Plumbing & Plumbers Forum - Retrofit wood-fired hot water into new, oil-fired CH and HW system?

Retrofit wood-fired hot water into new, oil-fired CH and HW system?

Discuss Retrofit wood-fired hot water into new, oil-fired CH and HW system? in the Renewable Energy at Plumbers Forums; Hi all, I'm feeling rather sheepish as I should have done my homework weeks ago, as you shall see, but I am where I am...! We've recently bought a new ...
  1. #1
    NorfolkBumpkin
    Guest

    Default Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Hi all,

    I'm feeling rather sheepish as I should have done my homework weeks ago, as you shall see, but I am where I am...!

    We've recently bought a new house and spent the past few months renovating it, which has included a new Charnwood Cove 2 wood burner and new oil boiler, hot water tank and hot water/CH system (with expansion cylinders rather than a cold water tank in the loft). The plumber we used (who we have no problems with and have used many times before) told me that fitting a woodburner-backboiler into the system would add substantial extra cost and so, disappointingly, we decided against.

    However, I've been thinking that I should have got a second opinion and that is what I am doing now. I'd be grateful if anyone can give me an idea of the feasibility and (very) approximate cost of installing a backboiler onto the Charnwood (you can get a flueboiler to fit our stove which I guess is the sort of thing we'd be looking at) and using this heat to complement the indirect hot water system which is currently heated by the oil boiler (and immersion).

    Any comments gratefully received - please bear in mind that I'm not a plumber so my technical knowledge is limited.

    Thanks,
    Alex


  2. #2
    Plumbers Arms member SimonG's Avatar
    Join Date
    Feb 2011
    Location
    The Land Of The Prince Bishops
    Posts
    7,225
    Thanks
    284
    Thanked 691 Times in 681 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Is it an unvented hot water cylinder you have? reading your post it sounds like it.

  3. If You Burn It, It Can Kill You.

  4. The Following User Says Thank You to SimonG For This Useful Post:


  5. #3
    UK Plumbersforums Trusted Advisor.

    Gray0689's Avatar
    Join Date
    Jun 2010
    Location
    Northern Ireland
    Posts
    4,668
    Thanks
    66
    Thanked 433 Times in 420 Posts

    Default

    I agree sounds like unvented
    You can't have an uncontrolled heat source incorporated with unvented cylinders
    Only way you can do it and have mains pressure water is by a thermal store
    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

  6. The Following User Says Thank You to Gray0689 For This Useful Post:


  7. #4
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,363
    Thanks
    281
    Thanked 1,178 Times in 1,045 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    As everything is unvented it is now a bit of a problem. Solid fuel needs to be connected to vented systems for obvious reasons.

    There are a couple of ways to do it but none are particularly cheap or easy to do now.

  8. The Following User Says Thank You to tamz For This Useful Post:


  9. #5
    UK Plumbersforums Trusted Advisor.

    ecowarm's Avatar
    Join Date
    Mar 2010
    Location
    lincolnshire
    Posts
    3,738
    Thanks
    297
    Thanked 374 Times in 357 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    It sound like you have left it too late now Mr Bumpkin, it would be a bigger and more expensive job and defo not DIY
    >>>>>>>>>I'M ASKIN, YOU DANCIN<<<<<<<<

  10. The Following User Says Thank You to ecowarm For This Useful Post:


  11. #6
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    2,436
    Thanks
    48
    Thanked 205 Times in 199 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    You can have an unvented cylinder heated by your wood burner but you would need an open vented heating system as ecowarm has suggested it will not be cheap to do it Properly

  12. The Following User Says Thank You to quality For This Useful Post:


  13. #7
    Plumbers Arms member SimonG's Avatar
    Join Date
    Feb 2011
    Location
    The Land Of The Prince Bishops
    Posts
    7,225
    Thanks
    284
    Thanked 691 Times in 681 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    That'll be the H2 panel then? I noticed on their website they have a version for unvented.
    If You Burn It, It Can Kill You.

  14. The Following User Says Thank You to SimonG For This Useful Post:


  15. #8
    NorfolkBumpkin
    Guest

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Many thanks for all of your comments - I may have just to leave it then and carry on forking out on oil! Thanks for your help.

  16. #9
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    13
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Hi
    Had an oil fired unvented system feeding a vented dual coil hot water cylinder & sealed radiator system.
    Fitted a Charnwood insert solid fuel boiler feeding it via the spare cylinder coil, tee'd from feed before coil into pump and into existing unvented radiator run (unventing it). Check valves after each pump & standard PSV's in place.
    Happy with performance ran both to max no issues.

  17. #10
    UK Plumbersforums Trusted Advisor.

    Gray0689's Avatar
    Join Date
    Jun 2010
    Location
    Northern Ireland
    Posts
    4,668
    Thanks
    66
    Thanked 433 Times in 420 Posts

    Default

    Quote Originally Posted by Solid Fuel View Post
    Hi
    Had an oil fired unvented system feeding a vented dual coil hot water cylinder & sealed radiator system.
    Fitted a Charnwood insert solid fuel boiler feeding it via the spare cylinder coil, tee'd from feed before coil into pump and into existing unvented radiator run (unventing it). Check valves after each pump & standard PSV's in place.
    Happy with performance ran both to max no issues.
    This don't make sense to me???
    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

  18. #11
    Plumbers Arms member SimonG's Avatar
    Join Date
    Feb 2011
    Location
    The Land Of The Prince Bishops
    Posts
    7,225
    Thanks
    284
    Thanked 691 Times in 681 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Quote Originally Posted by Gray0689 View Post
    This don't make sense to me???
    Even less to me as he has posted seperate topic on backflow. So it's not running 'no issues'.
    If You Burn It, It Can Kill You.

  19. The Following User Says Thank You to SimonG For This Useful Post:


  20. #12
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    2,436
    Thanks
    48
    Thanked 205 Times in 199 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Quote Originally Posted by SimonG View Post
    That'll be the H2 panel then? I noticed on their website they have a version for unvented.
    Yeh H2 panel it is , I have done a good few of various set ups and had very good results

  21. The Following 2 Users Say Thank You to quality For This Useful Post:

    SimonG (16-11-2011)

  22. #13
    Plumbers Arms member SimonG's Avatar
    Join Date
    Feb 2011
    Location
    The Land Of The Prince Bishops
    Posts
    7,225
    Thanks
    284
    Thanked 691 Times in 681 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Quote Originally Posted by quality View Post
    Yeh H2 panel it is , I have done a good few of various set ups and had very good results
    Still haven't had chance to use one, yet. Customers tend to think great idea, tie in the heating and the stove, until they see how much it will be!
    If You Burn It, It Can Kill You.

  23. The Following User Says Thank You to SimonG For This Useful Post:


  24. #14
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    2,436
    Thanks
    48
    Thanked 205 Times in 199 Posts

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    Yes this is the down side and it's not just the extra cost of the panels (which ain't ) it's extra work (which can be quite a lot) that boosts the price

  25. The Following User Says Thank You to quality For This Useful Post:


  26. #15
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    13
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: Retrofit wood-fired hot water into new, oil-fired CH and HW system?

    The Domestic HW is using an vented dual coil hot water tank.
    The original heating system was oil fired un-vented feeding into one of the coils.
    A solid fuel system was fitted using the spare coil on its primary circuit, the oil fired system was turned into a vented system and a both then fed via pumps and check valves into the now vented radiator circuit

  27. The Following User Says Thank You to Solid Fuel For This Useful Post:


Page 1 of 2 12 LastLast

Similar Threads

  1. advice on zoning a new oil-fired system
    By markproperjob in forum Central Heating Forum
    Replies: 2
    Last Post: 07-06-2011, 08:39 PM
  2. Wood burner with back boiler and Oil fired central heating
    By Daviddonk in forum Plumbing Forum
    Replies: 3
    Last Post: 01-02-2011, 07:58 PM
  3. Replies: 11
    Last Post: 31-12-2010, 06:06 PM
  4. No hot water - Oil fired boiler
    By HPPH in forum Plumbing Forum
    Replies: 5
    Last Post: 09-08-2010, 10:05 AM
  5. wood fired boiler hookup
    By josephus in forum Plumbing Forum
    Replies: 0
    Last Post: 04-10-2008, 11:24 PM

Visitors found this page by searching for:

can i tee oil and solid fuel into one coil

wood fire hot water retrofit

adding a log burner to oil fired ch

fluebioler hotwater

best plumber to fit wood fire hot water system

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.