    Question Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Help .. Running out of options..
    I have a client with a Grant vortex utility system 36-46 with riello burner.
    There is about a 20metre 10mm oil line under ground from tank to a fire valve (vertical? ) then tigerloop, Then in through a 22mm duct into the property under passage about 2.5mts then into boiler room out behind an unvented cylinder round into back of boiler. 2 Pipe then back to tiger loop.
    Flue is balanced flue straight up +/- 2mtrs through ceiling-roof
    It started locking out every few days last autum. I services it and changed dirty bowl filter.
    Went for a few days then locked out. I had a look and changed a stiff boiler temp control button and was fine all summer.
    Then a few weeks ago started locking out again. They always reset it by the time i got there and it seemed to run like a dream while I was there. Checked combustion, fan movement, oil supply etc. about 2 weeks ago went out locked out and smell of oil - cracked top of tigerloop?
    I then changed the tigerloop, flushed oil line ( few bits of sludge). Changed pump, drive dog and capacitor. Checked photo cell..
    All ran fine for a week then this morning locked out again. Going back tomorrow to have another look.
    I had a suspicion about the fire valve being vertical and no filter just before it. Problem is there is no room to install a filter where it comes out ground and to make fire valve horizontal.
    What is the affects of a vertically installed fire valve.
    Any Suggestions where to check next.?
    Is it only a fault in the burner that can cause a burner lock out?
    If there was a thermostat fault could that cause lock out or just over heat stat...?
    or poor flow through system...?
    Any suggestion welcome

  2. #2
    UK Plumbersforums Trusted Advisor.
    SimonG's Avatar
    Join Date
    Feb 2011
    Location
    in the land of make believe, in the county of durham, next best to Yorkshireland
    Posts
    16,035
    Thanks
    552
    Thanked 1,556 Times in 1,495 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Heldite all the oil line joints.
    Fly Me To The Moon And Let Me Play Among Stars.............




    No I'm not cheap, but I'm happy in my work.

    Wouldn't you rather have somebody that's happy working in your house?


  3. #3
    Member

    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    6,906
    Thanks
    231
    Thanked 777 Times in 758 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Don't waste your time and materials just changing parts.
    If a burner locks out, then the fault is to do with the burner, or its oil supply or fuel/air setting.
    A firevalve fitted vertical is totally fine.
    The oil pipe diameter needs to be not too big for Tigerloop and with no high spots and definitely no leaks. The suction hose could allow air in if jointed bad.
    Get an oil engineer to look at it. Too high an air setting will make boiler not start on cold weather first starts.
    Last edited by Best; 07-12-2016 at 12:25 AM.
    Last Plumber likes this.

  4. #4
    Forum Thug



    super-mod
    croppie's Avatar
    Join Date
    Jul 2010
    Location
    Lurking somewhere, generally up to no good........
    Posts
    23,718
    Thanks
    1,537
    Thanked 1,834 Times in 1,672 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Quote Originally Posted by SimonG View Post
    Heldite all the oil line joints.
    Wonderful stuff, heldite. ....
    Propino Tibi Salutem! Usque ad Mortem Bibendum!

    Croppie
    (By the way, I'm commercial!)


    IMPORTANT:
    Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal
    .


    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.


  5. #5
    Member
    Join Date
    Apr 2009
    Posts
    91
    Thanks
    10
    Thanked 0 Times in 0 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Quote Originally Posted by Best View Post
    Don't waste your time and materials just changing parts.
    If a burner locks out, then the fault is to do with the burner, or its oil supply or fuel/air setting.
    A firevalve fitted vertical is totally fine.
    The oil pipe diameter needs to be not too big for Tigerloop and with no high spots and definitely no leaks. The suction hose could allow air in if jointed bad.
    Get an oil engineer to look at it. Too high an air setting will make boiler not start on cold weather first starts.
    What do you mean oil pipe diameter needs to be too big for tigerloop?
    Unfortunately most of the oil line form tank to tigerloop is under concrete

  6. #6
    Member
    Join Date
    Apr 2009
    Posts
    91
    Thanks
    10
    Thanked 0 Times in 0 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Burner settings are O2 - 5.6%, Co2 - 11.3% , Co ppm - 27 , Xair - 36.6%

    So should I suspect air getting in suction hose or pipework form tigerloop. Presume any air being sucked in on oil line from tank will be vented through tiger loop?

  7. #7
    Plumbers Arms member
    Chalked's Avatar
    Join Date
    Jan 2013
    Posts
    3,810
    Thanks
    89
    Thanked 452 Times in 440 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    capacotor......
    Best likes this.

  8. #8
    Member

    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    6,906
    Thanks
    231
    Thanked 777 Times in 758 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Quote Originally Posted by RayPlumb View Post
    What do you mean oil pipe diameter needs to be too big for tigerloop?
    Unfortunately most of the oil line form tank to tigerloop is under concrete
    No, my wording was diameter needs to be NOT too big.
    Your analyser readings are good, so it could be air getting into oil line, or very possibly the capacitor as Chalked mentioned. Check the burner motor/fan starts instantly and try the burner on and off a dozen times to test motor always starts instantly. Any split second start will show capacitor faulty.

  9. #9
    Member
    Join Date
    Apr 2009
    Posts
    91
    Thanks
    10
    Thanked 0 Times in 0 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Quote Originally Posted by Best View Post
    No, my wording was diameter needs to be NOT too big.
    Your analyser readings are good, so it could be air getting into oil line, or very possibly the capacitor as Chalked mentioned. Check the burner motor/fan starts instantly and try the burner on and off a dozen times to test motor always starts instantly. Any split second start will show capacitor faulty.
    Thanks

  10. #10
    Member
    Join Date
    Nov 2013
    Location
    Workington, Cumbria
    Posts
    83
    Thanks
    2
    Thanked 6 Times in 6 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    If capacitor is OK then solenoid could be on it's way out. OK when cold but degrading when warmed up and cutting off oil feed.

  11. #11
    Member
    Join Date
    Apr 2009
    Posts
    91
    Thanks
    10
    Thanked 0 Times in 0 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Quote Originally Posted by mache View Post
    If capacitor is OK then solenoid could be on it's way out. OK when cold but degrading when warmed up and cutting off oil feed.
    I changed solenoid with one I knew worked. Day later locked out. Tested both and got 100 and 101ohms.

    Trying to work out if suction pipe sizing is correct.. I have 20- 25mts of 10mm copper pipe from oil tank to tigerloop. If pipework was forming gas and air in the pipe run would it not vent at the tigerloop ?

    The boiler nozzle capacity is 4.5kg/h
    Boiler is set at 41kw
    Last edited by RayPlumb; 07-12-2016 at 10:33 AM. Reason: correced

  12. #12
    Member
    Join Date
    Apr 2009
    Posts
    91
    Thanks
    10
    Thanked 0 Times in 0 Posts

    Default Re: Help.. Intermittent oil boiler lock out ( moved from Central heating Thread)

    Bottom of tank and tigerloop same height and burner down about 0.5mts

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Challenging - Intermittent Central Heating Problem
    By pank0906 in forum Central Heating Forum
    Replies: 2
    Last Post: 23-02-2016, 06:18 PM
  2. Intermittent heat to central heating
    By ftrilby in forum Central Heating Forum
    Replies: 8
    Last Post: 20-11-2013, 07:32 PM
  3. Vokera Linea 735 Intermittent Central Heating
    By Alex Beach in forum Central Heating Forum
    Replies: 1
    Last Post: 04-01-2012, 11:35 AM
  4. Replies: 7
    Last Post: 30-12-2011, 03:57 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.