Hi,

I am looking for advice from the skilled and knowledgeable as it seems very hard to pin down a plumber to look at all the issues I have without several call outs and costs.

I bought a house about 6 months ago (30year old) and got straight on with some renovations. As part of this process we had 4 radiators off the walls in order to decorate and plaster around them.

This was summer time so we had not tested the heating to know if any of the current issues were there before. The only issue we had noticed here the awful sound of waste water constantly making a drip sound in the internal SVP and a tap tap tap noise every time we put on the hot water tap.

I think the only way to rectify the SVP is have it re-routed and the tapping noise is to locate where this is occurring and either move the pipe away from the wood local to it or put some pipe insulation around it at the point it is tapping/expanding. Sensible?

Now onto the main issues. After a couple of weeks after having the central heating on the pipes in the loft started making a really loud clanking noise, like someone was hammering them with a large spanner, and you could hear them jolting about and banging. A couple more weeks passed and the boiler started making some louder running noises when first starting up. At first I genuinely thought it was a helicopter in the sky! It certainly wakes me up. You here the pipes violently rattle in the loft first then about 10 minutes later the boiler. Its like the fan on the boiler is going into overdrive, so much that it must send a vibration though the house and together with the noise creates the sound I hear. This can last up to 30mintes from start up and it accelerates then slows down on about a 10 second cycle.

We did have an engineer out (because one time the boiler locked out) and he didn't know why this was doing it. However, after re-setting the boiler and it not coming on he discovered that the pump in the airing cupboard was not working, he gave it a few taps and unscrewed it at the front, upon reattaching that screw/valve it kicked back in. From this he deduced it maybe poor flow that is causing the pipes in the loft to rattle and boiler over compensating to disperse the heat until the pump gets going. In other words, the pumps on its way out. On the occasion the boiler tripped the pump may have failed. For info the heating went off late on the evening hours after running normally.

Other info:

My radiators have been bled, despite me still hearing some gurgling from one of them (that radiator works fine and wont bleed anymore), I have two radiators which get a lot hotter at the top and both of those seem to take a long time to heat up (an hour).

I also have a loud tapping to my bedroom radiator when it initially comes on, I think again this is from the feed pipe so probably the pipe expanding against the wood under the floor.

When removing the radiators previously the water in them was black near the end of emptying them.

I did wonder if air had got into the system or their was a sludge problem.

On a separate issue I seem to barely have enough hot water to fill the bath before the water pressure dissapears to zero? Is this an undersized cylinder?

What I maybe need is a plumber down for the day on day rate to just spend a day sorting it, otherwise this lot could cost me a fortune.
I did agree with the plumber to replace he pump but Sadly I never heard from him again......

I was thinking of changing the pump myself as it looks like all I need to do is turn the valves above and below, unscrew, unwire then the same in reverse with the new pump.

I also feel like the whole system needs flushing?

Its a standard boiler, British gas 330 , Water tank in the loft, airing cupboard with a water cylinder and their is a magna clean fitted (I am going to clean this tonight).

Any advice? Possible problem identification /solutions. I was thinking of jumping to a combi in a few years so I didn't want to waste too much money on sorting issues that become de-funct issues. I obviously cant live with this as it is though.
 
Last edited by a moderator:
Welcome to the forum Kev, try and add a link from this post to the sub section in the link below.

[DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]
 
Sorry, can a mod move this into CH section, and apologise for some grammar, when typing it is not inputting some of my presses!
 
Sorry, can a mod move this into CH section, and apologise for some grammar, when typing it is not inputting some of my presses!

I`m sure one of them will attend to it later on today after they finish working.
 
How meny radiators on system ? unfortunley it sounds like you will have to spend a fair amount to get your system sorted, possibly to most expensive will be the power flush , do you have any figures in mind as to what it may cost ?? or what you want to spend ?
 
How meny radiators on system ? unfortunley it sounds like you will have to spend a fair amount to get your system sorted, possibly to most expensive will be the power flush , do you have any figures in mind as to what it may cost ?? or what you want to spend ?

What makes you give that assumption?
If the last plumber was right, perhaps I just need a new pump in the airing cupboard, perhaps this resolves the banging pipes and boiler ramping up and down which are the two main issues.

I'm not sure if Plumbers do jobs on a day basis but how much would a plumber expect to be paid for a days labour + material costs?

I`m making a stab in the dark regarding flushing the system etc but just putting it out there......

12 rads.
 
Hi, what size of pipe goes to the rads? Small bore pipes cause hassle with sludge and can cause the pump to work overtime trying to move the water through the system. Powerflushing these can also be a pain. Might be better to make that jump earlier than expected rather than waste time and money now.
 
Last edited:
You obviously wish to save money and you could try flushing your system yourself, using chemical cleaner into system for whatever period of time it has to work. Rads taken off should have been flushed thoroughly using a garden hose.
Does your system have any pressure relief valves that could be hammering open and closed?
Your soil pipe needs to be not tight to plasterboard or timber
 
We don't speak of pricing as it can vary from each region and also particular job. Better to get someone to look at job and give advice and costs.
But remember you have the plumbers wages and business costs together.
What sort of overall daily cost were you thinking is reasonable?
 
Last edited:
Just a stab in the dark .........
Could the noise in the SVP be from a faulty toilet cistern ie internal overflow or dump valve leaking water in to the pan?
 
What makes you give that assumption?
If the last plumber was right, perhaps I just need a new pump in the airing cupboard, perhaps this resolves the banging pipes and boiler ramping up and down which are the two main issues.

I'm not sure if Plumbers do jobs on a day basis but how much would a plumber expect to be paid for a days labour + material costs?

I`m making a stab in the dark regarding flushing the system etc but just putting it out there......

12 rads.

If as you suspect , you have sludge in the system just replacing the pump wont make any difference,
Costs for a plumber for the day, Depends on Location ! if he's going to be touching boiler then you will need a Gas Safe registered one so you will be in the ÂŁ150 to ÂŁ300 per day bracket, can-not comment on materials as don't know what will be required. Power flush 12 rads Around ÂŁ600 +.
 
thanks for feedback so far, from all I was prepared for cost s of around ÂŁ500 for pump replacement and flushed/rads rebalanced.


I will investigate some of the other comments as I'm not up on the terminology, pretty sure the SVP is really tight fit as it passes through the ceiling into the loft, it's not the cistern.

The pipes are not small bore, these look a standard traditional size. In my last house they were small bore.
 
You need cost of new pump, plus decent chemicals for cleaning system plus inhibitor to finally put into system to help prevent further corrosion.
 
As above bud chemically clean the system sentinel x 400 leave in the system and run it as normal to break up sludge and magnatite up to 2 weeks then drain the system while hot and flush change the pump at this stage refill and add sentinel x 100 inhibitor vent the system and fire up the boiler you should see a improvement, knocking and banging pipework is normally due to pipes being installed poorly take the floorboards up have a look ease notches in joists wrap hair felt lagging where pipes can expand and rub , screw the floorboards down
 
Thanks guys, I cleaned off all the sludge from the magna clean last night, rebalanced my radiators and I seem to be getting all rads on at high temp. Quite a few of the rads are not as hot at the bottom as they are at the top, maybe by 20% difference in temp.

Last night I had no knocking in the loft, all the usual creaking/tapping when the heat up (but that can be dealt with later). However, the Boiler was still cycling up and down as if it was struggling to keep temp down.

Can I ask, if it was the pump not performing or on its way out wouldn't you be able to hear the pumps speed vary too? Its just the pump sounds fine and I would have thought you would be able to hear that struggling in tandom with the boiler (if it was the ch pump)?
 
Pumps can appear to be working fine, but are actually only half working. This can happen with nearly new pumps also.
Usually if the pump is failing, the furthest rads from the boiler and also on drops pipework will not work well, if at all.
Also make sure your system is balanced properly so that there are no easy circuits for the pump to do and therefore not properly heat some of the rads. If turning off some rads makes the others work better, this might mean balancing is needed
 
Last edited:
Are you by any chance in a hard water area ? as you may have a slight scale build up as well , seems hard water area's suffer a lot more from sludge than soft water area's,
 
Guys, on here nobody has really mentioned the magna clean system I have built in.

I cleaned this yesterday so it was free from sludge.

If I used the MC3+ rapide cleaner which is supposed to remove sludge/limescale etc would this be a good thing to try. My problem with this is with needing to power flush after but according to what it says on the sales adverts it "does not require a partial drain down".

It does say this at the end "ADEY's new formula has been specially developed to deliver exceptional results when used in conjunction with ADEY’s best practice MagnaCleanse®flushing process"

1. Would I be right to use this and do nothing else but add it to the magnaclean canister and walk away?

2. The do an MC1 product which I believe is an inhibitor, can I, say in a couple weeks after add this into the cylinder.

Or am I barking up the wrong tree and should call in a pro! its I have this magnaclean and that should do the job its purposes to do.
 
I am not a plumber but if the rads are hot at the top and not so hot at the bottom that sounds like the bottom is full of sludge. I you guess the sludge wont heat up very fast.
I would guess that you need a power flush to get the sludge out of the rads.
If you have already removed 3 rads and refitted them you sound like you are OK at diy. So maybe a cheap way of doing a partial flush is to remove all the rads and flush them with a hose pipe outside.
While this wont be as effective as a proper power flush it might be better than nothing and get you going till you get a new boler. Obviously there is a possibility you could damage pipe work etc removing and refitting rads plus the need to refill with corrosion inhibitor etc.
One thing to remember is that normally a power flush will be required for a new boiler install. So it could actually be more cost effective to have the boiler replaced and power flushed if you consider that a new boiler will probably be more efficient than the old one so you will save on fuel.
 
Sorry, having some problems, repeat post clarified.

Guys, on here nobody has really mentioned the magna clean system I have built in.

I cleaned this yesterday so it was free from sludge.

If I used the MC3+ rapide cleaner which is supposed to remove sludge/limescale etc would this be a good thing to try. My problem with this is with needing to power flush after but according to what it says on the sales adverts it "does not require a partial drain down".

It does say this at the end "ADEY's new formula has been specially developed to deliver exceptional results when used in conjunction with ADEY’s best practice MagnaCleanse®flushing process". So it does look like it needs flushing if I was to talk that route.

1. So mc3+ needs a power flush?

2. They do an MC1 product which I believe is an inhibitor, I assume this wouldn't help until after a power flush?

I have this magnaclean and that should do the job its purposes to do?
 
Last edited by a moderator:
For info: the boiler is only 6 years old, this will be when the magnaclean was installed, so it should have been flushed then.......

Sludge wouldn't cause the boiler noise ramping up/down on a 10second cycle upon start up for 20minutes or so would it?
 
For info: the boiler is only 6 years old, this will be when the magnaclean was installed, so it should have been flushed then.......

Sludge wouldn't cause the boiler noise ramping up/down on a 10second cycle upon start up for 20minutes or so would it?

The key word there kev is "should" but was it powerflushed or chemical cleaned, guess we don`t the answer to that do we.
 
If you add a good quality system cleaner (I Only use Fernox Product's) F5 , then run system it will start to dislodge sludge, But you will need to clean the filter every couple of days, but first remove rads and rinse though with hose, bit of a time consuming job but if you are looking to save money that is the way to go, DIY. Did you say that someone quoted ÂŁ500 to replace pump and power flush system ? if that's so you need to get him round asap, You need to find out if you are in a HARD WATER AREA, as you may need to add extra chemicals to treat system.
 
If you add a good quality system cleaner (I Only use Fernox Product's) F5 , then run system it will start to dislodge sludge, But you will need to clean the filter every couple of days, but first remove rads and rinse though with hose, bit of a time consuming job but if you are looking to save money that is the way to go, DIY. Did you say that someone quoted ÂŁ500 to replace pump and power flush system ? if that's so you need to get him round asap, You need to find out if you are in a HARD WATER AREA, as you may need to add extra chemicals to treat system.

Sorry mate, I responded to that above, but not clearly enough. Yes I am in a hard water area.
After balancing the radiators the house is much warmer, I would say every rad is very hot for the top 2/3rds, the bottom reasonably hot. The best way I can describe this is they are barely touchable at the top but you can hold your hand on them at the bottom, but still hot.
So perhaps thats not too far being reasonably efficient, but still needs some longer term remedy.

Right now perhaps I need to concentrate on sorting the boiler
(see video link).
I think the first step has to be to try and replace the CH pump.
 
Last edited by a moderator:
Kev you have been told what to do mate your magna clean will catch any debris on its way back to the boiler but it's not there to clean the whole system out , drain down get your Adey m+3 cleaner in the system if that what you want to use and let the system run with the old pump for a week , drain and flush out , change the pump now add inhibitor Adey m+1 refill the system and vent out run the boiler job done
 
Status
Not open for further replies.

Reply to Central heating and pipework issus all over newly bought house. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock