Hi there,
I recently fitted an ABV to a Y plan system due to the fact that the heating side is full of TRVs and the boiler has a minimum flow requirement.
The boiler also has a requirement that if a bypass be fitted in a Y plan scenario, the bypass should be capable of dissipating 1kW of heat. Due to the fact that the primary runs to the three-port valve are long, they are well lagged, so I opted for the unusual arrangement of running the return from the bypass through a small radiator connected via male irons, just to help meet that specific requirement.
This worked well for two weeks. Today, I had to look at again because the radiator was getting hot, and now, despite the fact that the bypass is set to its highest setting (highest pressure required to open it) and that the pressure differential is low because the DHW coil is not a great restriction, nor is the old boiler very restrictive, the bypass radiator is warming up. The bypass is letting by. I had expected this could happen during central heating mode, but it shouldn't be happening now when only DHW is selected. Tried closing the cyclinder balance valve and re-opening in case some debris was blocking the valve, but still there is let-by.
So, either I drain the system and relocate the feed to the bypass from the radiator flow pipe (it currently tees off before the 3-port valve), or the bypass has developed a fault and is the problem.
Honeywell informs me that an ABV is designed to have some let-by. This isn't what I understood from college, in which I am taught that the whole point of an ABV is that is can shut off when bypass is not required which is why a fixed bypass is no longer acceptable.
What do people on this forum think?
Thanks for any comments!
R
I recently fitted an ABV to a Y plan system due to the fact that the heating side is full of TRVs and the boiler has a minimum flow requirement.
The boiler also has a requirement that if a bypass be fitted in a Y plan scenario, the bypass should be capable of dissipating 1kW of heat. Due to the fact that the primary runs to the three-port valve are long, they are well lagged, so I opted for the unusual arrangement of running the return from the bypass through a small radiator connected via male irons, just to help meet that specific requirement.
This worked well for two weeks. Today, I had to look at again because the radiator was getting hot, and now, despite the fact that the bypass is set to its highest setting (highest pressure required to open it) and that the pressure differential is low because the DHW coil is not a great restriction, nor is the old boiler very restrictive, the bypass radiator is warming up. The bypass is letting by. I had expected this could happen during central heating mode, but it shouldn't be happening now when only DHW is selected. Tried closing the cyclinder balance valve and re-opening in case some debris was blocking the valve, but still there is let-by.
So, either I drain the system and relocate the feed to the bypass from the radiator flow pipe (it currently tees off before the 3-port valve), or the bypass has developed a fault and is the problem.
Honeywell informs me that an ABV is designed to have some let-by. This isn't what I understood from college, in which I am taught that the whole point of an ABV is that is can shut off when bypass is not required which is why a fixed bypass is no longer acceptable.
What do people on this forum think?
Thanks for any comments!