confused.....
Has anyone an insight into this please:
I replaced a radiator in a bathroom, open vented system, 3 port valve, boiler, cylinder and controls upstairs.
All the radiators in the house are fitted with trv's (I know this shouldn't be the case) underneath the bathroom rad is a by pass, a length of 15mm tube connecting flow and return on an isolator.
The problem is, when the heating is first turned on the new rad gets really hot and is then turned off by the customer on the trv, (elderly cust who turns it on or off and doesn't let the trv do its job). When the room cools to below acceptable the trv turned on and the rad refuses to get hot and refuses to get hot until the heating is turned on again the next day.
I went back yesterday and opened the engineers valve fully. Maybe, I've restricted the flow too much but why does it work at all!
The confusion for me is the radiator works when the system is turned on, maybe the customer doesn't give it enough time. I thought the pump is playing up but again the rad gets hot when first on!
So, any insights please.
I have never failed, just found ways that won't work!
-
29-01-2012 #2UK Plumbersforums Trusted Advisor.


- Join Date
- Dec 2010
- Location
- Bridgend, Wales
- Posts
- 3,609
- Thanks
- 69
- Thanked 358 Times in 348 Posts
Trv sticking shut. Try swapping with ls. May say on the box bi-directional. But this isnt always the case
Btw. Have you balanced the system correctly
"nothing is impossible"
GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.
-
The Following User Says Thank You to SimonJohns For This Useful Post:
secret squirrel (29-01-2012)
-
29-01-2012 #3Plumbers Arms member
- Join Date
- Feb 2009
- Location
- Essex
- Posts
- 2,452
- Thanks
- 36
- Thanked 168 Times in 132 Posts
Re: confused.....
No, not balanced system just changed one rad for another same size.
I did think trv but being a new one! every thing points to that though....I have never failed, just found ways that won't work!
-
29-01-2012 #4UK Plumbersforums Trusted Advisor.


- Join Date
- Nov 2010
- Location
- Locks Heath fareham
- Posts
- 3,189
- Thanks
- 87
- Thanked 271 Times in 270 Posts
Re: confused.....
Bathroom rad on the heating circuit and not on the hot water circuit? Is it an old trv?
As Simon says does sound like a balancing issue.Behind every great man is a woman rolling her eyes.
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.
Read more: http://www.ukplumbersforums.co.uk/pl...#ixzz2AiWGkgEG
-
The Following User Says Thank You to APPlumbing For This Useful Post:
secret squirrel (29-01-2012)
-
29-01-2012 #5Plumbers Arms member
- Join Date
- Feb 2009
- Location
- Essex
- Posts
- 2,452
- Thanks
- 36
- Thanked 168 Times in 132 Posts
Re: confused.....
TRV is new, I will probably have to go back and play with the balancing, pin on trv didn't appear stuck,
Heating circuit or hot water circuit thats very interesting, if that is the case the previous rad would have done the same which would have held the heat for longer,
That makes sense, h/w and heating come on in the morning rad gets red hot, heating comes on during the day rad stays off.I have never failed, just found ways that won't work!
-
29-01-2012 #6UK Plumbersforums Trusted Advisor.

- Join Date
- May 2008
- Location
- Bolton
- Posts
- 4,195
- Thanks
- 190
- Thanked 353 Times in 333 Posts
Re: confused.....
its not unusual to find a rad on the hw. the bypass should be on the heating circ tho
IN CERVESA FELICITAS - IN BEER THERE IS JOY

The horse and mule live thirty years and nothing know of wines and beers,
But sinful, ginful beer soaked men, live to three score years and ten
-
29-01-2012 #7Plumbers Arms member
- Join Date
- Feb 2009
- Location
- Essex
- Posts
- 2,452
- Thanks
- 36
- Thanked 168 Times in 132 Posts
Re: confused.....
I think I couldn't see the wood for the trees, I had dismissed a balance issue because both rads were the same size,
I'm almost sure thinking about it the rad is on the heating circuit but this will need checking. The amount of times I've explained to customers about the h/w circuit and the bathroom rad. The problem is the cust hadn't said this was an issue before and I never checked!
And because the bypass is on this rad I'd have thought this would be a heating circuit, after all its been there years..
Balancing it is then....
BUT why does it heat up initially and then not, presuming its heating circuit etc. I can't think of a reason why,I have never failed, just found ways that won't work!
Similar Threads
-
A lil confused...
By Kerry85 in forum Plumbing ForumReplies: 11Last Post: 13-04-2011, 07:16 PM -
Confused!
By Ruby in forum New Member IntroductionsReplies: 4Last Post: 08-04-2011, 03:08 PM -
Confused!
By ConorM8350 in forum Plumbing ForumReplies: 9Last Post: 05-04-2011, 03:19 AM -
any help im confused
By ndwhite in forum Plumbing Courses FeedbackReplies: 8Last Post: 05-09-2010, 05:35 PM -
Confused!
By Mowgli82 in forum Central Heating ForumReplies: 2Last Post: 03-08-2010, 07:49 AM



Reply With Quote










Help remembering a few things...
55 Minutes Ago in Oil and Solid Fuel Forum