Discuss weird one in the Plumbing Forum at Plumbers Forums; we fitted a biasi combi a few weeks ago, now its leaking! but not from any of the pipe work its all bone dry, the boiler isn't dropping in pressure. ...-
09-12-2011 #1Steady Plumbing Forum Contributor
- Join Date
- Oct 2010
- Location
- manchester
- Posts
- 120
- Thanks
- 0
- Thanked 2 Times in 2 Posts
weird one
we fitted a biasi combi a few weeks ago, now its leaking!
but not from any of the pipe work its all bone dry, the boiler isn't dropping in pressure.
the leak doesn't happen through the day, but when the customer turns the stat down at night and goes to bed when she awakes she has a nice bowl full of water under the boiler to wake up to, any ideas?
-
09-12-2011 #2UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2011
- Location
- Newcastle Upon tyne
- Posts
- 6,054
- Thanks
- 299
- Thanked 770 Times in 744 Posts
Re: weird one
Has to be on the mains water side if the pressure isn't dropping yeh?
"Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein
-
09-12-2011 #3UK Plumbersforums Trusted Advisor.


- Join Date
- Dec 2010
- Location
- WestMidlands
- Posts
- 5,846
- Thanks
- 124
- Thanked 574 Times in 548 Posts
Re: weird one
Ammonia is found on Pluto, Jupiter and, in small amounts, on Uranus.
are you Gas Safe? want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details.Diyers,potchers,odd job people and have a go heroes need not apply!
AW Heating and Plumbing Services. Take the Plunge!
btw im commercial, NOT.
-
09-12-2011 #4UK Plumbersforums Trusted Advisor.


- Join Date
- Dec 2010
- Location
- Bridgend, Wales
- Posts
- 3,609
- Thanks
- 69
- Thanked 358 Times in 348 Posts
Could it be with the stat being so low the boiler is condensing more and leaking from that
"nothing is impossible"
GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.
-
09-12-2011 #5Steady Plumbing Forum Contributor
- Join Date
- Oct 2010
- Location
- manchester
- Posts
- 120
- Thanks
- 0
- Thanked 2 Times in 2 Posts
Re: weird one
yeah well i went before to have a look, yeah all i could think of is condensation or something to do with the mains, so suggested she turned the mains off before bed and see how she gets on, theres so much water though i just cant see it being condensation, its literally a full mop bucket of water, we will see anyway
Thanks lads
-
12-12-2011 #6Steady Plumbing Forum Contributor
- Join Date
- Oct 2010
- Location
- manchester
- Posts
- 120
- Thanks
- 0
- Thanked 2 Times in 2 Posts
Re: weird one
Went back this morning and the heat exchanger is leaking, when the boilers off and cold it leaks and when it's warmed up due to the heating being on it seals itself! Any idea how a heat exchanger could get damaged? Jack
-
12-12-2011 #7UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2011
- Location
- Newcastle Upon tyne
- Posts
- 6,054
- Thanks
- 299
- Thanked 770 Times in 744 Posts
Re: weird one
Its a new install mate, probably poor weld on the plate hex ... these things happen eh? I've known of many a leak only occur when the system has cooled ...
Glad to know you got it sorted though, manufacturers visit I take it
"Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein
-
12-12-2011 #8UK Plumbersforums Trusted Advisor.

- Join Date
- May 2008
- Location
- Bolton
- Posts
- 4,195
- Thanks
- 190
- Thanked 353 Times in 333 Posts
Re: weird one
warranty should cover it if its a new boiler.
IN CERVESA FELICITAS - IN BEER THERE IS JOY

The horse and mule live thirty years and nothing know of wines and beers,
But sinful, ginful beer soaked men, live to three score years and ten
-
12-12-2011 #9Plumbers Arms member

- Join Date
- Nov 2010
- Location
- West Sussex
- Posts
- 600
- Thanks
- 12
- Thanked 30 Times in 29 Posts
Re: weird one
Is there a water meter fitted? { all water meters have a built in non return valve}
A lot manufacturers insist/suggest on a small expansion vessel on the water main near the boiler, this takes up the expansion in the hot water side when the tap is turned off.
The above should stop heat exchangers splitting
safe-gas-installer.co.uk
-
12-12-2011 #10UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2011
- Location
- Newcastle Upon tyne
- Posts
- 6,054
- Thanks
- 299
- Thanked 770 Times in 744 Posts
Re: weird one
You know what Kev the first lot of combi's i remember fitting all had the mini expansion vessel fitted as standard. Manufacturers, trying to cut costs, have chosen to lump this fact onto the installer who, lets face it aren't necessarily taught to look out for the means of expansion provision!
"Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein
-
12-12-2011 #11Steady Plumbing Forum Contributor
- Join Date
- Oct 2010
- Location
- manchester
- Posts
- 120
- Thanks
- 0
- Thanked 2 Times in 2 Posts
Re: weird one
lol i have only been plumbing for 5 years but never even heard of a combi with additional expansion vessel, and don't remember reading anything in the manufactures instructions? but anyway its under warranty so we will have to wait and see! cheers jack
-
12-12-2011 #12UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2011
- Location
- Newcastle Upon tyne
- Posts
- 6,054
- Thanks
- 299
- Thanked 770 Times in 744 Posts
Re: weird one
Hey jack ... they call them 'shock arrestors' these days, but were fitted as standard to take up the expansion, however small, generated in the water to water heat exchangers
"Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein
-
12-12-2011 #13Plumbers Arms member

- Join Date
- Nov 2010
- Location
- West Sussex
- Posts
- 600
- Thanks
- 12
- Thanked 30 Times in 29 Posts
Re: weird one
Showing my age there Diamond !!
I was responsible for fitting loads of Saunier Duval combis in the past!!, 1986 onwards.( under the instruction of my employer tho BGAS]
I was guilty of this 2 years ago when installing a W Bosch Junior, heat exchanger split after 6 months, new fitted and expansion vessel no problem since.
It is now a standard part of any combi install I do.
That may be why I am the same price as B Gas as i was told today, however I was quoting to run 12mtrs of 35 mm and 15mtrs of 28mm copper for a 42 cdi combi. They suggested a 42 cdi can run on 27 mtr of 22mm as well as a double oven range gas cooker.
safe-gas-installer.co.uk
-
12-12-2011 #14UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2011
- Location
- Newcastle Upon tyne
- Posts
- 6,054
- Thanks
- 299
- Thanked 770 Times in 744 Posts
Re: weird one
Me too regards the saunia's and I remember the myson Midas too!
I've since got out of install to a large extent but recognise the benefits of the precautions the older boilers had. I still keep in contact with and recommend an old pal with the same ethics as you regards installing and I admire the professionalism and pride he has, and you portray, all be it sometime looked on as OTT lol
"Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein
-
12-12-2011 #15Plumbers Arms member

- Join Date
- Oct 2009
- Location
- Nottingham
- Posts
- 1,672
- Thanks
- 57
- Thanked 132 Times in 121 Posts
Re: weird one
Is there a magna clean fitted?
Similar Threads
-
now this is weird
By gas man in forum General Off-Topic ChatReplies: 10Last Post: 26-09-2011, 06:42 PM -
Weird blockage
By SimonJohns in forum Plumbing ForumReplies: 9Last Post: 16-08-2011, 10:59 PM -
news of the weird
By gas man in forum General Off-Topic ChatReplies: 19Last Post: 22-05-2011, 11:07 AM -
weird set up
By jambo in forum Central Heating ForumReplies: 2Last Post: 02-03-2010, 08:03 PM -
Weird pressure issue
By forrest1066 in forum Central Heating ForumReplies: 0Last Post: 29-10-2008, 08:17 AM



6Likes
Reply With Quote










Help remembering a few things...
1 Hour Ago in Oil and Solid Fuel Forum