smell from newly re-fitted bathroom suit

Discuss smell from newly re-fitted bathroom suit at UK Plumbers Forums; Can anyone help please! Recently fiished installing a bathroom suit in the upstaires of a house but the customer says she can smell a poo type smell when lying in ...
  1. #1
    Brooksie
    Guest

    Default smell from newly re-fitted bathroom suit

    Can anyone help please!

    Recently fiished installing a bathroom suit in the upstaires of a house but the customer says she can smell a poo type smell when lying in the bath. Unfortunately I can't smell the problem but her son says he too can smell it!

    I used a flexi poo discharge pipe for the first time to link the toilet to the 110 mm discharge connection sticking out of the floor.

    The toilet is a low level one with concealed cistern (which was a pig to fit) in a vanity type cabinet.

    The bath has a compact trap (19 mm seal), the sink has a standard 32 mm p trap and the WC''s trap is built in

    The main discharge pipe runs below the floor boards and the sink and bath wastes discharge vertically into this 110 mm pipe as it runs off to the main soil stack the far end of the neighbouring en-suit. There is very little fall on this pipe.

    Is there a way of testing the system for air leakage from above the floorboards?
    Are flexi poo pipes renound for splitting or malfuncyioning?
    Is there a way of further sealing up where the 110 mm flexi joint meets the rigid 110 mm pipe connection.

    Help and advise would be most appreciated.
    Thanks in advance
    Brooksie

  2. #2
    Member
    Join Date
    Mar 2008
    Posts
    518
    Thanks
    0
    Thanked 13 Times in 13 Posts

    Default Re: smell from newly re-fitted bathroom suit

    The most likely cause of a smell like this would be a loss of water in one of the traps ( bath or basin ), flexi wc connectors aren't ideal but they are generally sound. The way I'm reading it your bath/basin wastes are going into the horizontal run from the wc, it may be that when you flush the loo the rush of water is sucking the water from one of the traps which will then let foul air into the room. This may not be the exact scenario but its fairly likely your losing the water seal, flush the loo and visually check to see if the water is being sucked out of the traps. BTW i'm assuming this smell wasn't there before you did the work. Also assuming she hasn't s**t in the bath !

  3. #3
    HTB
    HTB is offline
    Member
    Join Date
    May 2008
    Location
    South Wales
    Posts
    230
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: smell from newly re-fitted bathroom suit

    Brooksie, I couldn't tell from your post whether the S+V pipe is normally vented or whether there is a Durgo valve fitted. I mention this only because I went to house once with a similar problem you describe, and the installer had put a Durgo valve on top of the S+V in the bathroom boxed in with the vanity unit. It was stuck open allowing smells into the room, it's worth a look.

  4. #4
    UK Plumbersforums Trusted Advisor.

    Mike Jackson's Avatar
    Join Date
    Nov 2008
    Location
    Hastings
    Posts
    5,495
    Thanks
    59
    Thanked 643 Times in 590 Posts

    Default Re: smell from newly re-fitted bathroom suit

    Most likely cause is the bath trap. Shallow bath traps shouldn't be used to connect to a soil stack. You need a trap with a 3" seal or equivalent. The smell is probably coming from the overflow on the bath. Fitting a HepVO valve and right angled adaptor will sort this out. As HTB said it could also be an AAV sticking but your bath waste doesn't comply with Part H of the building regulations.

    Mike

  5. #5
    HTB
    HTB is offline
    Member
    Join Date
    May 2008
    Location
    South Wales
    Posts
    230
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: smell from newly re-fitted bathroom suit

    I've never thought of fitting a Hep VO (or fanny trap as some call them, look in the end and you'll see why) to a bath outlet. I use them most commonly under low level (disabled access) shower trays, but thinking about it, there have been times when it would have been damn useful to put one under a bath when a joist stops you getting a "u" trap in. Thanks for the tip. (Shame they're about £15 a pop, but very useful)

  6. #6
    Brooksie
    Guest

    Smile Re: smell from newly re-fitted bathroom suit

    It turns out the smell was coming from a gap between the foul side and the fresh water bathroom side of the back to wall wc pan.

    During the manufacturing process a channel is made between the supply water side and foul side which is manually plugged up with clay before firing at 1100 degrees C. In the case of these 2 pans the plugging did not seal the 2 sides and conceqently foul air was getting into the pan and hence making the bathroom smell.

    I did check all traps and changed the bath traps for 76 mm ones to conform to Part H

    Thanks to all for their advise and sugestions. Checking that the customer had not number 2'ed in the bath (as suggested by NickH) did required a degree of sensitive questioning techniques on my side!!

    Claygate the sanitary ware importers provided a good service. Within 48 hours they sent a technical rep to the property in Hampshire from their base in Kent who confirmed my diagnosis, stated that there was at present no UK requirement to pressure test WC pans, offered some resonable advise and brought 2 replacement pans with him.

    Air leakage between foul and fresh sides of a pan is not something I've ever come across before but something that I will be testing for before installing future loos.

    Thanks again
    Brooksie the wiser

  7. #7
    Member
    Join Date
    Mar 2008
    Posts
    518
    Thanks
    0
    Thanked 13 Times in 13 Posts

    Default Re: smell from newly re-fitted bathroom suit

    Thats a new one to me mate, reckon that could be a real headf**k if you didn't spot it.

  8. #8
    Member
    Join Date
    Apr 2008
    Location
    A, A
    Posts
    121
    Thanks
    21
    Thanked 6 Times in 5 Posts

    Default Re: smell from newly re-fitted bathroom suit

    Now, that's what I call good detective work. Well done for being so determined to find it, a rarefault, I hope.
    Terry.

  9. #9
    Member
    Join Date
    Oct 2016
    Posts
    16
    Thanks
    8
    Thanked 0 Times in 0 Posts

    Default Re: smell from newly re-fitted bathroom suit

    How did you test this was the case Brooksie? I think I may have the same issue.

    Quote Originally Posted by Brooksie View Post
    It turns out the smell was coming from a gap between the foul side and the fresh water bathroom side of the back to wall wc pan.

    During the manufacturing process a channel is made between the supply water side and foul side which is manually plugged up with clay before firing at 1100 degrees C. In the case of these 2 pans the plugging did not seal the 2 sides and conceqently foul air was getting into the pan and hence making the bathroom smell.

    I did check all traps and changed the bath traps for 76 mm ones to conform to Part H

    Thanks to all for their advise and sugestions. Checking that the customer had not number 2'ed in the bath (as suggested by NickH) did required a degree of sensitive questioning techniques on my side!!

    Claygate the sanitary ware importers provided a good service. Within 48 hours they sent a technical rep to the property in Hampshire from their base in Kent who confirmed my diagnosis, stated that there was at present no UK requirement to pressure test WC pans, offered some resonable advise and brought 2 replacement pans with him.

    Air leakage between foul and fresh sides of a pan is not something I've ever come across before but something that I will be testing for before installing future loos.

    Thanks again
    Brooksie the wiser

  10. #10
    Member
    Join Date
    Oct 2016
    Posts
    16
    Thanks
    8
    Thanked 0 Times in 0 Posts

    Default Re: smell from newly re-fitted bathroom suit

    I have done this so far, as well as have my eyes water from the most disgusting smell.

    Quote Originally Posted by jimbo1 View Post
    The new cistern has an overflow that somehow exits water not via the pan but somehow behind the water trap of the loo, then on into the soil stack. It also takes the same pipe as the flush water so I am guessing it is a pipe inside a pipe. So does this mean there is a direct route to soil stack. I was expecting to see the overflow water go direct into the bowl to be honest not just hearing it fall into the waste pipe behind the water trap!

    Any thoughts.

  11. #11
    Super Moderator


    super-mod
    steveb's Avatar
    Join Date
    Nov 2007
    Location
    hythe hampshire
    Posts
    12,926
    Thanks
    633
    Thanked 1,221 Times in 1,185 Posts

    Default Re: smell from newly re-fitted bathroom suit

    Brooksie isn't around anymore so won't see your posts
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please don't be offended when we ask for your details. diyers, bodgers, odd job people and have a go heroes need not apply

    The Turtle Moves



Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Foul Smell in Bathroom
    By jpb in forum Plumbing Forum
    Replies: 3
    Last Post: 05-02-2013, 11:18 PM
  2. Leaks/deluges in my home during and following bathroom and en suit instalation
    By Christine in forum Bathrooms, Showers and Wetrooms
    Replies: 6
    Last Post: 05-02-2013, 10:35 PM
  3. Bad smell in bathroom
    By Charlie Smith in forum Plumbing Forum
    Replies: 3
    Last Post: 03-12-2012, 12:25 PM
  4. New bathroom fitted - labour only, so why so much?
    By tim procter in forum Plumbing Forum
    Replies: 28
    Last Post: 21-11-2011, 06:13 PM
  5. Newly fitted radiator won't heat up
    By Mark Mckenzie in forum Central Heating Forum
    Replies: 7
    Last Post: 25-08-2011, 07:44 PM
  6. Connecting to newly fitted water meter, in a field
    By wally5460 in forum Plumbing Forum
    Replies: 4
    Last Post: 02-07-2011, 09:53 PM
  7. Backfeeding through a newly fitted shower
    By Kirsty in forum Plumbing Forum
    Replies: 6
    Last Post: 12-03-2011, 06:44 PM
  8. Bad smell in bathroom
    By ecowarm in forum Plumbing Forum
    Replies: 14
    Last Post: 31-12-2010, 02:25 AM
  9. Bathroom Floorboards smell
    By jpp in forum Plumbing Forum
    Replies: 11
    Last Post: 20-06-2009, 07:13 PM
  10. hi everyone
    By noturbo in forum New Member Introductions
    Replies: 4
    Last Post: 26-11-2007, 03:44 AM

Visitors found this page by searching for:

fanny trap

bad smell after fitting bath

fanny trap plumbing

fanny valve

concealed bath overflow smells

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.