First time post so go easy, ive had an ongoing issue with my boiler loosing pressure, ive had boiker chexked over and they suggest its a fault with pipework, ive checked for ceiling staining and around all radiators however all dry and no obvious signs, weve tried fernox f4 leak sealer still to no avail, boiler pressure will drop every 3-4 days max depending on use, has even needed topping up after 24hrs, we are almost atbthe point of paying a leak detection company to come and check the system over, im concerned they may find nothing, so hoping yiubguys may have some tips i could try, i am an electrician by trade so have a good understanding just wodnering if i may of missed anything, so any advice on how you guys would approach this would be much appreciated
 
Hi Ben,
Is it a gas or oil fired boiler?
is the expansion vessel internal in the boiler or externally mounted.?
Any sign of water leak from the PRV (safety valve), this should'nt lift unless the boiler pressure reaches 3bar. (but could be leaking at any pressure).
 
Its a gas fired ideal logic+ 35kw, expanison tank is internal to boiler and has been checked, no water came from the schrader valve, ive become abit paranoid to be honest and constantly check the PRV pipe outside and its alwsys dry
 
Shouldn't really be looking inside boiler casing unless gas approved, if the EV has been precharged to 1bar and you have filled to 1.5 bar then you are losing ~ 2 litrs of water in a short time which points to a leak.
You could break the condensate pipe and see if its dripping/leaking with boiler shut down. After switching off/isolating you could fill the boiler to say 2bar when cold then shut the boiler flow and return valves and see if the pressure falls over a few hours, if so, then probably boiler Hx problem if valves are holding tight.
 
Id expect around that kind of age yes, we had the siphon changed a few years back as it had cracked another common issue i believe, can you tell me how To best check if this is happening presumbaly wster down condensate when boiler off
 
Turn the boiler iso valves off either side black 22mm leave 24 hours with no heating or hot water on eg turn boiler off
 
How long should the boiler be off before isolating? Presumbably if just been hesting the pressure will drop, is it worth disconnecting the condensate under the boiler over night
 
Same time and no
 
Shouldn’t drop below 1 if it’s around 2.2 now
 
I would think that if it's leaking down through the condensate pipe that it doesn't matter whether boiler and system are isolated from each other or not.
 
Just tried a couple. Of things from above, topped pressure to 1.4 then isolated flow and return and within about 10 minutes has dropped to 1.0, boiler, ia this normal or far too fast, i disconnected condensate pipe below but no drips as yet
 
Depends if the boiler was hot ?
 
Then after this drop shouldn’t drop no more
 
Ok, so just had to. Pit heating back on as it was getting cold and when i opened the valves i noticed the pressure gauge went back up to 1.4, is this normal or point towards a boiler issue, will try again over nIght though
 
Boilers at fault fixed price repair from ideal or new boiler hex is split
 
Hello guys, finally had a chance to update, last night i pressurised the boiler to 1.4 bar and shut off electrically and at the flow and return valves, within a few minutes it had dropped to just below 1 bar and by the morning, (10 hours later) was down to 0.8 bar,

When i then opened the valves it dropped further to 0.2bar and then required topping up,

Does this confirm the fault to be with the heat exchanger, can someone explain why the pressure would have dropped further to 0.2 bar?
 
Sounds like you’ve got a leaking HEX and a leaking system somewhere.

When you opened the valves back up the pressure should have increased back to 1.4 bar (or there abouts) if the system was good. As that would of still held pressure.
 
That was my worry, i will carry out the test again but making sure all radiators are bled etc first, it appears the bulk of the leak is with the HEX, as wrote previosuly above the pressure did go back up when testing for a short amount of time
 

Reply to Boiler losing pressure in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
229
P
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
199
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
276
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
154
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
496
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock