hi guys, went to see a intergas combi. Zero pressure so I tryed to fill it up but digital guage didn't go up. Then the prv on the boiler started making a loud noise like a rattling.so I stopped trying to fill up.

Any ideas?
 
Sounds like the digi sender eg the part that senses the pressure in the boiler either blocked or fecked

Does the boiler still work if so fit an external gauge
 
Would a inline filling loop with guage be suitable? I need to replace the filling loop any way. Would this cure the problem ?
 
Won't cure the gauge not working but will at least tell you the pressure in the system
 
You can but try bud I have done it on other makes of boiler if not this may help. Kop

Screenshot_20180919-181845.png


Screenshot_20180919-181827.png
 
Normally giving a tap on a flat surface and a good wash out sorts it but not guaranteed
 
Cheers I'll try that. I've ordered a inline pressure guage and I'll clean it. I'll also remove the pressure sensor and clean that out too.. fingers crossed.
Thank you a lot guys your my bread and water !
 
it is a semiconductor component i.e. electronic a good clean may sort it but probably not
 

Reply to Intergas combi compact no pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock