Baxi Bermuda 50/6 causing me a problem

When calling for heat the boiler just goes straight to lockout with a solid red light at front on PCB and an orange light flashing twice at rear

19 mBar at the gas valve

Pump starts and works fine

1.6k Ohms and 3.8k Ohms across the gas valve

12k Ohms at 22 degrees across the sensor

Potentiometer 0 - 8k Ohms

All appear to be approximately corresponding with MI's

Replaced the PCB - no change

Replaced gas valve - no change

Replaced potentiometer - no change

Now I am stumped - So would appreciate any of your experience, knowledge or suggestions of what else I could try / test

Edit: GSR but not sure where to submit my details
 
You'll need to increase your post count up to 10+ then send a message to [email protected] with a picture of your gsr card, front and back.

We do not discuss the repair of gas appliances in open forum.
 
Status
Not open for further replies.

Reply to Baxi Bermuda 50/6 Lockout Problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

In our Village Hall we have a Ideal Concord CXS/SD40/H central heating boiler. This was installed new when we had an extension built and the existing boiler needed upgrading. The Mechanical Engineers advising the architect insisted that we had a conventional cast iron combustion chamber boiler...
Replies
10
Views
1K
Hi I've come back from a two week holiday to find my Baxi boiler displaying an error. It's a Baxi Ecoblue Advance 19 Heat ERP and the error is a red light flashing 6 times. This seems to mean "Miscellaneous" in terms of error codes. A reset is doing nothing. I've had a plumber out who's...
Replies
1
Views
974
hi, been to a baxi solo 15 he with ignition lockout fault. seems to run though the ignition cycle, can hear the gas valve open but not sparke. It fired briefly when i disconnected the earth from condensate, but went out immediately. condensates dry, changed the sparker because of continuity...
Replies
7
Views
7K
Hi anyone. I have the F28 code on this unit. Gas IN is fine and on start up fires but within a second or two, the gas valve shuts. Taken the valve apart and the diaphram is ok,no splits. S code runs thru 1, 2 & 3 but will not progress to 4( burner ignited). Checked the low voltage solenoid and...
Replies
5
Views
1K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm. This question is for my own house setup. We are really fortunate to have a large house, about 5,000sqft in total over 3 floors. It was built around...
Replies
9
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock