Plumbing & Plumbers Forum - Heat pump low pressure
Like Tree3Likes

Heat pump low pressure

Discuss Heat pump low pressure at UK Plumbers Forums; Ps we have an A here sitting in our museum of oddities...
  1. #13
    Member Worcester's Avatar
    Join Date
    Jun 2011
    Posts
    978
    Thanks
    42
    Thanked 83 Times in 80 Posts

    Default Re: Heat pump low pressure

    Ps we have an A here sitting in our museum of oddities
    quality likes this.
    Worcester Renewables -Specialists in Renewable Energy Solutions
    Biomass, Pellet, Chip and Log Boilers and Stoves; Ground and Air Source Heat Pumps; Solar Thermal and Solar PV, Air Conditioning and Refrigeration, Ventilation and Heat Recovery
    Your Local Green Energy Solution Provider

  2. #14
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    3,654
    Thanks
    60
    Thanked 272 Times in 265 Posts

    Default Re: Heat pump low pressure

    Not a bad unit mechanically its just the control is pretty limited

  3. #15
    Member
    Join Date
    Feb 2016
    Posts
    103
    Thanks
    10
    Thanked 14 Times in 14 Posts

    Default Re: Heat pump low pressure

    Had a quick look today before she went to work. System working and up to temp.
    System is 5 years old and had no problems until a year and a half ago. It will typically cut out on low pressure about 3 times a month.
    Previous works seems to be magna clean and auto bypass and possible flush/cleaner (info pretty vague). She mentioned they said it was one of the dirtiest he's seen.
    Checked heat pump. Only About 800mm in front of unit to next door, rear ok. Mi's ask for 1500mm so not ideal.
    Coil pretty clean, fan ok, pcb connectors seemed ok.
    System seems to be circulating fine (flow shown through ufh manifolds). Up to pressure and no air. Cleaned magna clean, not much but quite large deposits rather than the average black sludge. Ran a manual defrost cycle and no issues was about 5°c outside at which point customer had to go to work.
    Said she'll call when it next occurs.
    Still unsure as to what could be causing low pressure as it is only intermittent. The front clearance/ unit
    positioning is not good, but it was trouble free for 3 years. Tempted to give this one a miss as really not in the know with heat pump fault finding. My experience with heat pumps is fitting a couple of ecodans to a spec and that was a couple of years ago. Will pop a couple of pics up.

  4. #16
    Member
    Join Date
    Feb 2016
    Posts
    103
    Thanks
    10
    Thanked 14 Times in 14 Posts

    Default Re: Heat pump low pressure

    Heat pump low pressure-20160309_083849.jpg
    Heat pump low pressure-20160309_085817.jpg
    Heat pump low pressure-20160309_090951.jpg
    Heat pump low pressure-20160309_085748.jpg
    Heat pump low pressure-20160309_084223.jpg
    Heat pump low pressure-20160309_083834.jpg

    Is the discolouration on some of the coil piping normal?

  5. #17
    Member Worcester's Avatar
    Join Date
    Jun 2011
    Posts
    978
    Thanks
    42
    Thanked 83 Times in 80 Posts

    Default Re: Heat pump low pressure

    Are you guys sure that unit doesn't have glycol in it??? That looks just like the A series collector, as opposed to an evaporator...
    Worcester Renewables -Specialists in Renewable Energy Solutions
    Biomass, Pellet, Chip and Log Boilers and Stoves; Ground and Air Source Heat Pumps; Solar Thermal and Solar PV, Air Conditioning and Refrigeration, Ventilation and Heat Recovery
    Your Local Green Energy Solution Provider

  6. #18
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    3,654
    Thanks
    60
    Thanked 272 Times in 265 Posts

    Default Re: Heat pump low pressure

    That is 100% a DHP AX the last 2 pictures are of the evapoartor. The ally way its installed in will not help as in cooler weather it will be like walking into a refrigerator which will not help with low pressure issues, But sound as its quite a recent issue I would suggest on the expansion valve being on its way as they do tend to hunt quite a bit because it only a standard mechanical TEV and 5 years service is pretty average life for one. I have replaced quite a few but there were only around 1200 DHP AXunits fitted in the UK
    Last edited by quality; 10-03-2016 at 07:52 AM.

  7. The Following User Says Thank You to quality For This Useful Post:


  8. #19
    Member
    Join Date
    Feb 2016
    Posts
    103
    Thanks
    10
    Thanked 14 Times in 14 Posts

    Default Re: Heat pump low pressure

    Thanks quality will look into that. I'm a bit reluctant to look into any flow related issue as seems thats the route the previous company took with no avail.
    Will have to get our refrigerant guy to test the system. With the TEV is that something you can test or would it be better/cost effective to just change?
    Also a little confused now as to wether this system needs glycol? Manual just says fill off the mains, just a normal filling loop on system so don't think so.
    Thanks
    Last edited by SmokeyJ; 10-03-2016 at 12:38 PM.

  9. #20
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    3,654
    Thanks
    60
    Thanked 272 Times in 265 Posts

    Default Re: Heat pump low pressure

    Just replace it and its sorted

  10. The Following User Says Thank You to quality For This Useful Post:


Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Which air source heat pump?
    By willing2learn in forum Renewable Energy
    Replies: 24
    Last Post: 29-01-2016, 07:38 AM
  2. tried to release pressure from the pressure gauge and now heat won't work
    By catherine 22 in forum Oil and Solid Fuel Forum
    Replies: 5
    Last Post: 29-01-2013, 11:02 PM
  3. Air source heat pump help
    By Dave Walker in forum Renewable Energy
    Replies: 14
    Last Post: 21-10-2012, 06:56 PM
  4. MCS & heat pump heat loss calculations
    By Nostrum in forum Renewable Energy
    Replies: 10
    Last Post: 11-04-2012, 05:02 PM
  5. airsource heat pump
    By northcarr in forum Central Heating Forum
    Replies: 4
    Last Post: 06-12-2009, 11:20 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.