If boiler and hob are operating safely, within manufacturers specifications but the pipework is undersized and getting more than a 1mb drop between meter and boiler, is that AR or NCS?
 
There is no NCS, how much drop.
Mention on the paper work.
 
There is no NCS, how much drop.
Mention on the paper work.

5mb drop, 2.9m3/h expected and getting 2.4m3/h but all flue gas readings and heat input readings are absolutely fine
 
Advise they need pipework upgrade, will they agree? Or will it be, it's been working ok for years.
 
Is your 5mb drop at the boiler or at the gas valve?
 
Is your 5mb drop at the boiler or at the gas valve?

At inlet on gas valve - I'm upping the pipework - seems all I'm doing lately is upgrading pipework lol
 
Status
Not open for further replies.

Reply to Gas Safety Question in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
181
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
1
Views
70
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
180
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
255
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock