.
Cheers.
I
If it works well it's fine. You want them on the lowest setting that works and gives the right flow and return temps.
With the valve:-
screw it shut, turn on the heating and hot water so both Motorised valves are open and the pipes start to get hot. Slowly open the Auto by-pass 1/4 turn at a time, (a few seconds in between turning), until you feel hot water flow through the by-pass. Then close it back around a half turn.
That's the best explanation I can give on a Forum. I would be going to greater lengths to set things up and balance the system if I were doing this in person but it will do!
Please do come back and tell us how you went on.Thanks I'll do it on Saturday and let you know how it goes.
Cheers.
Hi.Please do come back and tell us how you went on.
Does the light on the pump flash or stay solid?
Okay. That's fine. If you were running it in flashing mode, then it would not be running fixed-speed, and the automatic bypass valve wouldn't be able to work as it should.