High CO Readings on Baxi Combi 105 HE
Discuss High CO Readings on Baxi Combi 105 HE in the Plumbing Forum at Plumbers Forums; Hi, Can anyone help? During a landlords inspection carrying out a Flue Gas Analysis I found exceptionally high CO readings, more than 750 PPM. Readings are satisfactory with combustion case ...-
06-04-2011 #1New to Plumbing Forum
- Join Date
- Apr 2011
- Posts
- 3
- Thanks
- 0
- Thanked 0 Times in 0 Posts
High CO Readings on Baxi Combi 105 HE
Hi, Can anyone help?
During a landlords inspection carrying out a Flue Gas Analysis I found exceptionally high CO readings, more than 750 PPM. Readings are satisfactory with combustion case removed or if appliance is on minimum output ie. with gas valve solenoid wire removed.
Gas rate and burner pressure ok. Cleaned out burner and primary heat exchanger. Have checked flue, appears to be clear. Air intake has no POC. contamination with appliance running. Have replaced secondary heat exchanger/condensing unit and associated seals.
Am Now cosidering changing fan in case running slow or POC's leaking up air impellor shaft and back into case instead of going out of the flue.
Starting to run out of ideas. If anyone has any ideas or has come across this problem before i would be grateful to hear from them.
-
06-04-2011 #2Top Plumbing Forum Contributor
- Join Date
- Jan 2011
- Location
- Charing
- Posts
- 593
- Thanks
- 7
- Thanked 55 Times in 54 Posts
Re: High CO Readings on Baxi Combi 105 HE
Has it got a long flue?
Got a Alpha boiler with a problem, then you need help from Alpha man! Covering all areas in Kent and stock carried on the Van.
Steve
-
06-04-2011 #3Top Plumbing Forum Contributor
- Join Date
- Jun 2010
- Location
- Cumberland
- Posts
- 975
- Thanks
- 11
- Thanked 86 Times in 82 Posts
Re: High CO Readings on Baxi Combi 105 HE
Have had it a couple of times both were flue joints apart.
-
07-04-2011 #4New to Plumbing Forum
- Join Date
- Apr 2011
- Posts
- 3
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: High CO Readings on Baxi Combi 105 HE
No more than 1 metre...
-
07-04-2011 #5New to Plumbing Forum
- Join Date
- Apr 2011
- Posts
- 3
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: High CO Readings on Baxi Combi 105 HE
Thanks, I will go back through and have a closer inspection of flue...Flue is less than 1 meter long so no actual joints to speak of...I had the same problem last year and ended up handing job to Heatteam and they said they replaced the secondary heat exchanger/condensing unit which worked....
Similar Threads
-
Heatline solaris combi high pressure
By whambars in forum Central Heating ForumReplies: 1Last Post: 22-10-2011, 02:53 PM -
Oil Boiler - High Carbon Monoxide Readings
By WHPES in forum Central Heating ForumReplies: 3Last Post: 08-12-2010, 07:52 PM -
high flow combi
By peteisfishing in forum Central Heating ForumReplies: 4Last Post: 17-11-2010, 11:04 PM -
Unvented Cylinder or High Flow Combi?
By ln1234 in forum Plumbing ForumReplies: 7Last Post: 31-08-2009, 05:41 PM -
High pressure in combi boiler
By james789 in forum Plumbing ForumReplies: 1Last Post: 22-07-2009, 05:10 PM



Reply With Quote










Variable flow Water Pump for...
1 Minute Ago in Plumbing Forum