Search the forum,

Discuss Loss of flow rate - normal or too much in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
11
Hi,

I'm getting quite a big loss in flow rate upstairs compared to downstairs. Here are the details:

I'm not getting a great litre per minute of hot water from my combi, I'm getting around 12 lpm (which outputs 18 lpm at maximum). When I looked into it, I'm only getting about 12 lpm of cold water into the boiler from the mains, so the boiler seems to be working as it should.

BUT, I get 40 litres per minute of cold water at the property boundary (according to Yorkshire Water). At the first tap (an outside tap), I get about 20 lpm which I'm happy with. I recently had new alkathene pipe laid from the boundary to the house so there can't be any problems there, hopefully.

A little further along the plumbing, still downstairs, I tested the flow into my washing machine and it is also about 20 lpm. However, the pipes (all 15mm plastic push-fit) then go behind the plaster and up the wall to the next floor. I exposed some pipes and tested the flow rate on upstairs, directly from the 15mm pipe, and I am only getting 15lpm. My questions are as follows:

1. Does it sound normal that I am losing 5lpm from downstairs to upstairs?
2. I also don't understand why I'm losing a further 3lpm by the time the cold main reaches the boiler (boiler input is 12lpm) which is only about 5 metres from the pipes giving 15lpm, and on the same floor.

Thanks in advance.

Andy
 
It's a Viessmann Vitodens 111w.

So, not exactly a combi, but a combi for the purposes of this discussion I think?
 
I am not a Veissmann expert but just looked at the manual and it boasts that it should giving you around 18ltrs/m. Are all valves open fully into/out of the boiler?
 
Yeah, the Veissmann guys told me I should get 18litres/m too but pointed out that I won't get that with 12litres/m of cold going in!

Yes, all valves open fully into and out of the boiler.

What do you recon about the drop in litres/m from downstairs to upstairs that I mentioned. Is this normal?
 
Yes the 111 is a storage combi so can do much more than your 15lpm

I would put it frankly down to your plastic pipes 15mm plastic ends up around 10mm bore by the time you talk of inserts etc

My personal opinion/experience I would install 22mm copper from your new stop tap to the boiler you should be golden then
 
As above or can you trace back where the supply to the boiler comes from and upgrade the part that reduces? May be a 15mm isolation valve somewhere which reduces the flow further
 
Thanks for the replies, really appreciate it.

The difficulty is (as I'm sure is often the case) that a lot of the pipes are now very hidden. We can take up the carpets and floorboards without too many problems but there is quite a long stretch on the ground floor and 1st floor that is buried under tiled floors (with electric underfloor heating) which I I really want to avoid taking up!

Maybe the 'nuclear option' is best - leave the existing piping to retain cold water supply for taps, toilets, washing machine etc and run a new dedicated 22mm copper pipe directly to the boiler from the stop-tap. I'll have to go through the ceiling to avoid taking up the tiled floor upstairs.

That's what I'll do, unless anyone thinks otherwise?
 
That's a sensible option run a supply just for the boiler
 
That is what i would do, you will get a drop off in pressure and flow on the higher floors due to the weight of water exerting pressure dowards towards the stoptap the mains water supply has to over come this so obviously it will effect pressure and flow the higher you go , there are ways to help overcome this employ the services of a good plumber and ask about accumulators.cheers kop

Screenshot_2017-11-22-18-57-08.png
 
Status
Not open for further replies.

Reply to Loss of flow rate - normal or too much in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
209
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
226
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
171
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock