    Hi there,

    My hubby and I are in the middle of a renovation that's turned out to be the equivalent of a new build. We've had to change everything apart from the envelope including all the plumbing and electrics.

    The property is approx 260sq m on 3 floors and has a total of 9 rooms, 2 kitchens, 4 bathrooms (bath and shower) and an open plan living room into one of the kitchens which is in the loft. We've made room for boiler cupboard in the loft and are planning to have a system boiler with a hot water cylinder. There's a total of 22 radiators including 4 heated towel rails in the bathrooms.

    We have however had contradicting information on the size of tank required as well as the boiler size. Our fitter has advised to use a Valiant Boiler (Ecotec 637 and a 300l tank) however I have sought second opinion and was advised to double up on the fitters recommendation (i.e almost go for commercial sizes for both the tank and boiler) for the hot water and heating requirements.

    Long story above I know, but I would appreciate some pointers on how to proceed with this.

    Many thanks

  2. #2
    Member
    Join Date
    Mar 2013
    Posts
    1,328
    Thanks
    45
    Thanked 200 Times in 197 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    Hi, and welcome.
    Post is silent regarding mains water supply to building. 4 bathrooms plus 2 kitchens can use a lot of water, but if mains supply is 22mm to DHW cylinder, all outlets will not, simultaneously, give adequate flow. What flows out of tank is restricted to what flows in. Boiler size would permit one shower to be used continuously, reheating water as fast as it is used. The 300 litre cylinder gets depleted only when additional outlets are used.
    Whats your current flow and mains pressure.

  3. The Following User Says Thank You to joni os For This Useful Post:


  4. #3
    Plumbers Arms member
    Join Date
    Jun 2012
    Location
    London/Kent
    Posts
    3,950
    Thanks
    197
    Thanked 491 Times in 469 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    I would strongly advise you to have a proper set of designs done first.

    Do not rely of a plumbing / heating company unless they can provide proof positive that they have designed as well as installed systems of a similar size & type as yours.

    You really can't upscale heating (& for that matter hot water) systems for a standard type house to one the size of yours.

    Time and again we have been asked to go in to pick up the pieces after these large boilers have been installed incorrectly.

    You are going to be spending a lot of money on the kit alone, please don't waste your money & cause yourselves a lot of heartache for want of a few hundred quid at the beginning.

    Welcome to the forum
    Last edited by chris watkins; 1 Week Ago at 05:38 PM.
    ShaunCorbs and SimonG like this.
    Nolite id cogere, cape malleum majorem

  5. The Following User Says Thank You to chris watkins For This Useful Post:


  6. #4
    Member
    ShaunCorbs's Avatar
    Join Date
    May 2015
    Location
    North Wales (so hide all your sheep) :D
    Posts
    9,646
    Thanks
    136
    Thanked 682 Times in 671 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    Also just going off experience boiler too small cylinder will want 15-25kw that leaves you about 12kw for heating
    IMPORTANT:
    Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    Want gas safety or boiler repair advice? :
    Please supply your Gas Safe / Oftec / Hetas Number, DIYers, odd job people and have a go heroes need not apply, and remember any fuel burning appliance can kill


  7. The Following User Says Thank You to ShaunCorbs For This Useful Post:


  8. #5
    Member
    Join Date
    Dec 2016
    Location
    Bradwell , near Great yarmouth ,norfolk
    Posts
    43
    Thanks
    0
    Thanked 10 Times in 10 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    A property that size will need a light commercial boiler have a look at worcester bosch GB 162 50 KW , the heating will need to be zoned up and paired up with a 300 litre unvented cylinder and 300 litre acumulator that way you can use multiple showers baths ect without a drop in pressure the hot water system will need a secondary return back to the cylinder to provide hot water immediately the taps showers ect are turned on good luck with it . Regards k
    Last edited by king of pipes; 1 Week Ago at 08:50 PM.

  9. The Following User Says Thank You to king of pipes For This Useful Post:


  10. #6
    Member
    ShaunCorbs's Avatar
    Join Date
    May 2015
    Location
    North Wales (so hide all your sheep) :D
    Posts
    9,646
    Thanks
    136
    Thanked 682 Times in 671 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    depends on kw needed but 40-50 sounds about right, but your heating engy should heat loss your property

    depending on your mains flow and pressure you might not need an accumulator

    op where are you based?
    IMPORTANT:
    Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    Want gas safety or boiler repair advice? :
    Please supply your Gas Safe / Oftec / Hetas Number, DIYers, odd job people and have a go heroes need not apply, and remember any fuel burning appliance can kill


  11. The Following User Says Thank You to ShaunCorbs For This Useful Post:


  12. #7
    Plumbers Arms member
    Join Date
    Jun 2012
    Location
    London/Kent
    Posts
    3,950
    Thanks
    197
    Thanked 491 Times in 469 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    Quote Originally Posted by ShaunCorbs View Post
    Also just going off experience boiler too small cylinder will want 15-25kw that leaves you about 12kw for heating
    You might not need to heat the domestic hot water at the same time as the heating either.

    There are so many variables and if buts & maybes that is not even worth trying to second guess the designs of a property of this sizes.
    Nolite id cogere, cape malleum majorem

  13. The Following User Says Thank You to chris watkins For This Useful Post:


  14. #8
    Member
    ShaunCorbs's Avatar
    Join Date
    May 2015
    Location
    North Wales (so hide all your sheep) :D
    Posts
    9,646
    Thanks
    136
    Thanked 682 Times in 671 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    Quote Originally Posted by chris watkins View Post
    You might not need to heat the domestic hot water at the same time as the heating either.

    There are so many variables and if buts & maybes that is not even worth trying to second guess the designs of a property of this sizes.
    no but allways allow for it incase they do and call you up saying hot water wont heat up in 30 mins
    IMPORTANT:
    Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    Want gas safety or boiler repair advice? :
    Please supply your Gas Safe / Oftec / Hetas Number, DIYers, odd job people and have a go heroes need not apply, and remember any fuel burning appliance can kill


  15. The Following User Says Thank You to ShaunCorbs For This Useful Post:


  16. #9
    Member
    Last Plumber's Avatar
    Join Date
    Aug 2016
    Location
    Lancashire
    Posts
    1,121
    Thanks
    0
    Thanked 114 Times in 113 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    I advise you to get a Heating Engineer round to look it over and price it.

    You could even ask if they would spec it for you for your own plumber ( if you have someone in mind ), They will charge you for doing that though so ask how much first.

    If you are going to have to use a light commercial boiler, I would recommend getting a commercial Engineer to fit it for you too.

    This is all opinion of course.
    Last edited by Last Plumber; 1 Week Ago at 10:28 PM.

  17. The Following User Says Thank You to Last Plumber For This Useful Post:


  18. #10
    Member
    Join Date
    Dec 2016
    Location
    Bradwell , near Great yarmouth ,norfolk
    Posts
    43
    Thanks
    0
    Thanked 10 Times in 10 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    Reading your first post you say you have allowed a cupboard for the boiler and ho****er install carefull consideration Will be needed as the plant will be quite large and 600 litres of water weighs alot , I would suggest a purpose built boiler house on the side of the property a better option WHY I hear you ask , 1 the plant will be to big for a cupboard , 2 if anything fails you flood your lovely new home , 2 ease of access for your engineer who will maintain your boiler ect ie he will not have to trapes through your lovely home with all his tools to service your boiler ect so you have your privacy and security , 3 noise transfer through the house you will hear pumps running boiler firing modulating ect all worth considering , if you live in a hard water area you will need a light commercial water softner to to keep bathrooms being damaged from scale all this is worth considering regards k

  19. The Following User Says Thank You to king of pipes For This Useful Post:


  20. #11
    Member
    Last Plumber's Avatar
    Join Date
    Aug 2016
    Location
    Lancashire
    Posts
    1,121
    Thanks
    0
    Thanked 114 Times in 113 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    I know I have already said this once but You really need an experienced individual here.

    600 litres is a lot to install in a domestic property ( even yours ), A lot of our commercial work e.g. hotels, Nursing homes etc, have less than that, relative to the number of outlets you'll be using.

    With all due respect to them, some installers will 'guess' or way over estimate your requirements. You will end up with an over engineered inefficient Hot water system if you don't get it right !
    Last edited by Last Plumber; 1 Week Ago at 09:15 AM.
    chris watkins and joni os like this.

  21. The Following User Says Thank You to Last Plumber For This Useful Post:


  22. #12
    Member
    Join Date
    Dec 2016
    Location
    Bradwell , near Great yarmouth ,norfolk
    Posts
    43
    Thanks
    0
    Thanked 10 Times in 10 Posts

    Default Re: System boiler/hot water cylinder spec for large property

    Hi again you would not have 600 litres of hot waterr only 300 the other 300 would be in the accumulator and plumbed into the supply to the cylinder ect acting as a buffer to supply multiple outlets at the same time

  23. The Following User Says Thank You to king of pipes For This Useful Post:


Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Replies: 31
    Last Post: 20-01-2015, 07:00 PM
  2. Large Boosted Water System Maintenance - South Manchester
    By IanCun in forum I'm looking for a Plumber or Gas Engineer
    Replies: 0
    Last Post: 12-06-2012, 10:13 PM
  3. Replies: 3
    Last Post: 30-04-2012, 09:48 PM
  4. Replies: 18
    Last Post: 28-04-2012, 08:05 AM
  5. Hot water cylinder spec?
    By Andrew 03 in forum Plumbing Forum
    Replies: 6
    Last Post: 04-02-2011, 09:44 AM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.