Plumbing & Plumbers Forum - Hot water cylinder return balancing valve?
Like Tree3Likes
  • 1 Post By Mike Jackson
  • 1 Post By Best
  • 1 Post By Best

Hot water cylinder return balancing valve?

Discuss Hot water cylinder return balancing valve? in the Plumbing Forum at Plumbers Forums; Is it a must to fit these valves on all new hot water cylinders? And what's the purpose of these valves just to balance the heat output between the hot ...
  1. #1
    Top Plumbing Forum Contributor
    Join Date
    Jan 2010
    Location
    Heacham,Norfolk
    Posts
    350
    Thanks
    3
    Thanked 2 Times in 2 Posts

    Default Hot water cylinder return balancing valve?

    Is it a must to fit these valves on all new hot water cylinders? And what's the purpose of these valves just to balance the heat output between the hot water and heating?


  2. #2
    Super Plumbing Forum Contributor
    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    1,950
    Thanks
    41
    Thanked 196 Times in 194 Posts

    Default Re: Hot water cylinder return balancing valve?

    It is a must if the system is to be properly balanced. The coil in a cylinder means the flow & return are just linked together, with no resistance, so a bypass, short circuit, easy route is created & wastes the pumps performance. A valve fitted will be needed. Also IMO a good idea to have both the return & flow to cylinder fitted with valves so as to isolate if changing cylinder on oil or gas systems.


  3. #3
    UK Plumbersforums Trusted Advisor.

    Mike Jackson's Avatar
    Join Date
    Nov 2008
    Location
    Hastings
    Posts
    3,903
    Thanks
    46
    Thanked 396 Times in 366 Posts

    Default Re: Hot water cylinder return balancing valve?

    Under part L of the building regulations a balancing valve should no longer be fitted. For energy efficiency the coil requires the full output of the boiler for a rapid heat up, The reason for a balancing valve is to share the boiler output between the circuits and make sure that the coil doesn't rob the heating. Under Part L a programmer with independent time control of heating and hot water is required so this is not an issue as the hot water can be set to come on 30 minutes before the heating is required.
    Best likes this.
    Gas Safe Registered Engineer for all your Domestic gas, Heating and plumbing needs in Hastings, East Sussex. Check me out on the Gas Safe website, reg. No. 537192.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

    By the way I have a Land Rover.

  4. #4
    Top Plumbing Forum Contributor
    Join Date
    Jan 2010
    Location
    Heacham,Norfolk
    Posts
    350
    Thanks
    3
    Thanked 2 Times in 2 Posts

    Default Re: Hot water cylinder return balancing valve?

    Thank you for your answers. So if the hot water was too hot and hardly no heat in the radiators all you would do is simply close the balanceing valve off slightly so the heat going to the heating as well as heating the contents of the hot water cylinder evenly.

  5. #5
    Super Plumbing Forum Contributor
    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    1,950
    Thanks
    41
    Thanked 196 Times in 194 Posts

    Default Re: Hot water cylinder return balancing valve?

    I had no idea that part L regs now say a balancing valve should no longer be fitted. Interesting thought as to always heating water separately.
    However, if you do have the heating to hot water on at the same time as the radiators - & people will be in the habit of both heating at times, then the system will be badly balanced & would need a valve. Take the example, bad weather, heating on all day, people using a lot of hot water, so cylinder needs reheated.
    I wonder if a self adjusting valve, like the way the bypass valves work would make more sense on the cylinder circuit?

  6. #6
    Super Plumbing Forum Contributor
    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    1,950
    Thanks
    41
    Thanked 196 Times in 194 Posts

    Default Re: Hot water cylinder return balancing valve?

    Quote Originally Posted by Dannyparty92 View Post
    Thank you for your answers. So if the hot water was too hot and hardly no heat in the radiators all you would do is simply close the balanceing valve off slightly so the heat going to the heating as well as heating the contents of the hot water cylinder evenly.
    If the cylinder is supplied with 22mm or larger pipes, the valve will usually need well turned down to slow the flow enough.
    Dannyparty92 likes this.

  7. #7
    Top Plumbing Forum Contributor
    Join Date
    Jan 2010
    Location
    Heacham,Norfolk
    Posts
    350
    Thanks
    3
    Thanked 2 Times in 2 Posts

    Default Re: Hot water cylinder return balancing valve?

    Thanks for your answers guys so the balanceing is fitted on y plans s plans and gravity systems?

  8. #8
    Super Plumbing Forum Contributor
    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    1,950
    Thanks
    41
    Thanked 196 Times in 194 Posts

    Default Re: Hot water cylinder return balancing valve?

    You don't balance gravity pipes to cylinder as they are not pumped & so are not affecting the balancing of pumped circuits. Only solid fuel can nowadays have gravity pipes.
    Also not supposed to restrict gravity pipes & besides, a valve could be turned off by mistake someday, which on a solid fuel boiler wouldn't be a good idea.
    Always leave gravity primaries & their vent & feed pipes fully open & without valves.
    AWheating likes this.

  9. #9
    UK Plumbersforums Trusted Advisor.

    Mike Jackson's Avatar
    Join Date
    Nov 2008
    Location
    Hastings
    Posts
    3,903
    Thanks
    46
    Thanked 396 Times in 366 Posts

    Default Re: Hot water cylinder return balancing valve?

    Quote Originally Posted by Best View Post
    I had no idea that part L regs now say a balancing valve should no longer be fitted. Interesting thought as to always heating water separately.
    However, if you do have the heating to hot water on at the same time as the radiators - & people will be in the habit of both heating at times, then the system will be badly balanced & would need a valve. Take the example, bad weather, heating on all day, people using a lot of hot water, so cylinder needs reheated.
    I wonder if a self adjusting valve, like the way the bypass valves work would make more sense on the cylinder circuit?
    I learnt this last time I did my unvented. Also with the rapid recovery times of modern cylinders it's not such an issue.
    Gas Safe Registered Engineer for all your Domestic gas, Heating and plumbing needs in Hastings, East Sussex. Check me out on the Gas Safe website, reg. No. 537192.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

    By the way I have a Land Rover.

Similar Threads

  1. Replies: 1
    Last Post: 02-01-2012, 06:31 PM
  2. balancing valve on HW Return
    By cdodds2004 in forum Central Heating Forum
    Replies: 3
    Last Post: 05-12-2011, 07:32 PM
  3. Replies: 16
    Last Post: 30-11-2011, 12:45 PM
  4. Shower supply, pumped hot, cold main, which valve for balancing?
    By olivejar in forum Bathrooms, Showers and Wetrooms
    Replies: 9
    Last Post: 17-09-2011, 07:10 PM
  5. Hot Water Cylinder Mixing Valve
    By TheArtfulDodger in forum Plumbing Forum
    Replies: 6
    Last Post: 06-02-2010, 07:08 PM

Visitors found this page by searching for:

balance hot water cylinder

cylinder balancing valve

balancing hot water cylinder

hot water balancing valve

hot water cylinder balancing

balancing hot water system

hot water return balancing valve

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.