CO2 is the most important reading not the ratio? Statement from Valiant literature.
If this is correct then why is this not on the landlords safety certificate for example?
A landlords certificate requires gas rate and gas ratio co/co2 reading.
If these are both correct the boiler is deemed safety checked.

The co2 readings are sometimes lower than 9% in the MI. Am I contravening any gas regulations by not correcting it?

For example 7per cent instead of 9 percent in MI. I rang vaillant and they said its 'my call'.
 
All the readings are important and they normally say a tolerance normally something like 5-10%

For me I would adjust if it's below or above 8.7 or 9.3%
 
Most manufacturers go straight to CO2 , but as Shaun says they are all important
 
Rang Gassafe over this a few months ago and was told only the ratio is of any importance as far as they are concerned.
 
You could have on the money CO2, but if the CO was through the roof then you wouldn't just ignore it, the CO2, CO, O2, ratio, xs air and flue temperature will build you a picture of what's going on, I like to have as much information as possible on my screen when looking at fga
 
You could have on the money CO2, but if the CO was through the roof then you wouldn't just ignore it, the CO2, CO, O2, ratio, xs air and flue temperature will build you a picture of what's going on, I like to have as much information as possible on my screen when looking at fga
I always gas rate the boiler, check input working pressure, then take fga readings. If the co and ratio look good im tempted to leave it working. Adjusting the co2 often takes the co out of limits. I check the flue integrity, if that's good what else can I do?
If the co2 is 2%below I don't want to change gas valves when the boiler is basically safe.
 
If out of spec phone manufacturer up and ask them is it ok (just explain if you adjust it sends everything else out of wack)
 
CO2 is the most important reading not the ratio? Statement from Valiant literature.
If this is correct then why is this not on the landlords safety certificate for example?
A landlords certificate requires gas rate and gas ratio co/co2 reading.
If these are both correct the boiler is deemed safety checked.

The co2 readings are sometimes lower than 9% in the MI. Am I contravening any gas regulations by not correcting it?

For example 7per cent instead of 9 percent in MI. I rang vaillant and they said its 'my call'.

I don't maintain much vailant but can't you adjust it to within limits, that's what I dislike about the ideal boilers is they aren't factory set to the cleanest burn and could be better and aren't adjustable,
 
I had a an Ecotec plus 831 on Thursday that was low on CO2 and Gas rate, I adjusted it until the CO2 matched the mi's, did the Gas rate again and it was within tolerance, CO was below 100ppm if I remember rightly ratio 0.0008, i'm not saying you should adjust, but i made an engineering decision
 
I had a an Ecotec plus 831 on Thursday that was low on CO2 and Gas rate, I adjusted it until the CO2 matched the mi's, did the Gas rate again and it was within tolerance, CO was below 100ppm if I remember rightly ratio 0.0008, i'm not saying you should adjust, but i made an engineering decision


Yeh 0.008 ratio regulation for most flued appliances
 
Rang Gassafe over this a few months ago and was told only the ratio is of any importance as far as they are concerned.
This dosent surprise me. If they made co2 the priority reading there would be more boilers with corrected co2 and left with higher co values. Ive corrected co2 and the co moves from 50 to 250 which always concerns me. I know im covered if ive hit the ratio. The Anton chart I use gives co2 allowances from 3.4 to 10.2 falling within the correct co/co2 ratio, so does this mean all these values are valid? No action required.
 
Status
Not open for further replies.

Reply to CO2 is the most important reading not the ratio? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
230
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
377
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
53
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
213
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock