Is that rubber on the top of the flue ?
 
the above pic is ducting and at the bottom a fan providing the mechanical ventilation to a plant room, going through the ducting is a gas pipe.
even with the obstruction its providing ample air. the gas pipe is not sleeved and i cannot be certain if its a straight piece of pipe with no joints

going to hold off saying how i classified it as im interested to hear your opinions
 
I wouldn't like it either
 
I would hole saw into the side of that box and look to see what's inside. Then I would make a decision. Obviously cover the hole again after I've seen what's inside.
There are many options. One would be to sleeve it all the way through the box but you won't know what's possible until you've had eyes on it.
 
Last edited:
in the end i put it down as an AR, because it has no sleeve i was able to. However as wrong as it seems if it was sleeved i couldnt think of any reason to AR it.

it was in a hospital/old peoples home, so IDing it was to be avoided for as long as possible, but there was also no high ventilation or extraction (although not effecting combustion), they were using the plant room for storage and half the plant room was full of combustable looking rails of clothes. no earth bonding with electrical flex attached to every bit of gas pipe i could see

rough choices, who'd have thought box ticking would be so hard, life aint easy for a gas man
 
I would hole saw into the side of that box and look to see what's inside. Then I would make a decision. Obviously cover the hole again after I've seen what's inside.

Looks like it could be ab?
 
That changes things!
I cannot see the pic properly because it's a bit blurred.
Does it look like asbestos to you Ambrosia?
 
in the end i put it down as an AR, because it has no sleeve i was able to. However as wrong as it seems if it was sleeved i couldnt think of any reason to AR it.

it was in a hospital/old peoples home, so IDing it was to be avoided for as long as possible, but there was also no high ventilation or extraction (although not effecting combustion), they were using the plant room for storage and half the plant room was full of combustable looking rails of clothes. no earth bonding with electrical flex attached to every bit of gas pipe i could see

rough choices, who'd have thought box ticking would be so hard, life aint easy for a gas man
Story of my life lol
 
Sorry, just re read the post above and you mentioned it yourself.
I skim read it before.
 
Status
Not open for further replies.

Reply to what do you guys make of this in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock