Plumbing & Plumbers Forum - Sealed or vented?

Sealed or vented?

Discuss Sealed or vented? in the Plumbing Forum at Plumbers Forums; Sealed or Vented? We want to hire a plumber to install a new heating and plumbing in our home. It seems that before we can get proper quotes or make ...
  1. #1
    New to Plumbing Forum
    Join Date
    Nov 2010
    Posts
    5
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Sealed or vented?

    Sealed or Vented? We want to hire a plumber to install a new heating and plumbing in our home. It seems that before we can get proper quotes or make progress, we have to make a fundamental choice between using a sealed or a vented system. It’s a large house (six bedroom), and we’re a large family of two adults and four teenage children, and our highest priority of all relates to water pressure. It’s vital that we can at least have a system which allows us to be running three or four power showers, at the same time, and not have the water temperature or pressure affected if someone then turns on a tap or the dishwasher starts up etc. Right now, this doesn’t work at all with our current system, even with one shower on, if a tap goes on too then we’re either scalded or frozen, or both alternatively.

    I know little of the two system choices, other than the snippets I’ve picked up from plumbers so far. I’m told the advantage of a sealed system is no water tanks or pipework in the attic (so nothing to freeze), less risks of leaks going un-noticed and less risk of air locks (especially in an old house like hours where pipes do tend to go up and down a lot to get around the layout of the house), but with the disadvantage that cold water is based on mains pressure and the hot water only works on pressure, no pump like a vented system would have, so the more taps/showers that are on, the lower the pressure and the more likelihood of temperature changes when taps are turned etc. I’m told the advantage of a vented system is that the water supply to the showers will be from stored water (hot and cold) in the tanks, so constant pressure to all showers until the tanks run dry and much less impact of taps being turned on etc, but the disadvantages are tanks and pipes in the attic that can freeze, leaks can go un-noticed as no drop in pressure and higher risk of air locks…

    How on earth am I supposed to make this decision which way to go? I only know I want us all to be able to have a shower without being scaled or froze when the dishwasher starts or one of us stops our shower (and of course I’d prefer not to have frozen pipes, leaks and airlocks). Can anybody help me shine some light on this, how to make the decision, are there other things to be considered, are there ways around the disadvantages of either solution? We really need help here…


  2. #2
    Banned
    Join Date
    Dec 2009
    Location
    Portsmouth
    Posts
    672
    Thanks
    64
    Thanked 70 Times in 68 Posts

    Default Re: Sealed or vented?

    The most important thing is incoming flow rate.

    You can measure this yourself. Fill a known volume ie a 5 litre bucket, and time how long it takes to fill.

    This will give you your litre per minute flow rate.

    If it is sufficient, then a Unvented hot water storage cylinder is what you want, coupled with a system boiler. Being a system boiler it is a sealed system and less likey to get problems later on.

    The installer of the unvented also needs to be qualified to do so.

    Take your measurements and let us know how you get on.

    Wherabouts are you, someone on here may be local to you.

    ps take it from a tap that uses main pressure.... easily mistaken sometimes.

    hope this helps
    Graham

  3. Last edited by grahamgas; 17-11-2010 at 11:29 AM.

  4. #3
    New to Plumbing Forum
    Join Date
    Nov 2010
    Posts
    5
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Sealed or vented?

    Addition: Some replies I got asked about our current cold water pressure. I did a test, using the kitchen tap which is about as close to the mains as possible, I'm getting 10 litres per minute, though it's much slower if I go to the upstairs bathroom taps, less than half that.

  5. #4
    Moderator

    steveb's Avatar
    Join Date
    Nov 2007
    Location
    hythe hampshire
    Posts
    8,969
    Thanks
    441
    Thanked 746 Times in 726 Posts

    Default Re: Sealed or vented?

    the bathroom taps are probably fed from the cwst in the loft. an easy way to check is to put your thumb over the end of the cold and turn it on if you can stop the flow it is fed from above if it spurts out in is most likely mains fed.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please don't be offended when we ask for your details. diyers, bodgers, odd job people and have a go heroes need not apply


  6. #5
    New to Plumbing Forum
    Join Date
    Nov 2010
    Posts
    5
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Sealed or vented?

    What do you think, is 10 litres per minute a sufficient mains pressure to use a sealed system, delivering sufficient cold water to 4 showers at the same time and still have a decent pressure and not major temperature changes when the dishwasher kicks in?

  7. #6
    Moderator

    steveb's Avatar
    Join Date
    Nov 2007
    Location
    hythe hampshire
    Posts
    8,969
    Thanks
    441
    Thanked 746 Times in 726 Posts

    Default Re: Sealed or vented?

    10 litres per minute isn't the pressure it's the flow rate. you need to put a pressure tester on one of the first outlets on the system usually an outside tap to get an accurate pressure measurement.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please don't be offended when we ask for your details. diyers, bodgers, odd job people and have a go heroes need not apply


  8. #7
    New to Plumbing Forum
    Join Date
    Nov 2010
    Posts
    5
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Sealed or vented?

    OK, will do - Can you give me any idea what you think would be workable pressure for a sealed system running a six bed house with four showers, two baths, kitchen and utility room? Where is the line between what can be done with a sealed system in terms of cold water pressure, and where it becomes necessary to use a vented system with cold water stores in the loft?

  9. #8
    Plumbers Arms member Centralheatking's Avatar
    Join Date
    Jul 2010
    Location
    West Lancashire
    Posts
    737
    Thanks
    132
    Thanked 70 Times in 65 Posts

    Default Re: Sealed or vented?

    I honestly consider it no contest given the size of your home and your requirements.

    You need potentially large volumes of hot water (and cold) maybe at the same time.
    In order to make sure this works at all times go for a conventional system with high
    level cold water storage large dia pipes to deliver it - h & c. Mains cold to the kitchen
    and mains cold supplies to all bathroom/ensuit basins - teethwashing and drinking.

    Our place is 5 beds 3 w/c 2 showers and 1x with bath basins in every bedroom
    with upto 6 of us here at max - say xmas. Plumbed like this 10 years ago
    and it works.

    Then look at the summer when your neighbour is hosing their garden all the time cause they are not on a meter and your water supply is a trickle. Come home from work and have a shower then !

    Get a conventional system there will be plenty of advice as to which boiler is best

    There is no theory here just solid practical advice based on sound plumbing experience
    applied to my own home.

    centralheatking

  10. The Following User Says Thank You to Centralheatking For This Useful Post:

    stevenmarston (17-11-2010)

  11. #9
    New to Plumbing Forum
    Join Date
    Nov 2010
    Posts
    5
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Sealed or vented?

    Thanks for your detailed and really helpful response. I was wondering then, as you have this system, how did you deal with the disadvantages I'm told about, freezing pipes and tanks in the loft, air locks in the pipes and risk of leaks going un-noticed, any suggestions? Steve

  12. #10
    Plumbers Arms member
    moony's Avatar
    Join Date
    Oct 2009
    Location
    north wales, cheshire, shropshire
    Posts
    1,205
    Thanks
    66
    Thanked 41 Times in 41 Posts

    Default Re: Sealed or vented?

    insulate and install correctly and you wont have problems.

    i personally would consider upgrading mains and goin with the unvented.

  13. The Following User Says Thank You to moony For This Useful Post:

    stevenmarston (18-11-2010)

  14. #11
    Plumbers Arms member
    moony's Avatar
    Join Date
    Oct 2009
    Location
    north wales, cheshire, shropshire
    Posts
    1,205
    Thanks
    66
    Thanked 41 Times in 41 Posts

    Default Re: Sealed or vented?

    any plumber worth his salt should come around and do all this for you. and advise on the best system for your circumstances

  15. #12
    fuzzy
    Guest

    Default Re: Sealed or vented?

    unvented hot water and sealed heating, ie system boiler, no brainer for me

  16. #13
    UK Plumbersforums Trusted Advisor.

    Gray0689's Avatar
    Join Date
    Jun 2010
    Location
    Northern Ireland
    Posts
    4,654
    Thanks
    64
    Thanked 431 Times in 418 Posts

    Default

    Quote Originally Posted by fuzzy View Post
    unvented hot water and sealed heating, ie system boiler, no brainer for me
    Totally agree mate
    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

  17. #14
    Plumbers Arms member

    Join Date
    May 2008
    Posts
    700
    Thanks
    0
    Thanked 20 Times in 20 Posts

    Default Re: Sealed or vented?

    system boiler and unvented wins hands down i personaly like this type of system.

  18. #15
    Moderator


    croppie's Avatar
    Join Date
    Jul 2010
    Location
    Portadown, United Kingdom
    Posts
    7,586
    Thanks
    445
    Thanked 527 Times in 488 Posts

    Default Re: Sealed or vented?

    Aye. You can't beat belt and braces!
    Propino Tibi Salutem! Usque ad Mortem Bibendum!

    Croppie
    (By the way, I'm commercial!)

    IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

Page 1 of 2 12 LastLast

Similar Threads

  1. sealed or unsealed
    By philtheflush in forum Central Heating Forum
    Replies: 8
    Last Post: 08-11-2010, 09:53 PM
  2. sealed or unsealed
    By philtheflush in forum Plumbing Forum
    Replies: 0
    Last Post: 29-10-2010, 10:06 PM
  3. room sealed flue
    By piperdave in forum Gas Safe Register Forum - Public Forum
    Replies: 4
    Last Post: 23-03-2010, 10:40 PM
  4. Vented/Sealed
    By helpsy in forum Plumbing Forum
    Replies: 1
    Last Post: 11-03-2010, 09:03 PM
  5. sealed system
    By self-builder in forum Central Heating Forum
    Replies: 11
    Last Post: 12-02-2010, 05:42 PM

Visitors found this page by searching for:

power shower with sealed system

sealed boiler system or vented

vented or sealed system

sealed heating system shower problems

sealed or vented plumbing

vented central heating to sealed

showers for sealed systems

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.